Default Structural recommendation

This is an addition. These rafters are attached to the sheathing that is supported by trusses. No obvious structural implications. This is an older home 50+ years. Would you make any recommendations? Have it checked out by structural engineer etc? Thanks everyone. Long live NACHI!
Attached Thumbnails
structural-recommendation-dsc09532-medium-.jpg.JPG
Views:	95
Size:	59.1 KB
ID:	29500   structural-recommendation-dsc09531-medium-.jpg.JPG
Views:	89
Size:	73.9 KB
ID:	29501   structural-recommendation-dsc09529-medium-.jpg.JPG
Views:	89
Size:	43.5 KB
ID:	29502  




Mark Nicholet
Apple Home Inspections LTD
My Blog
CAHPI(BC) Associate member
InterNACHI member
Infrared-Certified
BC Licence # 47592
Reply With Quote
Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America)
  #2  
Old 6/23/09, 12:34 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,762
Send a message via Yahoo to jfunderburk
Default Re: Structural recommendation

It looks exactly like the addition made to my 100+ year old home. Just note that additions have been made, advise them to ensure the work was preformed by licensed contractors.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 6/23/09, 1:37 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,476
Default Re: Structural recommendation

Those are rafters or joists? In either case, they don't appear to be attached to the old roof.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #4  
Old 6/23/09, 1:44 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,762
Send a message via Yahoo to jfunderburk
Default Re: Structural recommendation

Well, with Nick's post, I agree that there is no visible evidence based on the photos that the rafters are attached. Assuming that they are, then my statement stands.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 6/23/09, 7:25 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Structural recommendation

I'm sure that those rafters bear onto the trusses that are below the sheathing.

Simply note the addition and call it a day.
Reply With Quote
  #6  
Old 6/24/09, 1:17 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Structural recommendation

It doesn't look right to me. I'd recommend an upgrade where those rafters are attached, and possibly additional support under that new roof.
If that's a new low slope roof, it should have been 2X6 or better.

Trusses before 1970 would likely be home-built, with plywood gussets.

I also mention the fire safety issue of having asphalt shingles in the attic cavity. Imagine fighting a fire in that house?
Reply With Quote
  #7  
Old 6/26/09, 2:29 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,454
Send a message via ICQ to kshepard
Default Re: Structural recommendation

Quote:
Originally Posted by dvalley View Post
I'm sure that those rafters bear onto the trusses that are below the sheathing.

Simply note the addition and call it a day.
Judging from how nicely the cuts fit that work looks like it was done by a carpenter and bears on framing below the sheathing. There will be one good solid toenail through the tongue (long point) of the slash cut (cut where the rafter rests on sheathing). Probably a couple of toenails through the sides of each slash cut which catch only sheathing unless blocking was installed. Not likely. Typical for what appears to be its age from the photo.
I wouldn't call anything.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #8  
Old 6/26/09, 7:46 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 1,374
Default Re: Structural recommendation

Not enough pictures to tell..........if the rafters are indeed resting of trusses...which I doubt based upon the spacing, 16 inches as opposed to 24 inches on center, AND they are at the peak of the truss I wouldn't think there would be an issue.

Do you have any pictures from the truss side?

Jeff
Reply With Quote
  #9  
Old 6/26/09, 11:21 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,454
Send a message via ICQ to kshepard
Default Re: Structural recommendation

Quote:
Originally Posted by jhaynes View Post
Not enough pictures to tell..........if the rafters are indeed resting of trusses...which I doubt based upon the spacing, 16 inches as opposed to 24 inches on center, AND they are at the peak of the truss I wouldn't think there would be an issue.

Do you have any pictures from the truss side?

Jeff
You got a point there Jeff, the spacing is pretty obvious in photo #1. Since shingle tabs are usually about 12", those rafters can't be more than 16" oc, in fact they look less.

Still, it looks like it's been there a while, and I'd want to see failure before I made a big deal out of it, although now that you've pointed out the spacing, I might mention it as non-standard framing.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #10  
Old 6/26/09, 11:32 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 1,374
Default Re: Structural recommendation

I would rather call it out before failure occurs...........I (and I am sure you as well) have seen framing members being held in place by one nail.........we don't want to end up being the inspector who is explaining himself in court why we missed a serious structural issue.....(I am not saying this is one by the way).

Any alteration or additions onto a home ALWAYS raises a red flag to me just for the simple fact that many of these additions are not permitted while equally as many are done by yahoos who happened to have the lowest bid ( I know many of them in our local area.....its amazing they are still in business).

Many framers will attach this type of configuration by simply nailing on the top edge (1 1/2 side) of the framing member so that it is not seen once sheathing is placed...........the reasoning being that their is less liking of splitting the rafter as well as having more holding power than toe nailing the side while catching very little of the truss or rafter beneath it.
I personally will put a bottom plate that spans across all the rafters however again we are talking low ballers that are not going to spend the extra $50.00 for 2x8's.

Further evaluation is warranted regardless......preferably being done by the home inspector at the time of the inspection.

regards

Jeff
Reply With Quote
  #11  
Old 6/27/09, 7:43 AM
John Evans John Evans is online now
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 506
Default Re: Structural recommendation

Mark,

I posted a similar situation in the members only section. To confirm my concerns about the structural integrity of the existing truss roof and the rafter addition, I emailed photos and details to a local structural engineer for comments. He indicated that placing additional load at the ridge of the trusses could be a problem. As we know, truss systems are designed for specific loads, adding additional stress and weight may cause problems with the roof structure. He was also concerned about the connections, but your connections look much better than the one I inspected. The engineer was only offering an opinion based on my photos, an on site evaluation would be required to complete his report.



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #12  
Old 6/27/09, 5:42 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,805
Default Re: Structural recommendation

Hard to tell with limited picture's. In cases like this I have always removed about 30'' of plywood near the ridge so the new rafters can be installed or sistered onto the existing one's. Hard to tell if these are toe nailed and into what? the old rafters or just plywood.

This is a hard call but I would mention it in the report.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Episode 63 - Structural Solutions inxil NACHI.TV 0 4/28/09 1:30 PM
"A Bridge Too Far" mcyr Exterior 7 12/18/08 6:38 PM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
Chicago area structural damage Anita Casey Structural 2 7/6/07 9:43 AM


All times are GMT -4. The time now is 8:32 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts