Two questions on type structure I do not see often.

Home is 1998 build and does not look modified meaning this is most likely part of the original design.

First question is besides earth to wood contact would you consider this post as needing bracing and second question is what do you call the part of the home it supports ?

All comments welcome.
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/23/11, 11:44 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Support post

picture?



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 11/23/11, 11:47 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

Quote:
Originally Posted by jmckee View Post
picture?
Sorry just caught that as I am working on the report.LOL.(darn you were fast)
Ignore the curvature in the one as it is off a fisheye effect from a video shot.
Post is at left side corner in last picture.

[ATTACH][ATTACH][ATTACH]support-post-post-support-4.jpg[/ATTACH][/ATTACH][/ATTACH]
Attached Thumbnails
support-post-post-support1.jpg   support-post-post-support-2.jpg   support-post-post-support-3-1024x768-.jpg  
Reply With Quote
  #4  
Old 11/23/11, 11:54 AM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: Support post

"Cantilever"?

Minimum 6 x 6,? Is it stucco clad? If so, its too close to grade. Is it in a driveway and subject to mechanical damage? Can you confirm if there was a proper concrete footing below the frost line? Was is secured both top and bottom?



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
  #5  
Old 11/23/11, 11:55 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Support post

well from Ohio I would say if the cantilever for the bedroom bump out were done properly the post would not be necessary, but it would be impossible to tell that without removing sub floor or drywall.The one picture seems to show a bow in the post which could indicate compression and perhaps an improperly framed cantilever...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #6  
Old 11/23/11, 12:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

I said ignore the bow as it is due to fisheye effect from that being a video shot however should I mention it being in need of bracing ?
Just comment on earth wood contact and leave it be?
The porch was built using nails for the ledger and improper support so my suspicion level is high.
Reply With Quote
  #7  
Old 11/23/11, 12:06 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

Quote:
Originally Posted by rstrand View Post
"Cantilever"?

Minimum 6 x 6,? Is it stucco clad? If so, its too close to grade. Is it in a driveway and subject to mechanical damage? Can you confirm if there was a proper concrete footing below the frost line? Was is secured both top and bottom?
No did not confirm footing but more concerned about 4x4 and it is aluminum siding as stucco is rare (thank goodness)in this area.Though missing tyvek was noted at the attic.

How would I Observe proper attachment at top ..lol?
Reply With Quote
  #8  
Old 11/23/11, 12:08 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Support post

If there were no bow Bob I would just mention the post earth contact and move on...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #9  
Old 11/23/11, 12:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

Quote:
Originally Posted by jmckee View Post
If there were no bow Bob I would just mention the post earth contact and move on...
I sorta agree but if you saw this at a deck you would call for diagonal bracing right?
Does the fact it is possibly cantilevered change that?

Maybe I am over thinking but sure would hate to miss an obvious.
Reply With Quote
  #10  
Old 11/23/11, 12:59 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Support post

Same principle applies as to a deck supported. If it is over 12' it should be a 6x6 post for support. I think someone ran this for convenience of the gutter system and not an actual support for the cantilevered bedroom. If it is a support this is foolish, a 45-degree support to the wall like you would see with a overhanging front entrance would have been a better Idea.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #11  
Old 11/23/11, 1:01 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

Quote:
Originally Posted by kwood View Post
Same principle applies as to a deck supported. If it is over 12' it should be a 6x6 post for support. I think someone ran this for convenience of the gutter system and not an actual support for the cantilevered bedroom. If it is a support this is foolish, a 45-degree support to the wall like you would see with a overhanging front entrance would have been a better Idea.
That makes sense.

So if your report would you comment on anything?

Gosh glad my afternoon cancelled for today.(yet another blunder) Bank did not deteriorated-winterize.
Reply With Quote
  #12  
Old 11/23/11, 2:38 PM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Support post

Quote:
Originally Posted by kwood View Post
Same principle applies as to a deck supported. If it is over 12' it should be a 6x6 post for support. I think someone ran this for convenience of the gutter system and not an actual support for the cantilevered bedroom. If it is a support this is foolish, a 45-degree support to the wall like you would see with a overhanging front entrance would have been a better Idea.
Our local AHJ used to require 6x6" over 6' high but recently began requiring 6x6" for all deck/bacony support posts.
Reply With Quote
  #13  
Old 11/23/11, 2:39 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Support post

It looks like a 6 x 6 PTL Timber
How is the Footing?
Concern is the downspout piping adjacent. How is the sub grade drain installed if a footing is present?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/23/11, 2:45 PM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Support post

Quote:
Originally Posted by kwood View Post
Same principle applies as to a deck supported. If it is over 12' it should be a 6x6 post for support. I think someone ran this for convenience of the gutter system and not an actual support for the cantilevered bedroom. If it is a support this is foolish, a 45-degree support to the wall like you would see with a overhanging front entrance would have been a better Idea.
If this cantilevered room extension does not need a support, then most likely it was an engineered design as most codes would not allow this distance (appears about 4') of overhang with 2"x standard lumber.

Likewise, a 45 degree support would most likely needed to be engineered.
Reply With Quote
  #15  
Old 11/23/11, 2:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Support post

Quote:
Originally Posted by jhagarty View Post
It looks like a 6 x 6 PTL Timber
How is the Footing?
Concern is the downspout piping adjacent. How is the sub grade drain installed if a footing is present?
It goes underground to edge of a giant reservoir behind my back while shooting.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
First 12 members to post win Safety Practices for the Home Inspector book. gromicko General Inspection Discussion 47 12/23/09 10:23 AM
47 piece DeWALT drill bit set. First 12 members to post win. gromicko Legislation, Licensing & Legal Issues for Inspectors 53 12/21/09 6:15 PM
Another way to support a house dvalley Exterior Inspections 3 10/30/09 3:45 PM
Post Turtle ldapkus Miscellaneous Discussion for Inspectors 8 10/30/08 1:36 PM


All times are GMT -4. The time now is 3:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts