Default Support Pier

Check out the picture of the masonry block support pier. The bottom block is turned on its side. Is this ever OK? I think it's way wrong becuase the bottom block is much weaker when it's turned that way. If it's wrong can you guys give me some words to write it up? Thanks in advance.
Attached Thumbnails
support-pier-blockhead1.jpg  
Reply With Quote
  #2  
Old 7/28/06, 8:15 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Support Pier

All block supports must be placed so that the hollow channel is vertical. Blocks that are layed down on their sides, have a tendency to crush.

Last edited by dvalley; 10/7/07 at 4:42 PM..
Reply With Quote
  #3  
Old 7/28/06, 9:05 AM
tszczepanski tszczepanski is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Lawton, OK
Posts: 16
Default Re: Support Pier

Floor supports installed in a non-standard manner. Recommend review by a structural engineer. Based on engineer's recommendations, recommend correction of pier construction or other structural work be accomplished by a licensed, reputable contractor.

You bring up a question I had concerning the location of some of these comments. When compiling a Summary, do these "recommendations for further review" get inserted there, or do you commonly just leave them in the body of the report? I know from experience, it seems no one reads the entire report, just the summary!
Thanks
Reply With Quote
  #4  
Old 7/28/06, 6:58 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Support Pier

I usually write it in my normal text area of the report in a different color to have the readers attention to that note and also rewrite it in my summary at the end of the report that people are more apt to read, because it is short and to the point.
It is more or else combined with the concerns and safety summary.
Hard to comment from the picture, due a pier that is picking up the load in the picture and the block might be achieving something else that I can not see.

Marcel
Reply With Quote
  #5  
Old 7/28/06, 7:14 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Support Pier

Quote:
Originally Posted by mcyr
I usually write it in my normal text area of the report in a different color to have the readers attention to that note and also rewrite it in my summary at the end of the report that people are more apt to read, because it is short and to the point.
It is more or else combined with the concerns and safety summary.
Hard to comment from the picture, due a pier that is picking up the load in the picture and the block might be achieving something else that I can not see.

Marcel
The main reason why you write this information in is protect your self.
We all hope that people fix the concerns that we tell them about.
Many people seldom do as we recommend until they have trouble .
</IMG></IMG>
Roy Cooke sr
Reply With Quote
  #6  
Old 7/28/06, 7:22 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Support Pier

That looks like a pier that was added after the fact...If that is the case I would report it as incorrect and needing correction, but would not suggest a SE.
Reply With Quote
  #7  
Old 7/28/06, 7:57 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Support Pier

A wise man once told me that when you are out there doing these Inspections and confronted with obstacles that you might not have seen before or understand, the best way about it is to right hard on what you see and install the CMA in your report. For the ones that are wondering what CMA is it = Cover my A##. Since it was worded a little different from the Wise Man, I will not make it verbatim in the text.
This almost sounds like CMI , must be a relative. ha. ha. That's OK, I don't qualify anyway. Maybe another 8 years or so, I might relish that designation.

Marcel
</IMG></IMG>
Reply With Quote
  #8  
Old 7/28/06, 10:36 PM
tszczepanski tszczepanski is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Lawton, OK
Posts: 16
Default Re: Support Pier

I see this type of condition regularly. The comment I suggested should cover your bases without getting too deep. Usually this is in a home with a few years on it and if I am seeing the picture correctly, it appears to have been there for some time. I think that if folks are buying the home, then they simply need to be alerted that problems may have existed in the past. So to answer the original question, I would say that it is not "book" correct, but if it is serving the purpose for a number of years and is functioning as intended, then simply alerting them to this fact is enough. That way, if there is a future problem in that area, you told them about a possible cause!
Reply With Quote
  #9  
Old 7/29/06, 11:59 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Support Pier

Blocks are not intended to be laid on the sides, and there is a reduced capacity. How severe the issue is depends on the loading, which isn't known.

Also, don't be fooled by the common misconception that if something has been a certain way for a while it's probably okay. The length of time it's been there really has nothing to do with the capacity ... and structures get weaker over time, not stronger. It could be just hanging on by a thread and then fail suddenly since it's unreinforced masonry.

As long as you don't suspect anything else, it's probably less expensive to have the condition repaired than to to have an engineer evaluate if it's acceptable.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 7/30/06, 5:37 PM
tszczepanski tszczepanski is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Lawton, OK
Posts: 16
Default Re: Support Pier

Well now, if you have no idea of the loading on this particular pier, then perhaps just having it corrected won't solve the problem. I prefer to have an expert look at these situations since the pier is probably a homeowner repair that they thought would be adequate. All things considered, a repair may be all that is needed, but then if it isn't, you are now the expert in determining the loads, size of pier, construction method. As I said before, USUALLY these conditions are found in homes (in this area) that are over 40 years old. Buyers investing in this type of property should be alerted to the condition, how they proceed is up to them, but I would still give the cannned statement for an engineer review (as you mentioned - for the loading and calcs).
Reply With Quote
  #11  
Old 7/30/06, 6:02 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Support Pier

How many times have we seen Mr. Weekend Bubba working on his car with cinder blocks, always on their sides holding up the car while Bubba works on it? Concrete blocks should have labels on them stating This Side Up.
Reply With Quote
  #12  
Old 7/30/06, 9:26 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Support Pier

Loading/capacity can't be inferred from a visual inspection for any structural component, and inspectors will often make the call to either recommend further evaluation or repairs for defects observed ... with repair recommendations usually associated with minor isolated material/installation defects. However if someone is more comfortable recommending further evaluation for possible defects that may affect capacity or where the gut feeling is something is very wrong, particularly where a homeowner structural fix is suspected, I think thats fine.

Quote:
Originally Posted by rwand1
Concrete blocks should have labels on them stating This Side Up.
Very true ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 8/1/06, 7:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Support Pier

Attachment 4844

Last edited by dvalley; 10/7/07 at 4:42 PM..
Reply With Quote
  #14  
Old 8/1/06, 7:41 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Support Pier

Its sort of reminiscent of the bubbas laying sod at the construction site. The site manager kept running to the windows of the new homes and would yell out, "green side up, green side up!"
Reply With Quote
  #15  
Old 8/2/06, 5:50 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Support Pier

David, that was pretty cute, LOL. Is it possible that we have to go to that point of explicitly to inform the general public and try to make every product on the market idiot proof?? I don't think so because every time you solve one, another idiot is born. I believe it is a no brainier and no win situation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Brick Support Pier Skip Erwin Structural Inspections 19 9/26/07 3:58 PM
Heavy timber posts and support beam hziegenbein Structural Inspections 4 9/24/07 8:22 PM
Concrete Pier support?? gbrasseur Structural Inspections 4 11/29/06 1:24 AM
Support post for Beam, is this right? mlong Structural Inspections 74 7/25/06 7:47 PM


All times are GMT -4. The time now is 3:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts