Default Result of Improper Door Installation

Discovered considerable structure damage concealed behind rim joist insulation. This area is directly below a sliding glass door, home built 1990.
It pays to look behind the rim insulation, I have discovered similar issues on previous inspections, mostly below doors.

result-improper-door-installation-clover-046.jpg

result-improper-door-installation-clover-047.jpg

result-improper-door-installation-clover-048.jpg

result-improper-door-installation-clover-049.jpg

result-improper-door-installation-clover-050.jpg



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America)
  #2  
Old 6/6/09, 7:41 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 4,255
Send a message via Yahoo to bboerner
Default Re: Result of Improper Door Installation

Do you look behind all rim insulation or just where doors are present up above?



Bill Boerner
St. Louis,MO - Professional Home Inspector

STLhomeinspector.com
All of metro St. Louis including all surrounding Areas Customer Testimonials



Home Inspector Pro Software - A Professionals choice in software.
Reply With Quote
  #3  
Old 6/6/09, 8:20 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 519
Default Re: Result of Improper Door Installation

Mostly below doors, and areas where the insulation is discolored.



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #4  
Old 6/6/09, 9:47 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Result of Improper Door Installation

Rule # 101: "Caulking is not flashing."

Nuff said.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 6/6/09, 11:02 PM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 554
Default Re: Result of Improper Door Installation

Same thing here from a previous thread. I pull back the insulation, as much as I can. If you saw this post, you'll see why.(video shot is actually my own house that I'm repairing right now). The inspector (about 9 years ago, when I was doing construction and not inspecting) didn't look behind the insulation and the sill is rotted out. This guy is still in business touting his 30 years experience.



Bobby Hamilton
Bloodhound Home Investigations
Youngstown Home Inspection
Boardman Ohio Home Inspection
Youngstown Home Inspector

Providing home inspections and state licensed termite inspections in the Youngstown and Northeast Ohio areas.
Reply With Quote
  #6  
Old 6/7/09, 12:17 AM
Richie Dimmerling Richie Dimmerling is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: whitehall, OH
Posts: 41
Default Re: Result of Improper Door Installation

It is good to check where you have decks too, I have seen problems with water intrusion from them not being flashed or improperly flashed.



Richie Dimmerling II, E.I., S.I.
Inspection Engineer
614.309.7552

Reply With Quote
  #7  
Old 6/7/09, 12:30 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Result of Improper Door Installation

And porches!



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 6/7/09, 7:52 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 519
Default Re: Result of Improper Door Installation

Unfortunately, we have too many finished basements with drywall ceilings that conceal these problems. A moisture meter is most likely useless unless the water migrates to the drywall surface. I doubt if my infrared imager would detect abnormal conditions in most finished basements that have similar water intrusion issues, although I do scan the rim areas.



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #9  
Old 6/7/09, 11:01 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,349
Default Re: Result of Improper Door Installation

This was a sliding door unit too!







Some people just don't know how to flash door units. Or build period.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #10  
Old 6/7/09, 1:18 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Result of Improper Door Installation

Quote:
Originally Posted by wdecker View Post
Rule # 101: "Caulking is not flashing."

Nuff said.
Exactly!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #11  
Old 6/7/09, 3:30 PM
Ian A. Niquette's Avatar
Ian A. Niquette Ian A. Niquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,193
Send a message via ICQ to iniquette
Default Re: Result of Improper Door Installation



No deck flashing



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network



What we've got here is......failure......to communicate.....
Reply With Quote
  #12  
Old 6/7/09, 3:40 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,349
Default Re: Result of Improper Door Installation

There wasn't any on this one either.









Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 6/7/09, 7:59 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 519
Default Re: Result of Improper Door Installation

Great images! Where are the local code inspectors? Marcel, can I borrow your deck ledger images?



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America)
  #14  
Old 6/7/09, 8:54 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,349
Default Re: Result of Improper Door Installation

Be my guest John.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #15  
Old 6/11/09, 8:54 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,824
Default Re: Result of Improper Door Installation

I always use one of these to check the rim joist, makes it easier and it works great for opening the attic hatch.
Attached Thumbnails
result-improper-door-installation-probe.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
De-rate? Due to improper seperation? rstewardson Electrical 4 3/24/09 12:43 PM
Improper engineering bclark HVAC 9 1/9/08 12:03 AM
Defects as described by Lawyers mcyr Misc. Discussion 3 10/28/07 8:58 AM
Question about improper installation cbell1 Exterior 3 10/24/07 10:13 PM


All times are GMT -4. The time now is 3:27 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts