Default Question about beams.

Doing phase construction inspections on a new house (for the builder, who is unexperienced (go figure)).

They have the beams in. Look at the post in picture 1, right in the center (not plumb), but especially, look at the mating of the beam from the right (picture 2). Is this mating OK? The beam from the right is not supported from below.

BTW: The backfill guy broke or bent about 1/2 the sill plate bolts (Picture 3).

Comments? How would you write this up?
Attached Thumbnails
question-beams-dscf6467-small.jpg   question-beams-dscf6468-small.jpg   question-beams-dscf6470-small.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 4/4/08, 8:45 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Question about beams.

Sorry Will, I don't see anything wrong.

Looks like a regular engineered system.

The unsuported beam connection is no different than bridge beams that I have seen and most of the time that same connection will be three to five feet away from the support column depending on load above.

Marcel
Reply With Quote
  #3  
Old 4/4/08, 8:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Question about beams.

Looks like a pretty standard connection to me as well. They'll plumb these up when they start dropping floor joists.

The damaged bolts would require an engineered repair in my area.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/4/08, 8:57 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Question about beams.

Quote:
Originally Posted by jpope
Looks like a pretty standard connection to me as well. They'll plumb these up when they start dropping floor joists.

The damaged bolts would require an engineered repair in my area.
Hey, Jeff;

Where do you see the damaged bolts?
Must have missed that unless it is the third picture that I could not define.

Marcel
Reply With Quote
  #5  
Old 4/4/08, 9:02 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Question about beams.

Thanks, guys. I don't know why the didn't use the same size (height) girder all the way across and why they didn't support it on the post.

Thanks again.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 4/4/08, 9:21 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Question about beams.

Quote:
Originally Posted by wdecker
Thanks, guys. I don't know why the didn't use the same size (height) girder all the way across and why they didn't support it on the post.

Thanks again.
Will, when it comes to steel beams, it is all about span and loading, and unnecessary beam size costs money, so it usually is sized to the loading of the span and connections make the transition.

By the way, I blew up the picture and noticed there is no bearing plates and anchorbolts on the steel columns.
I would be curious as to how they set them the right height.

Typically, you would see a baseplate on 3/4" of grout or leveling nuts to set the columns.

Any idea.?

Marcel
Reply With Quote
  #7  
Old 4/4/08, 11:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Question about beams.

Quote:
Originally Posted by mcyr
Hey, Jeff;

Where do you see the damaged bolts?
Must have missed that unless it is the third picture that I could not define.

Marcel
It looks like a couple of bent bolts in the top of the wall - third picture.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/4/08, 11:50 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Question about beams.

Quote:
Originally Posted by jpope
It looks like a couple of bent bolts in the top of the wall - third picture.
Sill plate bolts. The back filler guy broke off or bent about 1/3 of them.

Bad handeling of the Bobcat.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 4/4/08, 11:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Question about beams.

That's bad. Luckily, Simpson manufactures a strap that can replace those damaged anchor bolts. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 4/7/08, 1:35 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Question about beams.

Quote:
Originally Posted by jpope
That's bad. Luckily, Simpson manufactures a strap that can replace those damaged anchor bolts. . .
How is that strap anchored to the foundation?

Bent bolts are common and usually not a problem, but bent to this this extreme, once it's been straightened it'll be weaker than original specs. Pass on the liability.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 4/7/08, 11:10 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Question about beams.

They can be bolted to the side of the wall. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 4/7/08, 11:51 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Question about beams.

I douby they would go to this extreme, chances are they would drill and use quick bolts or wedge bolts and probably not be galvanized nor stainless because of the PT. contact.





Reply With Quote
  #13  
Old 4/7/08, 11:58 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Question about beams.

That's exactly what they use Marcel. Used to replace damaged or missing bolts, and for seismic upgrades to old, unbolted foundations.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 4/7/08, 8:31 PM
asargisian asargisian is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Columbia, MO
Posts: 313
Default Re: Question about beams.

actually the J bolts need to be replaced, only because the bolts are bent to close to the 2 corners meeting together. If the bolts were more further away from the corners, they can just use a nail gun to sink in support, as we did for inner walls. Also depends on what state requirements are for Earthquack anchors for the corners. I'll need to check my IRC or IBC, and get back with you guys, on what it will call for.

I know Southern Calif has to have Earthquack anchors on both sides of the corners, on all 4 corners of the home. My family uses them on every jobsite, for homes and apartments.



Missouri Home Energy Auditing Services

Residential & Commercial Inspections
Serving Central Missouri
Certified Missouri Home Inspector

InterNachi ID # 07110204

Environmental Inspection Solutions & Services

Thermal Infrared Imaging-Certified Thermographer


Energy Audit Consultant/Survey-Inspector

CMC Home Tune-uP Certified ID # 1505

E.S.A. Certified Mold Inspector & Assessor CMI CMIA




Last edited by asargisian; 4/7/08 at 8:42 PM..
Reply With Quote
  #15  
Old 4/7/08, 8:44 PM
asargisian asargisian is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Columbia, MO
Posts: 313
Default Re: Question about beams.

Marcel I have seen similar ones of those anchors, on commercial jobs but not residential. "Not Yet"



Missouri Home Energy Auditing Services

Residential & Commercial Inspections
Serving Central Missouri
Certified Missouri Home Inspector

InterNachi ID # 07110204

Environmental Inspection Solutions & Services

Thermal Infrared Imaging-Certified Thermographer


Energy Audit Consultant/Survey-Inspector

CMC Home Tune-uP Certified ID # 1505

E.S.A. Certified Mold Inspector & Assessor CMI CMIA



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 3:21 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts