hello.
i have a few questions about codes for single story res. construction. this will likely get long.

a little history:
i design and build dental offices here in CA, and have been doing this for quite some time with great success.
i have also drawn a number of plans for minor single story residential remodels as well as having been on the field for 20+ years for the construction.
in other words, i am not new to this.

at this time, i am doing an addition on my own residence. this makes this particular job a bit more personal. i am currently having some difficulty with plan check in my town. it seems that there are some differing interperitations of the code.

i am adding on apx. 450 s.f. to my 1100 s.f. home.
the addition concists of adding a master bedroom/bathroom/closet, and extending the living room apx. 5 feet.

now, one of the first issues is shear panel for the new bedroom area.
LA has created these type V sheets to help owner builders in making their drawings comply with code. there seems to be a discrepency in the type V sheet, and the actual code.

the type V sheet has a drawing of "alternate bracing" referring to cbc 2320.11.4 but it has in parentheses that this is for 1 story "u" occupancies only. now the same code number from the code book makes no such reference. rather it states:
Quote:

2320.11.4 Alternate braced wall panels.
Any braced wall
panel required by Section 2320.11.3 may be replaced by an alter-
nate braced wall panel constructed in accordance with the follow-
ing:
1. In one-story buildings, each panel shall have a length of not
less than 2 feet 8 inches (813 mm) and a height of not more than
10 feet (3048 mm). Each panel shall be sheathed on one face with

3
/8-inch-minimum-thickness (9.5 mm) plywood sheathing nailed
with 8d common or galvanized box nails in accordance with Table
23-II-B-1 and blocked at all plywood edges. Two anchor bolts
installed in accordance with Section 1806.6, shall be provided in
each panel. Anchor bolts shall be placed at panel quarter points.
Each panel end stud shall have a tie-down device fastened to the
foundation, capable of providing an approved uplift capacity of
not less than 1,800 pounds (816.5 kg). The tie-down device shall

be installed in accordance with the manufacturer.s recommenda-
tions. The panels shall be supported directly on a foundation or on
floor framing supported directly on a foundationwhich is continu-
ous across the entire length of the braced wall line. This founda-
tion shall be reinforced with not less than one No. 4 bar top and
bottom.
there is no mention of "u" occupancy in the book.
so which is correct? i would immagine the book.




now, onto another bit of confusion on the subjet of shear.

referring to the cbc 2320.11.3 on the type V drawings provided by the city, there is showing a 4' shear pannel on each and every corner of a square box. the shear is shown right on the corners in each direction.

this makes no sence to me, as i am sitting in front of a window right now that is in the very corner of my room as i type this.

the plan checker has interpereted this sketch as the law. he is not allowing me to have a window, or door within 4' of any corner of the room being added.
i have a huge problem with this as it completely ruins the design of the room. it forces me to remove one window, move another into the shower, and shrink another by almost half.

again, i refer to the code book for the same code number: cbc 2320.11.3
and this is how it reads:

Quote:

2320.11.3 Bracing.
Braced wall lines shall consist of braced
wall panels which meet the requirements for location, type and
amount of bracing specified in Table 23-IV-C-1 and are in line or
offset fromeach other by notmore than 4 feet (1219 mm). Braced
wall panels shall start at notmore than 8 feet (2438mm) fromeach
end of a braced wall line. All braced wall panels shall be clearly

indicated on the plans. Construction of braced wall panels shall be
by one of the following methods:
1. Nominal 1-inch by 4-inch (25 mm by 102 mm) continuous
diagonal braces let into top and bottom plates and intervening
studs, placed at an angle not more than 60 degrees or less than
45 degrees fromthe horizontal, and attached to the framing in con-
formance with Table 23-II-B-1.
2. Wood boards of
5/8-inch (16 mm) net minimum thickness
applied diagonally on studs spaced not over 24 inches (610 mm)
on center.
3. Wood structural panel sheathing with a thickness not less
than
5/16 inch (7.9mm) for 16-inch (406mm) stud spacing and not
less than
3/8 inch (9.5 mm) for 24-inch (610 mm) stud spacing in
accordance with Tables 23-II-A-1 and 23-IV-D-1.
4. Fiberboard sheathing 4-foot by 8-foot (1219 mm by 2438
mm) panels not less than
1/2 inch (13 mm) thick applied vertically
on studs spaced not over 16 inches (406 mm) on center when in-
stalled in accordance with Section 2315.6 and Table 23-II-J.
5. Gypsum board [sheathing
1/2 inch (13 mm) thick by 4 feet
(1219 mm) wide, wallboard or veneer base] on studs spaced not
over 24 inches (610 mm) on center and nailed at 7 inches (178
mm) on center with nails as required by Table 25-I.
6. Particleboard wall sheathing panels where installed in ac-
cordance with Table 23-IV-D-2.
7. Portland cement plaster on studs spaced 16 inches (406 mm)
on center installed in accordance with Table 25-I.
8. Hardboard panel siding when installed in accordance with
Section 2310.6 and Table 23-II-C.
Method 1 is not permitted in Seismic Zones 2B, 3 and 4. For
cripplewall bracing, seeSection 2320.11.5. ForMethods 2, 3, 4, 6,
7 and 8, each braced panelmust be at least 48 inches (1219mm) in
length, covering three stud spaces where studs are spaced
16 inches (406 mm) apart and covering two stud spaces where
studs are spaced 24 inches (610 mm) apart.
ForMethod 5, each braced wall panelmust be at least 96 inches
(2438 mm) in length when applied to one face of a braced wall
panel and 48 inches (1219 mm) when applied to both faces.
All vertical joints of panel sheathing shall occur over studs.
Horizontal joints shall occur over blocking equal in size to the
studding exceptwherewaived by the installation requirements for
the specific sheathing materials.
Braced wall panel sole plates shall be nailed to the floor framing
and top plates shall be connected to the framing above in accord-
ance with Table 23-II-B-1. Sills shall be bolted to the foundation
or slab in accordance with Section 1806.6. Where joists are per-
pendicular to braced wall lines above, blocking shall be provided
under and in line with the braced wall panels.

now i realize some of these methods do not apply to my seizmic zone, but i am reading this in a way that indicates the fact that the beginning of the shear pannel must be within 8' of the corner, and the next piece within 25' of that one.

am i interpereting this correctly?

i have no problem over building this thing as it is my own house. i do have a problem with being told i cant have a window or door within 4' of a corner.

more to come:
Reply With Quote
  #2  
Old 12/19/06, 5:46 PM
Erik W. Jordan Erik W. Jordan is offline
New User
 
Join Date: Dec 2006
Location: Los Angeles
Posts: 3
Please Note: Erik W. Jordan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: single story res. in CA

sorry to hit you guys with so much at one time. please be patient with me.

the next issue is the extention of the living room by 5'.

the way i handeled this is to remove the 23' living room wall, and support the existing ceiling, and roof framing with a parallam beam 5.25x16" which was engineered suitable for the weight and deflection by a weyerhauser engineer.

the existing roof is 3:12 with 3 tab shingles in an area with littl to no rain and no snow.

the existing ceiling members (2x4) are attached to the parallam with simpson 2x4 hangers on each member. the same for the roof members. each one gets a hanger to the face of the parallam.

now on the new side of the parallam, each ceiling member gets the same treatment. 1-2x4 hanger for each member.
the 2x6 roofing members will now run from the new wall over top of the parallam to create a 2.5:12 shedding type roof.

i sure hope this makes sence. i'll get some detail pics up soon.

now, bear in mind that there is a contnuous footing under this parallam, as there once was a bearing exterior wall in its same location. the footing is a minimum 12"x12"x24'.
there is a question in the mind of the plan checker as to the adequacy of this footing for the load of the parallam.

the parallam is supported on each end of its 23' length by a 4x6, and the appropriate simpson post cap.

please advise me here. am i wrong on this one, or is the plan checker thinking too much into it?

to top it off the plan checker i was working with was either fired or quit. so now i have to start over with a new one. what makes it worse is that the new one is following the previous checkers red lines no matter how off base they are.
compound that with the fact that there is only one plan checker in the building and no one to supercede him, i am in a bit of a quandry.

if anyone has any insight on my problem, please help me. i am very anxious to get this thing moving.

i know i pretty much dropped a bomb on anyone willing to read this LONG post, but would be very much appreciative of any insight.
thank you,
Erik
Reply With Quote
  #3  
Old 12/19/06, 6:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: single story res. in CA

I think the problem is that you're relying too heavily on "boiler-plate" drawings from the city/township. These are used when a homeowner is making additions without the benefit of hiring a structural engineer, and using conventional methods of framing and shearpaneling.

There are engineered systems that can be used to replace conventional shear walls, but they must be approved by a state licensed SE (the city will not do this for you).

Without this "enhanced" design approval, you are stuck with the boiler-plate drawings. The "plan-checkers" allow very little wiggle room unless there's an engineer willing to take the liability.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/19/06, 7:20 PM
Erik W. Jordan Erik W. Jordan is offline
New User
 
Join Date: Dec 2006
Location: Los Angeles
Posts: 3
Please Note: Erik W. Jordan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: single story res. in CA

arent the plan checkers still required to follow the specifications laid out by the code book? for example the shear pannel starting within 8' of the corner?
even the boiler plate drawing shows this. he is making his own rules requesting the pannels be on each corner.
Reply With Quote
  #5  
Old 12/19/06, 8:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: single story res. in CA

Only if there is no alternate, engineered design.

Conventional methods can be replaced by engineered designs. Simpson makes steel shearwalls to replace conventional-lumber shearwalls, and they don't require the same width to develop the same strength. However, they do require a different footing and hold-down design.
Attached Thumbnails
single-story-res-ca-sitelines1.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 12/20/06, 8:20 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: single story res. in CA

I allways knew that I voted for the right answer guy.

Jeff, I good not have explained this situation any better than you did.

Good job as usual.

Keep it up.

Marcel
Reply With Quote
  #7  
Old 12/20/06, 8:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: single story res. in CA

Thanks Marcel



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 12/27/06, 2:36 AM
ccoombs's Avatar
ccoombs ccoombs is offline
Active Poster
 
Join Date: Jul 2004
Location: Corona, CA
Posts: 121
Please Note: ccoombs is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: single story res. in CA

I agree with Marcel!

Erik – you stated that you are in L.A. The code items you quoted are from the CBC. The California Building Code is a variation of the Uniform Building Code. However, the city of L.A. has the L.A. City Building Code and the county has the L.A. County Building Code. Each jurisdiction is allowed to require additional items above a beyond the minimum code that the state requires. Both the city and county of L.A. have made major changes to the code. These changes are so significant that I know some engineers that refuse to do work in these jurisdictions.

As to your question regarding the windows in the corners: the existing house was built under a different code or with engineered plans or both. Every addition to an existing house has to meet the current code. If the required changes are too much, then I would suggest hiring an engineer.

As to the footing, the plan checker is correct. Unless you hire an engineer to do a soils report, the maximum assumed allowable soil pressure is 1,000 psf. With a 12” wide x 12” deep footing your maximum allowable point load is just over 3,000 lb. That is a very light point load for a 23’ long beam. Check the beam calcs reaction.

Most building departments won’t accept plans unless they have an engineer’s stamp.

I provide structural engineering for residential projects, so feel free to call our e-mail if you need any additional help.

Curtis
Sterling Engineering
curtis@sterlingengineering.net
951-737-9400

Last edited by ccoombs; 12/27/06 at 2:41 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single wall into B vent question sspradling Inspecting HVAC Systems 1 5/31/07 2:04 PM
Single lever washing machine valve phinsperger Plumbing Inspections 2 1/8/07 10:13 PM
Single system inspection mmasney Canadian Inspectors 5 11/18/06 10:37 AM
Realtor Story - Warm Fuzzy mlong Miscellaneous Discussion for Inspectors 9 2/3/06 9:06 AM