Default Request I-Truss install input

Todays inspection- 10 year old condo. with I trusses. I have only seen them installed with the bottom cord bearing on the sill plate.

To me it looks like someone had never installed I trusses and cut the web so that only the double top cord is taking all the load!

We have all seen our share of improper installs slip past the local building officials but I wanted to ask on the board if you have ever seen this building practice and if so is it correct ? I don't see how this is correct so I am asking for your input and verbiage. thanks in advance.

John
Attached Thumbnails
request-truss-install-input-hip-072.jpg   request-truss-install-input-hip-074.jpg  
Reply With Quote
  #2  
Old 9/5/08, 10:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Request I-Truss install input

They're fine. Notice the doubled top chord.

Top chord bearing floor truss being installed



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 9/5/08 at 10:49 PM..
Reply With Quote
  #3  
Old 9/5/08, 11:42 PM
Terry B. Clayton Terry B. Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 193
Default Re: Request I-Truss install input

Michael in the picture you provided the first 2 portions of the web have been doubled and the first may have triple 2 X's I am not that familiar with I-Joist but John's pictures don't show the extra structure. I am not trying to be rude just trying to learn, which has come leaps and bounds from all of the EXPERTS or not that take the time to share with us. Thanks for your input
Reply With Quote
  #4  
Old 9/5/08, 11:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Request I-Truss install input

Quote:
Originally Posted by mlarson
They're fine. Notice the doubled top chord.

Top chord bearing floor truss being installed
Agreed!

Notice the depth of the truss, it must span 30-35 feet or going to have to support a hell of a load.
Reply With Quote
  #5  
Old 9/6/08, 12:49 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Request I-Truss install input

A top bearing cord truss is quite common.

http://www.classictruss.com/floor_truss_facts.asp



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 9/6/08, 1:04 AM
Terry B. Clayton Terry B. Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 193
Default Re: Request I-Truss install input

Thank You Joseph for your help
Reply With Quote
  #7  
Old 9/8/08, 2:38 PM
John G. Jones's Avatar
John G. Jones John G. Jones is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Muskegon, Mi
Posts: 88
Send a message via MSN to jjones2
Default Re: Request I-Truss install input

thanks for the help guys, much appreciated.

John
Reply With Quote
  #8  
Old 9/14/08, 12:48 PM
hbrooks hbrooks is offline
InterNACHI Member
 
Join Date: May 2007
Location: Fredericksburg, VA
Posts: 2
Default Re: Request I-Truss install input

There is no termination tying the bottom chord to the top chord at the hanging end. If you note in the diagram shown in the link from Joseph Hagart, there is supposed to be a termination blocking and strapping. The installation in question looks like someone just whacked off some longer trusses to fit this space. Gee, contractors wouldn't do something like that would they? I would recommend review by a structural engineer or Professional Truss Designer

H. Stuart Brooks
Virginia Certified Home Inspector
Virginia Inspection Service, LLC
Reply With Quote
  #9  
Old 9/14/08, 2:50 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Request I-Truss install input

Trusses as shown in the photographs are quite common, and often the bottom chord is not extended at all. Termination blocking would perform no structural function. The extended bottom chords are designed as cantilevers, and do not need to be tied back to the top chord. The fact that some trusses are built that way does not make it a universal requirement.

See the diagrams on page 34 of the following:
http://www.alpeng.com/images/stories/pdfs/BGT_BOOK.pdf
They show floor trusses of the exact configuration as the photographs.

Nothing wrong with them.
Reply With Quote
  #10  
Old 9/16/08, 11:59 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Request I-Truss install input

Richard, thanks for taking the time to post on these boards. Your posts are very helpful.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #11  
Old 9/17/08, 1:16 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: Request I-Truss install input

Excellent reading and study material!! Thanks for your input!

Jeff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Truss Uplift rcooke Canadian Inspectors 5 2/26/08 8:43 PM


All times are GMT -4. The time now is 6:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts