Default Proper Support?

This 6,000 sf new home had a triple joist being supported by a piece of 2x8 & 2x4 and then supported by two 2x4's. Not sure why they were doing it like this. This was in the kitchen. You can also tell there is a versalam beam perpendicular to the joists. Alot of weight in this area...
I recommended triple studs directly under the top plate so the load would be transferred properly. Any thoughts?
Attached Thumbnails
proper-support-dsc04039.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/28/11, 2:28 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Proper Support?

I agree that a triple stud below the top plate, below the triple joist is needed. The pictured support does not seem to make a lot of sense. It's interesting that the wall has double studs across it. What was the purpose of that. What is this wall supporting above?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #3  
Old 12/28/11, 3:37 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Proper Support?

The 2x8 & 2x4 appear to be acting as a ledger. There should be a substantial support transfering the load directly to the foundation.

I would refer it to an engineer, but would not recommend a certain fix.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 12/28/11, 3:48 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Proper Support?

Quote:
Originally Posted by jfunderburk View Post
The 2x8 & 2x4 appear to be acting as a ledger. There should be a substantial support transfering the load directly to the foundation.

I would refer it to an engineer, but would not recommend a certain fix.
Exactly...it probably is a substantial load...an oddly built one at that.

If a person recommends a triple stud and the continued support below a floor, direct to the foundation, is forgotten, it would be problematic.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 12/28/11, 4:06 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Proper Support?

This whole thing looks like temporary supports to me. For one thing the drywallers are going to have fits when and if they come to this area. Even if this is fixed, the hanger bracket for the laminated beam was put in poorly and extends or hangs down below the bottom of the ceiling joists.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill








Last edited by dedwards; 12/28/11 at 4:12 PM..
Reply With Quote
  #6  
Old 12/28/11, 4:56 PM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: Proper Support?

Not proper support write it up.

With out knowing the loads the proper support may be more than three 2x4, plus you have to check the load path and make sure the load is properly transferred to the foundation. Don't tell them what to put in there just state it is not a proper support.





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #7  
Old 12/28/11, 5:26 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Proper Support?

Or you could say; According to good practice the support should transfer the load to the foundation and may not be a proper support. This should be confirmed by a qualified individual.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 12/28/11, 8:06 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Proper Support?

I agree, do not recommend a fix.
This picture does not show the whole picture.

You have three 2x8" joist supported on a ledger and 2 2x4's which looks like temporary, but ledger alone is not adequate to support that beam which appears to be supporting a substantial load unseen to us.

That built up beam is bolted with a couple of sandwich layers unknown indicating extra strength needed to support that PSL, or at least it looks more like a PSL than a Versa-lam or LVL.

Refer to Architectural Drawings, or defer to an Architect or SE for determination of it's adequacy.

If you look close, the built up beam is headed off indicating it is not bearing on the stud wall.

Weird framing for unknown reason from this end.
Reply With Quote
  #9  
Old 12/29/11, 1:44 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Proper Support?

Thanks for the input. I am waiting to hear back from the Super as to the path forward.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #10  
Old 12/30/11, 6:06 AM
Darren Tews, P.E. Darren Tews, P.E. is offline
InterNACHI Member
 
Join Date: May 2011
Posts: 47
Default Re: Proper Support?

I'm scratching my head with the framing method from the "top plate" upwards. Who rests the subfloor directly on top of the ends of studs? And what's up with the 2x4 running perpendicular from the lam beam in the top left of the photo.

The tripled up joists look like a triple flitch, and there doesn't appear to be enough through-bolts.



Licensed Engineer (NJ)
Licensed Home Inspector
Oak Ridge Engineering
Reply With Quote
  #11  
Old 12/31/11, 1:03 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Proper Support?

Richard,

I'm just guessing from pic, but looks like the installed blocking prevented bearing on plate (see pic) or maybe there was/is hardware there? Beam pocket or other may need to be built... maybe alters load path and foundation... fun

More bolts Darren? Now you sound like some of the SE's that would write up correction details for me. Just teasing..
Attached Thumbnails
proper-support-dsc04039.jpg  



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770









Last edited by tspargo; 12/31/11 at 1:12 AM.. Reason: edit
Reply With Quote
  #12  
Old 1/1/12, 11:03 AM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,495
Default Re: Proper Support?

Marcel was just pointing out that you could have taken better / more pictures.

Yes, there are blocks however it doesn't show if its blocked between what appears
to be bolted I-joist.


If that blocking is continuous then its a no brainer.....

just saying....
Reply With Quote
  #13  
Old 1/3/12, 11:08 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Proper Support?

Quote:
Originally Posted by dedwards View Post
This whole thing looks like temporary supports to me. For one thing the drywallers are going to have fits when and if they come to this area. Even if this is fixed, the hanger bracket for the laminated beam was put in poorly and extends or hangs down below the bottom of the ceiling joists.
I agree, that's temporary shoring.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/3/12, 4:16 PM
William C. Chandler William C. Chandler is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Deland, FL
Posts: 641
Default Re: Proper Support?

Based on the pic, the hangar and bolt pattern, the beam can't be for support. Is it solid? Do not understand why framers would need a temp support for any reason as framing is landed on top plate; so why would it need any bracing? Initial assumption would be the span was figured as such. I would go to plans and refer back to architect for clarification.




www.thebuildinginspector.net
William Chandler
Licensed Home Inspector #1025
Certified General Contractor #CGC060389
FHA 203(k) Inspector #A0954
Licensed Radon Measurement Technician #R2275
Certified Pollutant Storage Systems Contractor #PCC052624
Certified Underground Utility & Excavation Contractor #CUC057349
Reply With Quote
  #15  
Old 1/3/12, 4:27 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Proper Support?

Quote:
Originally Posted by wchandler View Post
Based on the pic, the hangar and bolt pattern, the beam can't be for support. Is it solid? Do not understand why framers would need a temp support for any reason as framing is landed on top plate; so why would it need any bracing? Initial assumption would be the span was figured as such. I would go to plans and refer back to architect for clarification.
I thought maybe it was a change.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deck support dokeefe Exterior Inspections 16 6/25/09 11:42 PM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Floor support posts kgerhauser Structural Inspections 7 7/17/07 12:23 AM


All times are GMT -4. The time now is 3:19 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts