Default Are roof rafter notches allowed

There were notches in one rafter, which was on a portion of the home that was an exterior wall. They were about every 2 feet or so. Are notches in rafters allowed? I do not think they are according to the code book but am not entirely sure.
Attached Thumbnails
roof-rafter-notches-allowed-dscn5267.jpg  
Reply With Quote
  #2  
Old 12/6/06, 10:07 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Are roof rafter notches allowed

Notching on those trusses would not be allowed without written exceptions and specific instruction (maintained on site) from the AOR (or EOR) who designed the cuts into them...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #3  
Old 12/6/06, 10:26 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: Are roof rafter notches allowed

IRC 802.10.4 and UBC 2320.1 calls out no field modification except with engineer approval.

I am concerned that the depth appears at approximately 50% of the chord.I would be additionally concerned if the notch were on the tension side of the chord instead of the compression. If there are no markings or approval notes on-site, I personally would call it out.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #4  
Old 12/6/06, 10:34 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Are roof rafter notches allowed

Quote:
Originally Posted by bsumpter
IRC 802.10.4 and UBC 2320.1 calls out no field modification except with engineer approval.

I am concerned that the depth appears at approximately 50% of the chord.I would be additionally concerned if the notch were on the tension side of the chord instead of the compression. If there are no markings or approval notes on-site, I personally would call it out.
Does this also apply to gable end trusses?
They are not built the same way and do not serve the same purpose and field trusses.

I'm more curious as to the contruction of the overhang on the other side of the end truss.
Reply With Quote
  #5  
Old 12/6/06, 11:01 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: Are roof rafter notches allowed

Usually the last truss is made shorter ("dropped" 3 1/2) so the lookout blocks can span from the last tall truss over the top of the shorter end truss and support the fly rafter that forms the projected rake.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #6  
Old 12/6/06, 2:02 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Are roof rafter notches allowed

I'd say "no" to cutting the trusses, any way shape or form, without the written approval from the Truss Manuf.
Look at the cuts, the truss seems to be notched approx. 50% and ragged at that. Note the lower (left) notch of the truss.
I'd write up as a structual change to the truss, and recommend further review.
Reply With Quote
  #7  
Old 12/6/06, 2:10 PM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 531
Default Re: Are roof rafter notches allowed

Hi Ron,

That appears to be the gable end wall, if it is there is no load
there to speak of and I would not write this up.

CJ
Reply With Quote
  #8  
Old 12/6/06, 2:31 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Smile Re: Are roof rafter notches allowed

Quote:
Originally Posted by gveal
I'd say "no" to cutting the trusses, any way shape or form, without the written approval from the Truss Manuf.
Look at the cuts, the truss seems to be notched approx. 50% and ragged at that. Note the lower (left) notch of the truss.
I'd write up as a structual change to the truss, and recommend further review.
I agree with with Greg and recommend further review. Down here in TX, I've seen the last truss (as in the picture) doubled to reinforce a gable end.

Trusses, when exposed to fires, are dangerous enough without having them compromised by cutting.

My .02 cents
Bruce
Reply With Quote
  #9  
Old 12/6/06, 5:18 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Are roof rafter notches allowed

I always recommend writing up any field modifications or cuts to trusses, unless there is documentation stating otherwise (rarely on-site).

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 12/8/06, 1:31 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Are roof rafter notches allowed

Always call out any modifications to trusses. They are not to be field-altered without engineer-approved designs which have to be inspected by a building official after changes are made.

You assume liability if you leave it out.

"Trusses with visible field alterations were visible in the roof framing. Altering of trusses in the field requires engineer-approved designs which must be inspected and approved by a building official after changes are made. You should ask the sellers to provide documents showing that alterations to the trusses were inspected and approved by the proper authorities."




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 12/8/06, 11:44 PM
ccoombs's Avatar
ccoombs ccoombs is offline
Active Poster
 
Join Date: Jul 2004
Location: Corona, CA
Posts: 121
Please Note: ccoombs is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Are roof rafter notches allowed

This type of notching is done on almost every gable end truss in California. The work done in the picture looks very clean!

I would note it in your inspection report to cover any potential liability but I would not recommend further evaluation.

If the gable end truss sits over an exterior wall it will be continuously supported. These trusses will typically be designed as a drag truss and take into account the notching.
Reply With Quote
  #12  
Old 12/9/06, 1:51 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Are roof rafter notches allowed

I was looking at it wrong. With the gabled end sheathed and typically nailed off at 6&12 it should be fine. I guess I'd mention it but structurally it's not going anywhere.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #13  
Old 12/9/06, 8:36 AM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Are roof rafter notches allowed

Up here, notching the gable end truss is common, it is done to support the lookouts and fascia on the end of the gable. Since the webbing in the truss is vertical, it is considered by Building inspectors to be ok. More truss makers are switching to drop gables where the only notching is on the 2X6 outrigger itself.
Reply With Quote
  #14  
Old 2/9/09, 8:23 PM
Mike Truss Guy's Avatar
Mike Truss Guy Mike Truss Guy is offline
New User
 
Join Date: Feb 2009
Location: Las Vegas
Posts: 17
Please Note: Mike Truss Guy is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Are roof rafter notches allowed

Those gable trusses are notched for outlookers. Typically in the truss calc package that is submitted, there is a detail showing this notch detail. Remember that this truss is covered with sheathing and sits on a continuous bearing wall.
Reply With Quote
  #15  
Old 2/21/09, 2:40 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Are roof rafter notches allowed

Yes, it is generally OK. Many time the calc's include a pre-req for nailing a 1 x 4 under notches on a gable end.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM
Acceptable roof rafter repairs ldapkus Exterior Inspections 14 7/17/06 11:49 AM


All times are GMT -4. The time now is 3:23 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts