Default Stabil bracing system

I inspected a home that had a basement system company do a repair to a wall. I attached some photos. The company warranties the wall for foundation & moisture. They did replace the exterior drainage and appears they did exterior excavation on this wall.

I thought the stabil braces where inadequate & told the home owner to monitor condition & contact contractor if wall moves.

What do you think of the braces?
Also they used a thin sheet of material on the interior wall. Is this a newer type of epoxy system?

Thanks

Dave

Last edited by dmacy; 11/20/07 at 6:39 PM..
Reply With Quote
  #2  
Old 2/7/06, 2:58 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stabil bracing system

Dave,
The same company must have done this job. I too feel the braces are inadeqate. As you can see this one is bent or bending.
Also what type of strength could be gained by bracing it against the side of a floor joist?
They buyer said this had a lifetime warranty, I told her to get the paperwork call the company and make sure it is transferrable.

Steve
Attached Thumbnails
stabil-bracing-system-wallbrace.jpg   stabil-bracing-system-wallbrace-2-.jpg.jpg
Views:	98
Size:	61.3 KB
ID:	1107   stabil-bracing-system-wallbrace3-2-.jpg.jpg
Views:	115
Size:	75.5 KB
ID:	1108  
Reply With Quote
  #3  
Old 2/7/06, 3:01 PM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 531
Default Re: Stabil bracing system

looks inadequate to me, do you have any floor to ceiling pictures.

CJ
Reply With Quote
  #4  
Old 2/7/06, 6:03 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Stabil bracing system

I've never seen anything like this.

Can you post pics of the entire length of this set-up?

What is it?
Reply With Quote
  #5  
Old 2/7/06, 6:53 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Stabil bracing system

I dont have a picture of the whole setup.

It hard to explain. I dont like the interior bracing. It does nothing for the top portion of the wall.

There are 2 interior braces both anchored at the base. At the top you can see how they attached to the sub floor.

the top portion of the wall is where the movement is. The braces are not doing anything for that area of the wall.

There is a lifetime transferable warranty on this system.

At least they did some exterior work to release the pressure from the wall.

I think the wall braces are worthless.

Dave
Reply With Quote
  #6  
Old 2/7/06, 6:56 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Stabil bracing system

Quote:
Originally Posted by dmacy

I inspected a home that had a basement system company do a repair to a wall. I attached some photos. The company warranties the wall for foundation & moisture. They did replace the exterior drainage and appears they did exterior excavation on this wall.

I thought the stabil braces where inadequate & told the home owner to monitor condition & contact contractor if wall moves.

What do you think of the braces?
Also they used a thin sheet of material on the interior wall. Is this a newer type of epoxy system?

Thanks

Dave
System appears inadequate.

Structural repairs generally require an evaluation that will include recommendations / drawings to be followed when making the structural repair. Without documentation supporting the repair, the system would need further engineering evaluation at this time.

Telling the Client "...monitor condition & contact contractor if wall moves..." could present potential Liability. If the Wall moves again, it will be too late. The expectation of the Client will then be for you to pay the cost of repair.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/7/06 at 9:29 PM..
Reply With Quote
  #7  
Old 3/19/06, 9:37 PM
wtrprfr1 wtrprfr1 is offline
New User
 
Join Date: Mar 2006
Posts: 8
Please Note: wtrprfr1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stabil bracing system

Just to let you guys know, the basement waterproofing industry has a horrible reputation. The industry is run with commision salesman, that in many instances, will say or do anything to get the deal. The guarantees these companies provide are usually only for seepage. Go to my websight and read the important information page. This will help you advise your clients on how this industry works.

www.integritywaterproofing.com
Reply With Quote
  #8  
Old 3/20/06, 6:45 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Stabil bracing system

wtrprfr,

Nice site. You design a basement waterproofing system that resembles a B-dry system in my area. I recommend this sort of waterproofing system on many fieldstone foundations.

www.bdry.com

It's expensive but it works.
Reply With Quote
  #9  
Old 3/20/06, 11:20 AM
ccoombs's Avatar
ccoombs ccoombs is offline
Active Poster
 
Join Date: Jul 2004
Location: Corona, CA
Posts: 121
Please Note: ccoombs is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stabil bracing system

I would say they are doing absolutely nothing structurally. I would be contacting state agencies looking for other complaints regarding this system. I'm not sure what your state requires, but I would be asking for engineering to back up the fix provided (If they have paper work saying it works, I wouldn't believe it).

Last edited by ccoombs; 3/21/06 at 2:03 AM..
Reply With Quote
  #10  
Old 3/21/06, 1:57 AM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stabil bracing system

Very amateurish,err I mean non-standard.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 11:02 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts