A few questionable places on this home today. Only a few years old.
The attic gable ends lacked any type of connection along the studs except the gable end rafter. One section of the floor framing only rested on about an inch of girder. This did have good base support. These were questionable to me. Marcel or Tim any thoughts? Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
R502.6 Bearing. The ends of each joist, beam or girder shall
have not less than 1.5 inches (38 mm) of bearing on wood or metal and not less than 3 inches (76 mm) on masonry or concrete except where supported on a 1-inch-by-4-inch (25.4 mm by 102 mm) ribbon strip and nailed to the adjacent stud or by the use of approved joist hangers. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
|||
|
|||
|
Lack of joist hangers is a big one given the improper support of only one inch. Visqueen vapor barrier needs taped and should extend up the stemwall at least 18". Given there are no straps on truss connections, gable end bracing would be a good idea.
www.thebuildinginspector.net William Chandler Licensed Home Inspector #1025 Certified General Contractor #CGC060389 FHA 203(k) Inspector #A0954 Licensed Radon Measurement Technician #R2275 Certified Pollutant Storage Systems Contractor #PCC052624 Certified Underground Utility & Excavation Contractor #CUC057349 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Strong-Drive® SD Screw for Structural Connectors | jjonas | Structural Inspections | 4 | 12/23/09 5:04 PM |
| Need input/example of Structural Report | bwestcott | General Inspection Discussion | 3 | 10/8/09 7:13 AM |
| "A Bridge Too Far" | mcyr | Exterior Inspections | 7 | 12/18/08 5:38 PM |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 3:05 PM |