Default Question about Field Modifications to Wood I-Beam

-During a Phased Inspection, I noticed that the builder had either ‘cut’ or ‘enlarged the cuts’ in numerous wood I-Beams so he could run HVAC flex duct through them. In my report, I stated that ‘Field Modifications’ are ‘not allowed’ to Wood I-Beams. (The holes were ‘not’ pre-defined knockouts)
-The builder responded that “it is only the middle third that cannot be modified”. I do not believe he is correct. As I see it, the corresponding IRC code reference is 502.8.2, “…..or I-joists are not permitted unless the effects of such penetrations are specifically considered in the design of the member.”
-Am I correct, that this means NO field modifications are allowed on wood I-Beam Joists, regardless of ‘where’ they are in the joist span.?



Rodney Sims
(Real Estate inspection Specialist)
(with 'INFRARED' Thermal Imaging)
CELL: 713-829-7732
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/13/10, 5:02 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Question about Field Modifications to Wood I-Beam

Quote:
Originally Posted by rsims2 View Post
-During a Phased Inspection, I noticed that the builder had either ‘cut’ or ‘enlarged the cuts’ in numerous wood I-Beams so he could run HVAC flex duct through them. In my report, I stated that ‘Field Modifications’ are ‘not allowed’ to Wood I-Beams. (The holes were ‘not’ pre-defined knockouts)
-The builder responded that “it is only the middle third that cannot be modified”. I do not believe he is correct. As I see it, the corresponding IRC code reference is 502.8.2, “…..or I-joists are not permitted unless the effects of such penetrations are specifically considered in the design of the member.”
-Am I correct, that this means NO field modifications are allowed on wood I-Beam Joists, regardless of ‘where’ they are in the joist span.?

Field cuts are typically allowed. Check with the specific manufacturer and keep the cuts within their specifications.

For example, see page 1:

http://www.ilevel.com/literature/TJ-9001.pdf



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 10/13/10, 5:06 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Question about Field Modifications to Wood I-Beam

I agree with Larry.

PS... Welcome !!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mold Resistant Wood by FrameGuard mcyr General Inspection Discussion 15 1/16/09 9:14 AM
National Field Rep. question? mwood1 General Inspection Discussion 2 12/11/06 3:36 PM


All times are GMT -4. The time now is 3:21 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts