Default Request I-Truss install input

Todays inspection- 10 year old condo. with I trusses. I have only seen them installed with the bottom cord bearing on the sill plate.

To me it looks like someone had never installed I trusses and cut the web so that only the double top cord is taking all the load!

We have all seen our share of improper installs slip past the local building officials but I wanted to ask on the board if you have ever seen this building practice and if so is it correct ? I don't see how this is correct so I am asking for your input and verbiage. thanks in advance.

John
Attached Thumbnails
request-truss-install-input-hip-072.jpg   request-truss-install-input-hip-074.jpg  
Reply With Quote
  #2  
Old 9/5/08, 10:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Request I-Truss install input

They're fine. Notice the doubled top chord.

Top chord bearing floor truss being installed



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 9/5/08 at 10:49 PM..
Reply With Quote
  #3  
Old 9/5/08, 11:42 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 244
Default Re: Request I-Truss install input

Michael in the picture you provided the first 2 portions of the web have been doubled and the first may have triple 2 X's I am not that familiar with I-Joist but John's pictures don't show the extra structure. I am not trying to be rude just trying to learn, which has come leaps and bounds from all of the EXPERTS or not that take the time to share with us. Thanks for your input
Reply With Quote
  #4  
Old 9/5/08, 11:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Request I-Truss install input

Quote:
Originally Posted by mlarson
They're fine. Notice the doubled top chord.

Top chord bearing floor truss being installed
Agreed!

Notice the depth of the truss, it must span 30-35 feet or going to have to support a hell of a load.
Reply With Quote
  #5  
Old 9/6/08, 12:49 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Request I-Truss install input

A top bearing cord truss is quite common.

http://www.classictruss.com/floor_truss_facts.asp



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 9/6/08, 1:04 AM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 244
Default Re: Request I-Truss install input

Thank You Joseph for your help
Reply With Quote
  #7  
Old 9/8/08, 2:38 PM
jjones2's Avatar
jjones2 jjones2 is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Muskegon, Mi
Posts: 89
Send a message via MSN to jjones2
Default Re: Request I-Truss install input

thanks for the help guys, much appreciated.

John
Reply With Quote
  #8  
Old 9/14/08, 12:48 PM
hbrooks hbrooks is offline
InterNACHI Member
 
Join Date: May 2007
Location: Fredericksburg, VA
Posts: 2
Default Re: Request I-Truss install input

There is no termination tying the bottom chord to the top chord at the hanging end. If you note in the diagram shown in the link from Joseph Hagart, there is supposed to be a termination blocking and strapping. The installation in question looks like someone just whacked off some longer trusses to fit this space. Gee, contractors wouldn't do something like that would they? I would recommend review by a structural engineer or Professional Truss Designer

H. Stuart Brooks
Virginia Certified Home Inspector
Virginia Inspection Service, LLC
Reply With Quote
  #9  
Old 9/14/08, 2:50 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Request I-Truss install input

Trusses as shown in the photographs are quite common, and often the bottom chord is not extended at all. Termination blocking would perform no structural function. The extended bottom chords are designed as cantilevers, and do not need to be tied back to the top chord. The fact that some trusses are built that way does not make it a universal requirement.

See the diagrams on page 34 of the following:
http://www.alpeng.com/images/stories/pdfs/BGT_BOOK.pdf
They show floor trusses of the exact configuration as the photographs.

Nothing wrong with them.
Reply With Quote
  #10  
Old 9/16/08, 11:59 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Request I-Truss install input

Richard, thanks for taking the time to post on these boards. Your posts are very helpful.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 9/17/08, 1:16 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,116
Default Re: Request I-Truss install input

Excellent reading and study material!! Thanks for your input!

Jeff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Truss Uplift rcooke Canadian Inspectors 5 2/26/08 8:43 PM


All times are GMT -4. The time now is 12:43 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts