Thumbs down Re: Steel post question

I have always advised my clients about these temp posts, they have, as far as I know, some that are rated up to 1200 lbs, but that is no where near enough for a structural load. And any column that supports a substantial load, should be "permanently mechanically attached" both bottom and top, I spotted some in a state of failure just the other day, many have a top plate that pivots, no way jose!!



Mike Nelson CPI, CMI
NYS License # 16000005765


(Just because you understand how something is built, in no way prepares you for the innumerable insults a human being can heap upon a domicile)
Reply With Quote
  #32  
Old 3/1/07, 5:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Steel post question

Quote:
Originally Posted by mnelson1
I have always advised my clients about these temp posts, they have, as far as I know, some that are rated up to 1200 lbs, but that is no where near enough for a structural load. And any column that supports a substantial load, should be "permanently mechanically attached" both bottom and top, I spotted some in a state of failure just the other day, many have a top plate that pivots, no way jose!!
Any pictures Mike? We like pictures.

Thanks again for the instruction in Denver last weekend.
Reply With Quote
  #33  
Old 3/1/07, 5:39 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

Well, kinda' makes the point that "functioning as intended" can be a pretty slippery concept.

The contractor who installed the telescoping column intended that it support the girder - and it's done so for 30 years, and probably would do so for 30 more (or for that matter, for 300 more).

So it's" functioning" as intended", and most contractors are going to advice a client to leave it as it is.

The manufacturer however did not intend the column to function as a permanent support, so it's not functioning as the manufacturer intended, and an engineer is probably going to say (if only to CYA) that it should be replaced with a support intended this the use and location.
Reply With Quote
  #34  
Old 3/1/07, 5:56 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Steel post question

If you're not sure, and you get conflicting information when you ask... you can err onthe side of safety and add a disclaimer alongside the narrative describing whether or not you saw evidence of failure. If it were easy... well, that's why we get $10 and hour and everyone else only gets $9.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #35  
Old 3/1/07, 7:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Steel post question

Quote:
Originally Posted by kshepard
If you're not sure, and you get conflicting information when you ask... you can err onthe side of safety and add a disclaimer alongside the narrative describing whether or not you saw evidence of failure. If it were easy... well, that's why we get $10 and hour and everyone else only gets $9.
Kenton, can I bid $12 an hour to come up and work for me?
That would not include commuting. Sorry.

Marcel
Reply With Quote
  #36  
Old 3/1/07, 7:18 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

The manufacturer however did not intend the column to function as a permanent support, so it's not functioning as the manufacturer intended, and an engineer is probably going to say (if only to CYA) that it should be replaced with a support intended this the use and location.


Where would I get such information when I come across this in the field. To call something like this out at time of inspection, could be a major situation with all parties.(REALTOR, SELLER, and your client) If there is no lable on post then I need something for my files to pull out that states legally that the telescoping posts are not right for the application???????????????
Reply With Quote
  #37  
Old 3/1/07, 8:04 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

If the article cited above is correct, if it's a telescoping post, it's not intended for permanent installation.
Reply With Quote
  #38  
Old 3/1/07, 9:01 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel post question

OK 1 last question then I get off this topic. I was told by another inspector that stating a finding like this is outside the scope of a home inspection, and do not need to report something like this. My question is, are we as professional inspectors to 1.call it out and document it, or 2.just document it in the report, or 3.don't have to say or document again thing. Please I'd like to know the proper way to do things in this industry, not how another inspector might do it but what should be done. Thanks and I will conclude with this.
Reply With Quote
  #39  
Old 3/2/07, 12:51 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

Quote:
Originally Posted by brepanshek
I was told by another inspector that stating a finding like this is outside the scope of a home inspection, and do not need to report something like this.
A visual inspection of exposed framing and supports is part of a home inspection, so I disagree with that position (as long at it's visible).

You should look to see if any visible framing and supports looks solid with no obvious deterioration as part of a home inspection. And if you see any steel supports that are the telescoping type, or looks to be a temporary screw jack like the one with a pivoting top, and/or do not have adequate attachment and support at the top or bottom (e.g. permanent steel post just resting on a slab) then it should get flagged for further evaluation.

It is beyond a home inspection (and would cross PE licensing laws) to comment on the adequacy or suitability of any members or supports.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #40  
Old 3/2/07, 3:29 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Steel post question

Quote:

2.3. Basement, Foundation & Crawlspace
I. The inspector shall inspect:
A. The basement.
B. The foundation
C. The crawlspace.
D. The visible structural components.
E. Any present conditions or clear indications of active water penetration observed by the inspector.
F. And report any general indications of foundation movement that are observed by the inspector, such as but not limited to sheetrock cracks, brick cracks, out-of-square door frames or floor slopes.


II. The inspector is not required to:
A. Enter any crawlspaces that are not readily accessible or where entry could cause damage or pose a hazard to the inspector.
B. Move stored items or debris.
C. Operate sump pumps with inaccessible floats.
D. Identify size, spacing, span, location or determine adequacy of foundation bolting, bracing, joists, joist spans or support systems.
E. Provide any engineering or architectural service.
F. Report on the adequacy of any structural system or component.

Nice call Robert.
Reply With Quote
  #41  
Old 3/2/07, 5:13 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Steel post question

There's nothing wrong with recommending upgrades or repairs.
Reply With Quote
  #42  
Old 3/2/07, 5:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Steel post question

Quote:
Originally Posted by dvalley
There's nothing wrong with recommending upgrades or repairs.
I agree.

Marcel
Reply With Quote
  #43  
Old 3/2/07, 8:59 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Steel post question

Quote:
Originally Posted by dvalley
There's nothing wrong with recommending upgrades or repairs.
In the case of adjustable columns you really need to do some research and check the listing/approval and do some rough calcs in order to make a correct call.

Some are approved for heights as little as 4' and others are approved for heights up to like 9' ... some of the ones with approvals for 7' to 9' have a higher capacity, and some have a much lower capacity which may not work for even supporting one level at typical column spacing. It really depends on the steel thickness and configuration. There is no way to definitively tell just doing a visual examination.

If you recommend upgrades/repairs where they may not be needed and the client gets a second opinion from an engineer (I have done a number of them where it was just flagged to have it looked at), or a savvy contractor who is not just out to milk them and knows what conditions the particular type is okay for, you could end up with egg on your face.

So for an HI it's my opinion the best course of action with suspect adjustable columns is to flag it for further evaluation ... and if you feel strongly about it you can always flag it for evaluation by an SE and also recommend budgeting for repairs.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 3/3/07 at 11:44 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 11:50 AM
Where's NACHI on this Website? lcapaul General Inspection Discussion 77 7/31/07 4:00 PM


All times are GMT -4. The time now is 11:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts