Default structuaral problems

Brand new three story town home today. It is the builders model unit. On the third floor there are two doors out of square (settlement cracks at the top of both the doors). The floors to both stall showers have sunk about an eight of an inch, large enough for me to stick a thin metal ruler under an poke back to the pan. The window sills have lost their seal in the corners. This is only on the third floor. The other two floors show no problems.

Just wondering how some of you would write this up. Something is wrong here, but obviously it cant be seen because i am looking at a finished product. FYI - there is no indication of any problem on the exterior of the unit.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
Find an InterNACHI certified Pennsylvania Home Inspector (and anywhere else in North America)
  #2  
Old 10/22/09, 9:19 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Brand new three story town home today. It is the builders model unit. On the third floor there are two doors out of square (settlement cracks at the top of both the doors). The floors to both stall showers have sunk about an eight of an inch, large enough for me to stick a thin metal ruler under an poke back to the pan. The window sills have lost their seal in the corners. This is only on the third floor. The other two floors show no problems.

Just wondering how some of you would write this up. Something is wrong here, but obviously it cant be seen because i am looking at a finished product. FYI - there is no indication of any problem on the exterior of the unit.
If it is a new home, it should be under warranty from the builder.

Ask the builder to explain the defects on this new building and fix them.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #3  
Old 10/22/09, 9:25 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: structuaral problems

Not a matter of whether it is under warranty or not. My client has to make a decision on to buy or not to buy based on this issue, knowing that it could lead to future problems.

I am leaning toward suggesting that my client get a separate structural inspection, at the builders expense, of course.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #4  
Old 10/22/09, 9:30 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: structuaral problems

Observed signs of movement at a couple of locations and signs of settlement to create cracks above doors.
Recommend a licensed qualified builder to evaluate and repair.

William, since this is the third floor and I am assuming it is all wood frame, it is conceivable that some of those walls are bearing walls and possibly picking up the weight of the roof also.
If some of those walls were framed on the second floor of the house and run parallel to the floor framing, this could cause what you are explaining.
Also some of the walls could be offset to far from bearing walls below.
There are a lot of variables to cause this in a new structure.

Pictures would help.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #5  
Old 10/22/09, 9:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Not a matter of whether it is under warranty or not. My client has to make a decision on to buy or not to buy based on this issue, knowing that it could lead to future problems.

I am leaning toward suggesting that my client get a separate structural inspection, at the builders expense, of course.
There's that course of action and, additionally, you could describe what you noted in post 1 and recommend repairs, as needed, to maintain structural integrity. Hard to tell what is behind walls and floors.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #6  
Old 10/22/09, 9:36 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: structuaral problems

Here are some pictures. FYI- concrete block
Attached Thumbnails
structuaral-problems-362-cannery-row-delray-fink-001.jpg 001.jpg
Views:	63
Size:	88.4 KB
ID:	32767   structuaral-problems-362-cannery-row-delray-fink-010.jpg 010.jpg
Views:	71
Size:	15.4 KB
ID:	32768   structuaral-problems-362-cannery-row-delray-fink-014.jpg 014.jpg
Views:	70
Size:	35.3 KB
ID:	32769   structuaral-problems-362-cannery-row-delray-fink-021.jpg 021.jpg
Views:	71
Size:	17.2 KB
ID:	32770  



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #7  
Old 10/22/09, 9:44 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: structuaral problems

William, the block walls don't affect what I said earlier.
The tile floor gap is minor shrinkage and can be sealed with a silicone to match the grout. This is normal on a wood floor dependant on where it was framed in relation to the span of the floor framing below it.
It could also have been caused by high moisture content in the wood and now it is shrinking.

Like Larry above mention, to make a long story short.
Report what you observed and recommend that it be repaired.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #8  
Old 10/22/09, 11:41 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Not a matter of whether it is under warranty or not. My client has to make a decision on to buy or not to buy based on this issue, knowing that it could lead to future problems.

I am leaning toward suggesting that my client get a separate structural inspection, at the builders expense, of course.
Recommend your client gets a *Mike Holmes inspection*...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #9  
Old 10/26/09, 7:33 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 77
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Not a matter of whether it is under warranty or not. My client has to make a decision on to buy or not to buy based on this issue, knowing that it could lead to future problems.

I am leaning toward suggesting that my client get a separate structural inspection, at the builders expense, of course.
Larry i agree with Marcel, write it and have the builder repair. all of the pictures are of non-bearing interior walls and are exhibiting common shrinkage. on new construction you will see alot of cracking above door openings because the dry-wall hanger will cut the board at that point to start a new full board because of the avalibility of the framing member. more often than not it will not be at the tapered end of the board which prohibits the finisher from properly filling the tape joint with compound. as soon as the airconditioning is turned on and the building begins to dry out (shrink ) the joint cracks. i would not suggest recomending a structural inspection unless you have definitive evidence to suggest a structural fault and are prepared to defend your conclusion with the general contractor, the engineer of record, the speciality design engineer, and the governing jurisdiction, because that building is multi family they all would have just signed off stating that it meets or excedes the design critera. good luck.



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
O.S.H.A. certified
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
Reply With Quote
  #10  
Old 10/27/09, 8:45 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: structuaral problems

Quote:
Originally Posted by mtyson View Post
Larry i agree with Marcel, write it and have the builder repair. all of the pictures are of non-bearing interior walls and are exhibiting common shrinkage. on new construction you will see alot of cracking above door openings because the dry-wall hanger will cut the board at that point to start a new full board because of the avalibility of the framing member. more often than not it will not be at the tapered end of the board which prohibits the finisher from properly filling the tape joint with compound. as soon as the airconditioning is turned on and the building begins to dry out (shrink ) the joint cracks. i would not suggest recomending a structural inspection unless you have definitive evidence to suggest a structural fault and are prepared to defend your conclusion with the general contractor, the engineer of record, the speciality design engineer, and the governing jurisdiction, because that building is multi family they all would have just signed off stating that it meets or excedes the design critera. good luck.
Mark,

did you not read the whole post? Not only are there cracks, but two of the doors will not close. And what about the separation of the shower floors. It also says that this is the model unit, which means the AC has been running the whole time. I do not know how you can make such remarks with the information given.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #11  
Old 10/27/09, 9:20 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Mark,

did you not read the whole post? I do not know how you can make such remarks with the information given.
Quote:
Originally Posted by mtyson View Post
Larry i agree with Marcel,...
Well, he does think I'm you...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #12  
Old 10/27/09, 9:45 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 3,074
Default Re: structuaral problems

I have had 2 inspections in the last week that needed follow up by a structural engineer.

The first house was built in 2005. There was a crack in the garage floor. It was about 1/4 to 3/8 wide, with about a 1/4 inch of differential settlement. Inside the home all of the rooms on that side had cracked drop angles, cracks around window and door headers and the baseboards had separated at least a 1/4 inch. I recommended they obtain the opinion of a structural engineer. The buyer decided to look at other houses after reading the engineer report. My first inspection today is for his next house.

The second house was built in 1959. The garage floor had a crack of 3/4 inch about 6 ft away from the exterior block wall. There was about 3/4 inch differential. The garage had a work area that has a step up. I could see that the floor had sunk at least a half inch towards the exterior wall. I recommended that they obtain the opinion of a structural engineer.

I think you are taking on a lot of risk if you don't recommend that the client obtain an opinion from the expert when there is clear evidence that something is happening.

Bill I would have no problem with telling the client that there is evidence that settlement is occurring and given the number of red flags I would recommend that you obtain the opinion of an expert.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #13  
Old 10/27/09, 9:26 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 77
Default Re: structuaral problems

Quote:
Originally Posted by wsiegel View Post
Mark,

did you not read the whole post? Not only are there cracks, but two of the doors will not close. And what about the separation of the shower floors. It also says that this is the model unit, which means the AC has been running the whole time. I do not know how you can make such remarks with the information given.
Yes I read the entire post, an yes i am painting with a broad stroke, but with the limited info. shown in the pictures it is my opinion that what is occuring is normal movement due to the local industry standard construction practices and not structural defects. I would be willing to wager an icey cold beverage that the problem with the doors is a lack of shims between the jamb and the framing member on the hinge side. as far as the shower goes the gap between the wall tile and the floor tile is a normal occurance and just needs to be filled with sealant. The building is a multi family reinforced masonry structure. meaning that all of the bearing points for the floor and roof systems are attached to reinforced masonry.with no visable signs of faliure on the exterior my experiance tells me that it is safe to to say that the defects are not structural. Remember a building of that size was probably on a 6 month building cycle and the air cinditioning would not have been turned on until after the certificate of occupancy was issued. I have supervised the construction of high rise condominiums as well as over 1500 single family homes here in south fl. so i do have some experiance on local industry standard construction practices, while i'm not condoning not shimming doors but that in itself does not make it a structural defect. I'm not trying to be a know it all or a jerk off i just want you to be certain of your conclussions so that you don't end up with egg on your face or worse in court defending yourself against a slander suit



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
O.S.H.A. certified
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Preventing Moisture related Problems mcyr Ancillary Services & Additional Topics 1 12/19/07 9:30 AM
Tidbits from the ASHI Message Board jbushart Misc. Discussion 124 4/27/07 12:05 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 8:22 PM
CBC - Province called on to force home-sellers to disclose property's problems rwand1 Canadian Inspectors 2 4/5/06 9:40 PM


All times are GMT -4. The time now is 7:07 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts