Default roof

Yesterday I inspected a house, that had a bat and board style roof instead of plywood sheeting. This house was built 50+ years ago. It has a composition shingle roof with several leaks. Can you put this type of roof on a bat and board roof? I don't beleive you can, I wrote it up repair or replace with plywood or OSB sheeting. Any views on this?
Attached Thumbnails
roof-hpim0261.jpg  
Reply With Quote
  #2  
Old 3/21/06, 9:00 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: roof

Space planking is fine. It is actually better than plywood or OSB as it allows much better ventilation to the underside of the shingles. Typical for age. It there are leaks of course the shingles should be replaced/repaired. The planking is no problem and the existing shingles could be stripped with new shingles applied on existing decking.
Reply With Quote
  #3  
Old 3/21/06, 9:06 AM
jmaisano's Avatar
jmaisano jmaisano is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: woodstock, GA
Posts: 29
Default Re: roof

i agree but on this roof some of the spaceing is more than 1" wide and the nail strip falls in that space and is leaking i dont believe this is the rite roof covering for this type of sheeting?
orr is it just a poor job of roofing
Reply With Quote
  #4  
Old 3/21/06, 9:18 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: roof

In that case they could whe replacing shingles fill the larger gaps with firring. Or they could place OSB or plywood over current planking. Personally I like plank spaced decking. But the spacing should not be more than quarter inch.
Reply With Quote
  #5  
Old 3/21/06, 12:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: roof

OK......you want my TAKE on it....

I called my brother who also is a roof contractor and asked him because for many years I have been taught that Roll Comp, Asphault Comp., Built Up require solid decking and I believe this is considered solid decking the way it looks in the picture...

Now just for fun I called him...my brother said the reason solid is required on Asphault is because of the placement of the nails to support the shingle itself...would be too hard to maintain the correct placement since many will not determine the proper way to lay the decking......so it would be impossible for a 2nd layer to ever be applied correctly since it would not show the exact location of the under decking to nail into correctly....Not to mention the requirement for FELT could make the install quite tricky.

Again.....this is just to say WHY spaced decking is not allowed....put them together like in the picture and it becomes solid decking and fine.

also since 1 layer of 15LB felt on roofs 4:12 and 2 layers on 2:12 the underneath would not need to breathe like you would have on Wood Shingles....

Anyway.....If I saw spaced decking and a asphault roof I would refer it to a roofing contractor......but again thats MY opinion and this looks SOLID to me......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 3/21/06 at 12:11 PM..
Reply With Quote
  #6  
Old 3/21/06, 8:56 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,908
Default Re: roof

Some may disagree, but my old mans' house was built in approximately 1940,and the house was roofed with boards that were not squared off. The roofing shingles spanned the gaps and the attic ventilation did not exist. The roofing would last for 30-40 years. From 1951-1969, I do not remember that the roofing was replaced.

Of course, I was not an Inspector back then. ha. ha.

The lack of solid substrate underlayment, is not always the problem. Look further.

Marcel
Reply With Quote
  #7  
Old 3/22/06, 12:22 AM
jmaisano's Avatar
jmaisano jmaisano is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: woodstock, GA
Posts: 29
Default Re: roof

Thanks Paul, that's what I was looking for. The subject has been in much debate in my mind and with some of the people I have worked with in the past that are roofers. It seems half of them say this is no problem, and the other half say this is a problem. I wish I had better pictures, but this is not a soild roof sheeting. Some of the gaps are as much as 1in thick. It has come to my conclusion that I was right in my original assessment. I wrote it up as half liscened roofer evaluate and make reapairs as needed.
Reply With Quote
  #8  
Old 3/22/06, 5:13 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: roof

Quote:
Originally Posted by jmaisano
I wrote it up as half liscened roofer evaluate and make reapairs as needed.
Would that be the same "half" licensed roofer who did the original work?
Sorry.
Darn margaritas.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #9  
Old 3/22/06, 7:29 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: roof

A good roofer would not have any problem with plank spaced roof decking. They do make chalk lines and can mark the nail line very easily.

A roof of this age has most certainly been reshingled over the years without the necessity of solid decking. Perhaps the shingles are old and the current installation was never installed correctly?
Reply With Quote
  #10  
Old 3/22/06, 1:40 PM
Adam J. Slimack Adam J. Slimack is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Clarence, NY
Posts: 162
Default Re: roof

Am i missing something? The picture looks to me like a tongue and groove roof deck typical of 50s construction. Looks like the ridge has been cut back (or at least one side of it) for a ridge vent.

If thats what i'm seeing, i would rather have this roof deck than a plywood or particle board deck as the inevitable leaking near roof penetrations (over time) will not adversely affect the 1x as soon as it would the plywood / osb.

Adam, A Plus
Reply With Quote
  #11  
Old 3/25/06, 9:49 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: roof

I am with Raymond and Adam on this one that asphalt shingles on wood plank roof decks/sheathing is fine, as long as it's not deteriorated and there are no large gaps between the planks. While contractors may be able to install asphalt shingles on spaced wood plank decks/sheathing, it's not good practice and would not meet current construction standards.

Spaced wood plank decks/sheathing is permitted for wood shingles, with a few limitations/requirements (see IRC R905.7.1), but not for asphalt shingles. IRC 905.2.1 on sheathing for asphalt shingles requires that "Asphalt shingles shall be fastened to solidly sheathed decks". Planks with significant gaps would not be "solid" ...

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 3/25/06, 9:57 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: roof

Almost all the old homes in my area have spaced planking that is usually 1/4" - 1/2" gap max. Planking spaced further apart on old house may be an indication that the roof was once wood shake.
Reply With Quote
  #13  
Old 3/25/06, 10:16 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: roof

Quote:
Originally Posted by rwand1
Planking spaced further apart on old house may be an indication that the roof was once wood shake.
Good point to keep in mind ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 3/25/06, 10:34 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: roof

Hi to all,

Would I write up asphalt shingles installed over board sheathing, NO WAY prior to the 1960's there was no solid sheathing at all and all roofs were laid over boards.

I have been involved in many re-roofing projects over older board decking and as others have said you just need to repair any damaged boards (they frequently have split edges from old nailing) I would not report the roof as deficient due to this condition, we can't start imposing modern IRC codes on home built prior to the code and before the advent of modern sheathing materials.

If the singles are not correctly nailed due to gaps between the boards then that is all I would report.

My own home in New England (built 1920ish) had practically unfinished baords as the roof decking, and some needed replacement, and some areas needed to be furred out. (the boards themselves were non-dimensional 1" thick and varried between 6' an 12" wide)

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #15  
Old 3/25/06, 11:00 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,705
Send a message via Yahoo to jfunderburk
Default Re: roof

Quote:
Originally Posted by jmaisano
I wrote it up repair or replace with plywood or OSB sheeting. Any views on this?
Tear off the existing roof sheathing because it isn't plywood? Seems rather extreme. Do you have a roofing contractor license? If not, I wouldn't ever say such a thing. "Recommend evaluation and repair by a licensed roofing contractor."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 11:50 AM
Cracked shingles pwigle Exterior Inspections 54 4/24/09 12:52 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 1:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 2:19 AM


All times are GMT -4. The time now is 12:26 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts