Default Re: Steel post question

For those who want the link to the ASHI member who wrote that:

http://www.octoberhome.com/articles/...ustcolumn.html

There are numerous great articles out there by this author.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #17  
Old 2/15/07, 10:38 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Steel post question

Attended a NACHI structural class earlier this week. The engineer didn't say anything about the adjustable columns being "temporary". He did say that the maximum exposure of the threads shouild be no more than 3 inches.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #18  
Old 2/15/07, 10:58 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

Quote:
I don't consider it a big deal if a support post is missing 2 bolts. It's not going anywhere with all that weight bearing down on it.

Most manufacturers state that all holes (in their brackets) must be utilized, but use your own discretion.
Thanks David. I might just buy a few bolts then. Should be an easy fix.
Reply With Quote
  #19  
Old 2/18/07, 4:46 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

The unacceptable temporary supports posts generally have telescoping sections, in addition to the screw adjustment. Adjustable steel columns are permitted if they are the permanent type (no telescoping sections) and about at least 11 gage steel. And most manufacturers now allow either screws up or down, which I don't think is an issue (that is if attached at the ends correctly) ... although many builders think it's good practice to embed the threads in the slab or damage the threads if at the top.

See 2.2 of following ICC approval report, as well as typical details at the end ... http://www.icc-es.org/reports/pdf_files/BNBC/94-54.pdf

Note that steel columns for new construction need to be 3" nominal diameter Sch-40/Std weight (3-1/2" OD & 0.216" thick) per IRC R407, or they need special ICC approval with a stamp on the column.

Note that "Lally Column" refers to an older trade name very thin steel pipe (16 - 18 gage) that needed to be filled with concrete for capacity. Very susceptible to moisture and rust (e.g. leaking basement), that could significantly compromise the stability. Many just refer to any steel column as a "Lally Column" (similar to the brand name "BX" armored elec cable, which also isn't made any more). And around here, steel columns are not filled with concrete any more. Generally a waste with the thicker steel required now.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 2/19/07 at 9:21 PM..
Reply With Quote
  #20  
Old 2/18/07, 4:58 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

P.S. And having a maximum of 3" of exposed threads is recommended for stability ... although not required by many screw column manufacturers (e.g. 6-1/2" of exposed threads max per 3.3 of the above ICC sample report I linked ... which is a lot in my opinion ... )



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #21  
Old 2/18/07, 7:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Steel post question

Quote:
Originally Posted by badair
Write these or similar up. They are not intended as permanent structural supports no matter what their size is.

I posted a jack like this in a post I said I wrote up and everyone said the jack was fine.....I said NOT....wrote it up.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #22  
Old 2/18/07, 11:12 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

Quote:
Originally Posted by pabernathy
I posted a jack like this in a post I said I wrote up and everyone said the jack was fine.....I said NOT....wrote it up.
Do ya have a pic. On the surface I think you made the right call Paul, as that does indeed look like the telescoping temporary type posts ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 2/19/07 at 9:19 PM..
Reply With Quote
  #23  
Old 2/22/07, 12:42 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Steel post question

Robert, by "telecscoping" are you talking about an additional threaded section toward the middle of the column somewhere (never seen) or a column that uses pins to hold the two sections in place after it's been rough adjusted, then uses a threaded section near one end to make final adjustments?

What's the verdict here. If I walk into a basement and see an adjustable column 3 inches or more in diameter, with 3 inches (or 6 1/2 inches) or less of exposed thread, do I then have to find a stamp on the column certifying it for permanent use?

Good article Marcel!




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #24  
Old 2/22/07, 7:00 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Steel post question

Quote:
Originally Posted by kshepard
What's the verdict here. If I walk into a basement and see an adjustable column 3 inches or more in diameter, with 3 inches (or 6 1/2 inches) or less of exposed thread, do I then have to find a stamp on the column certifying it for permanent use?
Kenton,

I call out all telescoping support posts as temporary posts, whether it displays a stamp or not. And the thread length is not a deciding factor for me.

Telescoping support posts get written up as "Recommend replacing temporary support posts with cement filled lally columns.
Reply With Quote
  #25  
Old 2/22/07, 11:34 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

In my opinion all telescoping type steel posts should be flagged for further evaluation and possible replacement.

Even if it has an approval stamp, is that approval for temporary shoring or for a permanent steel column? What are the approval restrictions? One type is limited to a height of 51" when used as a permanent column. You would have to research the approval, or just flag it and move on.

Also I wouldn't call out how to repair it ... as for example concrete filled steel columns are not used in many areas any more in typical construction, and may not be needed unless loads are very heavy.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #26  
Old 2/23/07, 12:38 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Steel post question

I'm convinced.

"Temporary adjustable steel supports should be replaced with permanent supports which comply with applicable codes".




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #27  
Old 2/23/07, 12:52 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: Steel post question

Wow...great information everyone...I didn't realize all of these were "temporary"...here in Minnesota, virtually every house with a basement has at least one of these...I've seen as many as twelve...We have a preponderance of homes over 100 years old here...many are three story Victorians..."stick-built", brick, stone, you name it...with most on stone foundations...fantastic homes, but after 100 years...some of these foundations get pretty scarey !!!
Reply With Quote
  #28  
Old 3/1/07, 12:26 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

The thing i hate about being a home inspector is knowing exactly what to callout. For an example here with telescoping posts. I read this thread a couple of days ago and when on an inspection today and came across a raised ranch home with a main wood beam down the center supported with telescoping steel poles with 4"-5" thread exposed on top and the base was below the concrete basement floor. I found no stickers on the post for it's use, so the big question here is....

The home has been standing there for 30 odd years, Do I call this out and say their only designed for tempory supports???? I hate that there are so many opinions in this field, so confusing, What should we all be stating when finding this in the feild as Home Inspectors

(I was looked at as a wacko by the home owner and the realtor for even saying something about the columns)
Reply With Quote
  #29  
Old 3/1/07, 3:13 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

You guys need to take small risks (rather than no risks, which is impossible) and use a little discretion.

You are only on the line if it fails, or if someone else thinks it will fail. What is the risk of it failing? Are you more likely to be hit by a bus, or do you really think it poses a threat?

And what is the cost if it does fail? Big...report it. Small....why bother?

So risks*costs

My HI overlooked many small issues that violated code, but did highlight the biggies.

Last edited by Ian Gills; 3/1/07 at 3:22 PM..
Reply With Quote
  #30  
Old 3/1/07, 5:04 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: Steel post question

Fantastic article, Marcel...I learned alot...I see these columns everyday...everybody has their own opinion about them...Thanks !!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 12:50 PM
Where's NACHI on this Website? lcapaul General Inspection Discussion 77 7/31/07 5:00 PM


All times are GMT -4. The time now is 9:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts