Floor joist altered to route a radon vent to the exterior side wall.
- 2x4 added with drywall screws along the bottom of the cut joist..... - 2x4 added to the frame of the superior wall - 2x4 wedge tucked in where the two are out of alignment..... Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
| Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Quote:
|
|
#3
|
||||
|
||||
|
Problem is...
This is a contracted repair made by a Carpenter.. I have the reciept and a copy of the Work Order / Contract. Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#4
|
||||
|
||||
|
Quote:
So, who's problem is it, exactly? |
|
#5
|
||||
|
||||
|
How much of the joist was cut out?
I had a similar cut joist and saw the engineers report during the reinspect. It basically said that no issue was present since the cut joist was near a wall with another joist nearby. Guess who hired the engineer? Yep, the sellers. I would still write it up. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#6
|
||||
|
||||
|
Quote:
I agree and would, at the least, write it up as amateurish work. IMO, it is not a proper repair for a 4.5" hole from a 4" pipe (it appears). The funny part is the 2 x 4 "column" with the squash block is offset enough to not support anything and is virtually useless; it does look pretty though. |
|
#7
|
||||
|
||||
|
That squash block is doing Zero.
Why not just transfer the joist too the opposite side of the radon vent? The right side. Write it up....... If the squash block is already moving, then any weight will expose it fragility. montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
|
#8
|
|||
|
|||
|
Just for a FYI the max. notching of floor joists without repair must occur in the outside 1/3 and can be no larger than D/3 in width and D/6 in depth notch not meeting that requirement is included in my report. If it is drilled it must be no closer than 2" from the top or bottom of the joist and must be no more than D/3
Mark S. Tyson M Tyson construction LLC Tyson Home Inspections Certified General Contractor #1516843 Florida Licensed Home Inspector #1824 Member N.A.C.H.I. IAC2 certified Member Florida Building Officials Association http://www.TysonHomeInspections.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Phoenix Appliance, Air Conditioning, Heating and Repair | Scott P. Corsley | General Inspection Discussion | 1 | 5/1/08 6:34 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |