Default Report Help Strucural Beam Cuts

I am not sure how to adress these issues I found on an inspection. I would think that these cuts seams should have been bolted or welded.

And the plumbing drain hole is totaly not allowed.

How wouldf you write it up?
Attached Thumbnails
report-help-strucural-beam-cuts-beam-2.jpg   report-help-strucural-beam-cuts-beams.jpg   report-help-strucural-beam-cuts-beams-plumbing.jpg  



Rick Kie
Reply With Quote
  #2  
Old 2/17/09, 7:13 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Report Help Strucural Beam Cuts

Ricky,

It appears that the bearing end of that beam has settled, which caused the V-opening at the abutting seam. Or maybe the temporary jack (which is an improper support for a steel beam) was raised too high.

As for the hole, I don't see a problem with it.

Restrictions on size and position of openings

Guidance on the size and position of Steel beam web openings:

Horizontal position: Openings should be positioned not less than twice the beam depth or span/10 from a support and not less than the beam depth from any point load.

Vertical position: The opening should, if possible, be positioned at the mid-height of the beam. Otherwise, the depths of the upper and lower sections should not differ by more than a factor of 2.

Opening size:
The opening length and height should not exceed 1.5D and 0.6D respectively in un-stiffened sections or 2.0D and 0.7D in stiffened sections (D = o/a beam depth).

Spacing of openings: The distance between adjacent openings should not be less than the beam depth.

Circular openings should be treated by assuming a length equal to 0.9 x the radius of the opening, and a depth equal to 1.8 x the radius. All other openings should have radiused corners.
Reply With Quote
  #3  
Old 2/17/09, 9:46 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Report Help Strucural Beam Cuts

Quote:
Vertical position: The opening should, if possible, be positioned at the mid-height of the beam. Otherwise, the depths of the upper and lower sections should not differ by more than a factor of 2.
...and you don't see a problem with it??
Reply With Quote
  #4  
Old 2/17/09, 9:56 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Report Help Strucural Beam Cuts

The support should be replaced, the joint should be secured and the drain hole is no problem at all. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/17/09, 1:59 PM
Douglas Cossar's Avatar
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,228
Default Re: Report Help Strucural Beam Cuts

That plumber, or whom ever had one heck of a holesaw



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #6  
Old 2/17/09, 6:54 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by dvalley View Post
Guidance on the size and position of Steel beam web openings:

Horizontal position: Openings should be positioned not less than twice the beam depth or span/10 from a support and not less than the beam depth from any point load.

Vertical position: The opening should, if possible, be positioned at the mid-height of the beam. Otherwise, the depths of the upper and lower sections should not differ by more than a factor of 2.

Opening size: The opening length and height should not exceed 1.5D and 0.6D respectively in un-stiffened sections or 2.0D and 0.7D in stiffened sections (D = o/a beam depth).

Spacing of openings: The distance between adjacent openings should not be less than the beam depth.

Circular openings should be treated by assuming a length equal to 0.9 x the radius of the opening, and a depth equal to 1.8 x the radius. All other openings should have radiused corners.

I'm having trouble understanding this. I can see how you could have a horizontal opening in a web but how do you have a verticle hole in a web?
Too bad there's no diagram.
Reply With Quote
  #7  
Old 2/17/09, 7:01 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by jallingham View Post
I'm having trouble understanding this. I can see how you could have a horizontal opening in a web but how do you have a verticle hole in a web?
Too bad there's no diagram.
Think location...horizontal is left and right and verticle is up and down.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 2/17/09, 10:19 PM
George R. Schaser George R. Schaser is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 2
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by rkie View Post
I am not sure how to adress these issues I found on an inspection. I would think that these cuts seams should have been bolted or welded.

And the plumbing drain hole is totaly not allowed.

How wouldf you write it up?
all I beam seams & or joints must be welded or bolted plates are necessary on this type application. No holes and or alterations are not allowed without consent by a structural engineer.
Reply With Quote
  #9  
Old 2/17/09, 11:01 PM
George R. Schaser George R. Schaser is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 2
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by gschaser View Post
all I beam seams & or joints must be welded or bolted plates are necessary on this type application. No holes and or alterations are not allowed without consent by a structural engineer.
Holes can be plated on both sides of beam to maintain structural strenth.
Reply With Quote
  #10  
Old 2/18/09, 7:13 AM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Report Help Strucural Beam Cuts

Thanks for everyones input.



Rick Kie
Reply With Quote
  #11  
Old 2/18/09, 10:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by gschaser View Post
No holes and or alterations are not allowed without consent by a structural engineer. Holes can be plated on both sides of beam to maintain structural strenth.
The holes in the web do not need any reinforcement. There is absolutely nothing wrong with the hole as it is pictured, and they do not need engineer approval.

The hole cannot be in the web over a support, but is allowed anywhere within the span.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 2/18/09, 2:04 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Report Help Strucural Beam Cuts

Looking at the first picture and the way it is painted it almost looks like there was different support there before.

Web hole fine, beam needs to be secured to a permanent support.
Reply With Quote
  #13  
Old 2/18/09, 5:38 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Report Help Strucural Beam Cuts

Quote:
Vertical position: The opening should, if possible, be positioned at the mid-height of the beam. Otherwise, the depths of the upper and lower sections should not differ by more than a factor of 2.
Show me how the hole does not violate this provision. The hole is not in the mid-height of the beam, and the depths of the upper and lower sections differ by a factor of about a thousand. (exaggerated somewhat for effect) My guess is that a structural engineer might require this particular hole to be reinforced somehow, if he would not condemn it completely.
Reply With Quote
  #14  
Old 2/18/09, 8:10 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Report Help Strucural Beam Cuts

Quote:
Originally Posted by Richard A. Hetzel View Post
Show me how the hole does not violate this provision. The hole is not in the mid-height of the beam, and the depths of the upper and lower sections differ by a factor of about a thousand. (exaggerated somewhat for effect) My guess is that a structural engineer might require this particular hole to be reinforced somehow, if he would not condemn it completely.
That's how I read that, too, Richard.

Where did you get that info David?...or Jeff, can you address?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 2/18/09, 10:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Report Help Strucural Beam Cuts

Where did that "provision" come from? It's not anything I recognize. I would like to see it in its entire context.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
In the works for FetchReport.com inxil Miscellaneous Discussion for Inspectors 28 7/23/09 4:15 PM
**HOT** Texas Inspectors use of REI-7A-0 escanlan Legislation, Licensing & Legal Issues for Inspectors 27 11/20/07 12:09 AM


All times are GMT -4. The time now is 3:22 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts