Here's the deal. Manufactured home (i.e. mobile home) on a 9.5 ft tall, 60 ft. long block wall foundation. The front wall is leaning and shifted inward.
Look at the photos of how the home is secured to the foundation. Just for point of reference, the wood sill plate is secured to the mobile home with screws attaching it the the steel frame. The wood is attached to the block foundation with anchors set in mortar filled into the hollow of the block. The anchor is attached to a strap that is loosely wrapped around the sill and fastened with screws (like decking screws?) and a few random nails. What is your take on this. |
|
#2
|
||||
|
||||
|
Quote:
Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#3
|
|||
|
|||
|
Please Note:
cceccarelli is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just so you know, in my report I did refer this whole situation to a structural engineer.
There's more to the story than I told though. The owner called the company that set the home on the foundation. The mobile home setting company said they fastened the home to the foundation to Michigan code. Michigan code or not, what's your take on the method and workmanship they used. |
|
#4
|
||||
|
||||
|
Please Note:
rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
See Sections 6 and 7 in this: http://www.michigan.gov/documents/dl...k_145096_7.pdf See Part 6 in this: http://www.state.mi.us/orr/emi/admin...Dpt=CI&RngHigh= Approved tiedown assemblies http://www.michigan.gov/documents/dl...s_137165_7.pdf |
|
#5
|
|||
|
|||
|
Please Note:
cceccarelli is a non-member guest and is in no way affiliated with InterNACHI or its members.
Ron,
I reviewed the documents you referenced. They're not descriptive enough to use. The document references back to local code and the manufacturer instruction for tie downs. The strap for this home was fastened with decking screws and wasn't wrapped tightly. Screws don't have much shear force strength. I think the strap should have been wrapped tight around the wood sill and fastened with sufficent sized nails. |
|
#6
|
||||
|
||||
|
Please Note:
rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is no way that installation is an approved manufacturer installation. There is no way that they used one of the approved tiedown systems in the list. Let them prove that one or both of those statements are false.
|
|