  #16  
Old 9/14/09, 1:21 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,960
Default Re: Structural engineer anyone?

Quote:
Steel I-beams are similar to an engineered joist. Cuts and holes are allowed in specific locations within the web.
10-4...I wouldn't make an issue of it either, but would note it in the report anyway, as an altered Steel Beam, if the client has concerns let them seek further evaluation if desired.
Reply With Quote
Find an InterNACHI certified Indiana Home Inspector (and anywhere else in North America)
  #17  
Old 9/14/09, 1:30 AM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Structural engineer anyone?

The best place for a hole of that nature in a steel beam is at or near the center of the span. To properly evaluate the beam as it exists now, one would have to know the design loads on the beam, the exact designation of the beam (W10x19, W12x21 etc.), the strength of the steel used, and the span of the beam. The hole may be too big for a fully-loaded beam, but may well be acceptable on a less-than-fully-loaded beam. If the hole is found to be too big, a possible remedy might be to weld plates on either side of the web at the hole location. The length and thickness of the plates would be determined once the beam is evaluated.
Reply With Quote
  #18  
Old 9/14/09, 1:32 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,960
Default Re: Structural engineer anyone?

Quote:
Originally Posted by Richard A. Hetzel View Post
The best place for a hole of that nature in a steel beam is at or near the center of the span. To properly evaluate the beam as it exists now, one would have to know the design loads on the beam, the exact designation of the beam (W10x19, W12x21 etc.), the strength of the steel used, and the span of the beam. The hole may be too big for a fully-loaded beam, but may well be acceptable on a less-than-fully-loaded beam. If the hole is found to be too big, a possible remedy might be to weld plates on either side of the web at the hole location. The length and thickness of the plates would be determined once the beam is evaluated.
Good response Richard,,,!
Reply With Quote
  #19  
Old 9/14/09, 3:07 AM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 681
Default Re: Structural engineer anyone?

Quote:
Originally Posted by Richard A. Hetzel View Post
The best place for a hole of that nature in a steel beam is at or near the center of the span. To properly evaluate the beam as it exists now, one would have to know the design loads on the beam, the exact designation of the beam (W10x19, W12x21 etc.), the strength of the steel used, and the span of the beam. The hole may be too big for a fully-loaded beam, but may well be acceptable on a less-than-fully-loaded beam. If the hole is found to be too big, a possible remedy might be to weld plates on either side of the web at the hole location. The length and thickness of the plates would be determined once the beam is evaluated.
I do believe that a structural engineer is the qualifed person to make this decision, correct?

I found this thread also http://www.nachi.org/forum/f23/steel-beam-boring-20891/
which seems to support the need for a structural engineer.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #20  
Old 9/14/09, 11:13 AM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,997
Default Re: Structural engineer anyone?

Quote:
Originally Posted by mmerino View Post
Thanks Jeff, I will most likely recommend that and engineer take a look, the client was really concerned about it.
There's your answer. Satisfy the client - have a specialist evaluate it.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #21  
Old 9/14/09, 12:29 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Structural engineer anyone?

No question, a structural engineer is the right person to evaluate the beam and its hole. The knowledge and calculations required are probably beyond the expertise of even an architect who knows what he or she is doing.

What counts in the middle of the span is the distance between flanges, where maximum moment probably occurs (if the load on the beam is uniform). The web is least critical at that point except to keep the flanges apart. Loads on the web increase as the supports are neared, and are mostly shear loads.
Reply With Quote
  #22  
Old 9/14/09, 3:10 PM
rmayo rmayo is offline
New User
 
Join Date: May 2006
Location: Rolla, MO
Posts: 3
Please Note: rmayo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Structural engineer anyone?

Michael

I am a SE & HI and the hole in the web is feasible if done properly including design calculations. However the cost to check the design would not be cost effective. It would be cheaper to install one of the newer door openers and weld a plate over the hole in the beam.

PS: here is a web site with information on web cutouts in steel beams:

http://www.steel-insdag.org/new/pdfs/chapter28.pdf
Reply With Quote
  #23  
Old 9/14/09, 5:48 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 13,975
Default Re: Structural engineer anyone?

Discussion of design criteria;

Web penetrations in beams are often a cost-effective means of minimizing the depth of a floor system that contains mechanical or electrical ductwork.
However, if they are numerous and require stiffening, it is probably more economical to eliminate them and pass all ductwork below the beams, if possible. Thus, stiffening at web penetrations should be called for only if required. The use of a heavier beam, a relocated opening, a change in the size of the opening, and the use of current design procedures can often eliminate the need for reinforcement of beam web penetrations. If web penetrations are to be use and stiffening is required, the most efficient and economical detail is the use of longitudinal stiffeners above and below the opening as illustrated in Figure 2. For more information, see Darwin.

Figure 2. Web penetration reinforcement of an I-shaped beam.



http://www.themainehomeinspector.com/
Serving all of Kennebec County and Central Maine
Cyr Home and Commercial Property Inspections

IAC2 Certified
http://co.nachi.org/inachiawards
Inachi 2009 US Member of the Year




Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #24  
Old 9/14/09, 9:43 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 681
Default Re: Structural engineer anyone?

Quote:
Originally Posted by rmayo View Post
Michael

I am a SE & HI and the hole in the web is feasible if done properly including design calculations. However the cost to check the design would not be cost effective. It would be cheaper to install one of the newer door openers and weld a plate over the hole in the beam.

PS: here is a web site with information on web cutouts in steel beams:

http://www.steel-insdag.org/new/pdfs/chapter28.pdf
Thanks for the info. I did recommend the SE to the buyer. It is in his hands now. But, I learned something for the next time. I am going to send him an email with a link to the newer openers.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #25  
Old 9/26/09, 2:09 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 84
Default Re: Structural engineer anyone?

Quote:
Originally Posted by mmerino View Post
This is an automatic recommendation for a structural engineer. They cut the beam, which carries the second floor weight, to fit the garage door opener track. This got me wondering, can you ever cut a steel beam?
yes you can. in my prior life i ran into many instances where the design intent and the structual design conflicted resulting in making field alterations. with that said the cut has to be designed by the mfg. engineer and approved by the engineer of record. i can tell you that in 100% of the time some type of addittional reinforcement would have been welded in place. in the case you are showing i would have expected to see eithe 1/4" or perhaps even 3/8" steel flitch plates welded to one or perhaps both sides of the web at the cut and extend 12' to 16' on each side. refer to engineer for evaluation



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
O.S.H.A. certified
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #26  
Old 10/4/09, 10:30 AM
pmacaulay pmacaulay is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 8
Default Re: Structural engineer anyone?

What did he use,a "can opener"? Is that a wire running thru in the top right of the opening? Don't take any chances, call for further evaluation and cover your ***.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural 3 11/6/07 3:05 PM
Illinios structural engineer jkrumm General Inspection Discussion 1 4/19/07 12:21 AM
Site-built trusses- always recommend a structural engineer? kshepard Structural 21 6/19/06 3:57 PM


All times are GMT -4. The time now is 4:23 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts