Quote:
Kenton, I do not disagree. However, if shims are not under the bottom of the I-joist the full load is transfered through the surface area of the 2x4" block ends. The top of the block, being met by the particle board sheeting could push its way through the sheeting because the load in this area is not shared by neither the top nor the bottom of the engineered I-joist. I realize at this point (and not before) that the blocks are there because a bearing wall is just above, so the top of the sheeting is pressed into the bottom plate of the bearing wall by the block. And, the bottom of the blocks now distribute the weight from the bearing wall above to the outermost edges of the support beam/post/etc. When shims are used the weight is evenly distributed across the top of the sheeting and the top of the beam/post/etc as the engineer intended. Further, the manufacturer of the I-joist compile their span specification with the intent that the bottom of the I-joist will be stressed in compression at this point - without the shim the bottom is stressed in tension, a very different scenario than the manufacturer intended. I would fear unanticipated lift of the ceiling joist at the top of the bearing wall and perhaps distortion of roof line. Right? This, I believe, is why a maximum of 1/16" is specified when the block is cut. |
|
#32
|
|||
|
|||
|
Please Note:
tmels is a non-member guest and is in no way affiliated with InterNACHI or its members.
Kenton you are correct
If there is something wrong here it is that the beam was installed lower than the exterior walls. Because these joists do not come with crowns in them they are strait. If the beam was installed at the correct height everything would look the way it is supposed to. |
|
#33
|
|||
|
|||
|
Please Note:
dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Robert, Thanks for the informative link. Curiously, it specifically states, 1) that the squash blocks are not intended to replace blocking along the length of the load bearing wall, rather intermittently to allow passage of duct work; and 2) the 1/16" extens above the top of the I-joist cord (NOT the bottom.) From this article and the pitcures at the beginning of this post, I would note that two inappropriate conditions exist. |
|
#34
|
||||
|
||||
|
Quote:
Note that for certain I-Joists and light loads, some manufacturers don't specify squash blocks. Even in those cases I still think it is considered good practice to have squash blocks at any bearing wall locations whenever there isn't solid blocking. JMO & 2-nickels Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#35
|
|||
|
|||
|
Please Note:
dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The only thing left that is yet a thorn in my side is the extreme gap at the bottom of the I-Joist. I just cannot believe that it is okay to be contrary to recommended practice. If any of you live close to a Trust Joist EWP plant (or another mfg.) it would sure be nice to get their final word. On the other hand, I can e-mail the question. </IMG> |
|
#36
|
||||
|
||||
|
Yep. That wall should have solid blocking to uniformly tranfer the load to the beam. The squash blocks create a series of point loads. It's a squirrely situation because if the downstairs wall is supposed to pick up the load from a bearing wall above, you'd expect to see joists resing on that wall.
|
|
#37
|
|||
|
|||
|
Please Note:
dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Well said. |
|
#38
|
||||
|
||||
|
Actually, the purpose of the squash blocks is to transfer load from a bearing wall above to the girder. The bearing wall bottom plate and sheathing transfers stud loads to the squash blocks. That usually works fine as long as jack studs for large openings or posts are directly supported by joists (or blocking where it falls between two joists).
It looks like an unfinished basement, so solid fireblocking wouldn't be required. But blocking or some other means to prevent rotation of the joists is required at ends. However that blocking is usually not "jam fit", so the load is primarily transfered through the squash blocks even when there is solid blocking. Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
![]() |