2 car garage over unfinished basement.
Pic 1: 2 6" steel beams running 21ft 1 screw column in the middle of each beam...neither column is anchored on either end. ends of beams rest on foundation wall. is there a problem with the bottom chords of the beams not being continuous??? Pic 2: Between the top of the beam and the ceiling looked to be a fiberboard material. It's only installed directly above the beams...rest of ceiling is concrete. Possibly acting as a cushion??? Pic 3: ceiling in corner of basement under garage...no, the pic is not playing with your eyes. garage floor is bowing in this area. Garage floor definately flexes and vibrates when you jump on it. What's odd is that there was a hump all the way down the garage floor, but it was perpendicular to the beams. Never ran into a suspended concrete garage floor like this. Because of this and the factors listed above, I believe a Strucural Engineer is in order. Any objections?...please share any input. |
|
#2
|
||||
|
||||
|
By removing the bottom flange of the I-beams, they have greatly reduced their load-bearing capacity.
That and the temporary supports are enough for me to say this needs some serious attention. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
That IS one I would HIGHLY recommend an IN GA NEER look at.
|
|
#4
|
||||
|
||||
|
Engineering review is warranted.
Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#5
|
||||
|
||||
|
Yikes!
|
|
#6
|
||||
|
||||
|
double yikes
Joe Kormos A-1st Look Home Inspectors Inc. 630-201-0933 Your 1st Choice in Property Inspection Professionals www.a-1stlookhomeinspectors.com www.a-1stlook.com Let us look before you buy...for peace of mind “Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford |
|
#7
|
||||
|
||||
|
Would it be possible that this slab is constructed with precast cored planks.
That would explain the camber in the middle typical of precast planks with a topping. Hard to tell from the pictures. Those temporary post might have been installed because of the bounce and springy action of this system. Mention of steel beam, but I can't see them. Typical bearing for precast plank is 2 & 1/2" secured on the ends with re-bar in the cores and topping. http://www.pci.org/view_file.cfm?file=AS-00SU-3.PDF Marcel </IMG></IMG> LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#8
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Don't tell me, let me guess...somebody designed and built this thing all by himself, and got a great deal on a couple of pieces of steel, and then decided he wanted to use his trampoline for a garage and added the jacking posts.
How many things can you find right in those pictures? |
|
#9
|
||||
|
||||
|
Please Note:
cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
it all seemed original to me. the beams are directly above the temporary posts. painted white like the ceiling. notice how the bottom flange is only intermittent. Also, in the garage itself, there was an 18" high plywood "skirting" all the way around the perimiter where the floor meets the wall...drywall above that on walls and ceiling. Thinking it was due to there obviously being no floor drain. Snow and rain from cars has no where to go. Drywall likely soaked it up. There were some water stains on the floor throughout. The "skirting" wouldn't likely be part of the retrofit of the precast panels Marcel was talking about, would it? |
|
#10
|
||||
|
||||
|
Precast panels would have been a rarity in the 60's, and very unlikely in residential construction.
The bottom flange is not intermittant, it's gone. What you see is not part of the flange, but plates welded on, perhaps where supports once were considered. It looks like they cut the I-beam in half, to use it in two locations. The I-beam and support posts make it clear that this was not designed this way. Not knowing what's inside the concrete, you should certainly defer this. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
||||
|
||||
|
Quote:
What puzzles me is why would anyone would use a T-beam for support when they cost more than a regular beam then turn around and re-weld some support plates. Assuming as you said, that a bigger I- beam would have been torched down the middle is not logical due to what happens when torching a piece of steel of that size. The beam would have distorted so much from the heat it would have been unusable. I agree that a structural Engineer needs to look at this, but considering that this design has been in place since the 60's, that I was not made aware of, it might only proof that obviously it was able to sustain the load all these years and is far from meeting todays structural standards and this is what I would recommend $5000 later. I guess the structural engineer could determine as to whether or not these temporary jack post are necessary. Feel free to make me understand the logic behind this one. Marcel </IMG></IMG> LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#12
|
||||
|
||||
|
Quote:
It would have made more sense if the flange was on the bottom rather than the top. My guess is that this was an "after-thought" and possibly installed to eliminate some of the deflection that may have occurred from parking the truck in the garage. But again, this is all speculation on my part. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Quote:
Something in the pictures of the previous post just dose not look right. Further evaluation would be an understatement on my part at this time. Thanks for sharing Jeff. Learn something new every day, and been in Construction for over 40 years. ha. ha. Never to old to learn are we. ??? Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#14
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the flanges were at the bottom, that would mean that whatever the floor is made of would be supported only on the thin edge of the web. Usually when tees are used as beams, they are used with the flange on top. They are just not used a beams that often...occasionally as lintels.
A beam that depth with no bottom flange spanning 20 feet with a concrete floor above it had best have a couple of posts. Someone took a wild guess at this one and missed the mark. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 3:05 PM |
| Moisture in slabs | mcyr | Structural Inspections | 7 | 8/20/07 7:33 PM |
| bbbb | mcyr | Structural Inspections | 1 | 8/19/07 10:26 PM |
| Moisture control for slab on grade in protecting floor finishes | mcyr | General Inspection Discussion | 2 | 8/13/07 7:53 PM |