Default How scary is this?

The cantelever looks real scary at first... but if you look at the wall logs (side walls) they cantelever way back and help carry the load. There'd be more if they weren't interruped by the window.
The floor joists bearing on the beam (yep, it's got a bow) below the popped-out gable wall cantelever way back into the home, so they help too.
The two posts look skinny (7-8"), but how much are they really carrying?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 1:39 AM..
Reply With Quote
  #2  
Old 9/20/07, 8:05 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: How scary is this?

Quote:
Originally Posted by kshepard
The cantelever looks real scary at first... but if you look at the wall logs (side walls) they cantelever way back and help carry the load. There'd be more if they weren't interruped by the window.
The floor joists bearing on the beam (yep, it's got a bow) below the popped-out gable wall cantelever way back into the home, so they help too.
The two posts look skinny (7-8"), but how much are they really carrying?
This is one of those where "it all helps" considering the puny log "headers" above the overhead door type opening carrying the floor logs.

Certainly a design that is lacking.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 9/20/07, 3:54 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How scary is this?

I fail to find anything obviously wrong. The cantilever is tiny, and in fact isn't even a cantilever, so the loads on the posts are also minuscule. There would have to be a lot more information available in order to evaluate it any further.
Reply With Quote
  #4  
Old 9/20/07, 4:20 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: How scary is this?

Quote:
Originally Posted by Richard A. Hetzel
I fail to find anything obviously wrong. The cantilever is tiny, and in fact isn't even a cantilever, so the loads on the posts are also minuscule...
Richard, can you elaborate a little?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #5  
Old 9/21/07, 1:20 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How scary is this?

Okay. The overhang appears to be four feet wide. Half of the floor load on that four feet is carried by the log/beam across the front of the house. If we use a design total load of 50 PSF, and assume the house is 20 feet wide, the log/beam carries 2,000 pounds design floor load plus the weight of the wall above. Half of that is 1,000 pounds which is the design load on each of the two posts, ignoring the weight of the wall. The posts appear to be eight inches in diameter, which is far in excess of what would be required for the design load.

A normal wall weighs about 10 pounds per square foot. Maybe the log wall weighs, what? 30 pounds? At an average height of maybe 11 feet, that's another 330 pounds per foot on the beam, or another 6600 pounds. Thus, the weight of the wall is far greater than the floor load, and that brings the total load on each column to 4300 pounds. I'm not going to do the column calculation; I'll just state an opinion that the column can carry much more than 4300 pounds.
Reply With Quote
  #6  
Old 9/21/07, 11:22 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: How scary is this?

Excellent Richard, thank you.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 9/22/07, 2:09 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: How scary is this?

Kenton,
What would you guesstimate the cantilevered section weights? Id imagine just the outside wall alone is pretty impressive. We are not talking kiln dried 2X4's here, but whole logs. Is there such a calculation?


**EDIT** I guess I should have read further down, Richard tackled this in his post.

On a side note, it looks like they were doing a pretting good job at filling in the checking at the log ends.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681

Last edited by pdoane; 9/22/07 at 2:13 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Scary story wsiegel Miscellaneous Discussion for Inspectors 5 8/26/07 9:44 PM


All times are GMT -4. The time now is 9:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts