Arrow Suspended Concrete Floor

2 car garage over unfinished basement.

Pic 1:
2 6" steel beams running 21ft
1 screw column in the middle of each beam...neither column is anchored on either end.
ends of beams rest on foundation wall.
is there a problem with the bottom chords of the beams not being continuous???

Pic 2:
Between the top of the beam and the ceiling looked to be a fiberboard material.
It's only installed directly above the beams...rest of ceiling is concrete.
Possibly acting as a cushion???

Pic 3:
ceiling in corner of basement under garage...no, the pic is not playing with your eyes.
garage floor is bowing in this area.

Garage floor definately flexes and vibrates when you jump on it.

What's odd is that there was a hump all the way down the garage floor, but it was perpendicular to the beams.

Never ran into a suspended concrete garage floor like this.
Because of this and the factors listed above, I believe a Strucural Engineer is in order.

Any objections?...please share any input.
Attached Thumbnails
suspended-concrete-floor-100_1534-small-.jpg.jpg
Views:	571
Size:	28.6 KB
ID:	10933   suspended-concrete-floor-100_1533-small-.jpg.jpg
Views:	440
Size:	26.7 KB
ID:	10934   suspended-concrete-floor-100_1532-small-.jpg.jpg
Views:	429
Size:	18.1 KB
ID:	10935  
Reply With Quote
  #2  
Old 4/19/07, 10:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Suspended Concrete Floor

By removing the bottom flange of the I-beams, they have greatly reduced their load-bearing capacity.

That and the temporary supports are enough for me to say this needs some serious attention.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 4/19/07, 10:34 PM
rmccullough rmccullough is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Arvada, CO
Posts: 272
Default Re: Suspended Concrete Floor

That IS one I would HIGHLY recommend an IN GA NEER look at.
Reply With Quote
  #4  
Old 4/19/07, 10:38 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Suspended Concrete Floor

Engineering review is warranted.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #5  
Old 4/20/07, 12:57 AM
Thomas Jansson's Avatar
Thomas Jansson Thomas Jansson is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Chicago, IL
Posts: 194
Default Re: Suspended Concrete Floor

Yikes!
Reply With Quote
  #6  
Old 4/20/07, 1:22 AM
jkormos's Avatar
jkormos jkormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 641
Default Re: Suspended Concrete Floor

double yikes



Joe Kormos
A-1st Look Home Inspectors Inc.
630-201-0933
Your 1st Choice in Property Inspection Professionals
www.a-1stlookhomeinspectors.com
www.a-1stlook.com
Let us look before you buy...for peace of mind
“Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford
Reply With Quote
  #7  
Old 4/20/07, 7:06 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Suspended Concrete Floor

Would it be possible that this slab is constructed with precast cored planks.
That would explain the camber in the middle typical of precast planks with a topping.
Hard to tell from the pictures.
Those temporary post might have been installed because of the bounce and springy action of this system.
Mention of steel beam, but I can't see them.

Typical bearing for precast plank is 2 & 1/2" secured on the ends with re-bar in the cores and topping.


http://www.pci.org/view_file.cfm?file=AS-00SU-3.PDF

Marcel
</IMG></IMG>
Reply With Quote
  #8  
Old 4/20/07, 7:29 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suspended Concrete Floor

Don't tell me, let me guess...somebody designed and built this thing all by himself, and got a great deal on a couple of pieces of steel, and then decided he wanted to use his trampoline for a garage and added the jacking posts.

How many things can you find right in those pictures?
Reply With Quote
  #9  
Old 4/20/07, 8:31 AM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 96
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suspended Concrete Floor

Quote:
Originally Posted by mcyr
Would it be possible that this slab is constructed with precast cored planks.


Mention of steel beam, but I can't see them.

</IMG></IMG>
were precasts around in the late 60's when this was built?
it all seemed original to me.

the beams are directly above the temporary posts.
painted white like the ceiling.
notice how the bottom flange is only intermittent.


Also, in the garage itself, there was an 18" high plywood "skirting" all the way around the perimiter where the floor meets the wall...drywall above that on walls and ceiling.

Thinking it was due to there obviously being no floor drain.
Snow and rain from cars has no where to go.
Drywall likely soaked it up.

There were some water stains on the floor throughout.

The "skirting" wouldn't likely be part of the retrofit of the precast panels Marcel was talking about, would it?
Reply With Quote
  #10  
Old 4/20/07, 11:17 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Suspended Concrete Floor

Precast panels would have been a rarity in the 60's, and very unlikely in residential construction.

The bottom flange is not intermittant, it's gone. What you see is not part of the flange, but plates welded on, perhaps where supports once were considered.

It looks like they cut the I-beam in half, to use it in two locations.

The I-beam and support posts make it clear that this was not designed this way. Not knowing what's inside the concrete, you should certainly defer this.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 4/20/07, 5:14 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Suspended Concrete Floor

Quote:
Originally Posted by jpope
Precast panels would have been a rarity in the 60's, and very unlikely in residential construction.

The bottom flange is not intermittant, it's gone. What you see is not part of the flange, but plates welded on, perhaps where supports once were considered.

It looks like they cut the I-beam in half, to use it in two locations.

The I-beam and support posts make it clear that this was not designed this way. Not knowing what's inside the concrete, you should certainly defer this.
Must be the picture quality, that whole thing on my end looks like the edge of a concrete plank, but I will take your word Jeff on this one.

What puzzles me is why would anyone would use a T-beam for support when they cost more than a regular beam then turn around and re-weld some support plates.

Assuming as you said, that a bigger I- beam would have been torched down the middle is not logical due to what happens when torching a piece of steel of that size. The beam would have distorted so much from the heat it would have been unusable.

I agree that a structural Engineer needs to look at this, but considering that this design has been in place since the 60's, that I was not made aware of, it might only proof that obviously it was able to sustain the load all these years and is far from meeting todays structural standards and this is what I would recommend $5000 later.

I guess the structural engineer could determine as to whether or not these temporary jack post are necessary.

Feel free to make me understand the logic behind this one.



Marcel
</IMG></IMG>
Reply With Quote
  #12  
Old 4/20/07, 5:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Suspended Concrete Floor

Quote:
Originally Posted by mcyr
Assuming as you said, that a bigger I- beam would have been torched down the middle is not logical due to what happens when torching a piece of steel of that size. The beam would have distorted so much from the heat it would have been unusable.
I based that assumption on the jagged edge of the beam (indicative of a torch cut). I've personally cut many I-beams, columns and soldier-piles this way for various reasons on projects, but never to use as a permanent means of support.

It would have made more sense if the flange was on the bottom rather than the top.

My guess is that this was an "after-thought" and possibly installed to eliminate some of the deflection that may have occurred from parking the truck in the garage. But again, this is all speculation on my part.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 4/20/07, 5:56 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Suspended Concrete Floor

Quote:
Originally Posted by jpope
I based that assumption on the jagged edge of the beam (indicative of a torch cut). I've personally cut many I-beams, columns and soldier-piles this way for various reasons on projects, but never to use as a permanent means of support.

It would have made more sense if the flange was on the bottom rather than the top.

My guess is that this was an "after-thought" and possibly installed to eliminate some of the deflection that may have occurred from parking the truck in the garage. But again, this is all speculation on my part.
I have torch many pieces of steel myself, since I started being taught how to weld at 14 years old, but I agree with the highlighted above.

Something in the pictures of the previous post just dose not look right.

Further evaluation would be an understatement on my part at this time.

Thanks for sharing Jeff. Learn something new every day, and been in Construction for over 40 years. ha. ha.

Never to old to learn are we. ???

Marcel
Reply With Quote
  #14  
Old 4/20/07, 6:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Suspended Concrete Floor

Quote:
Originally Posted by mcyr
Never to old to learn are we. ???
Ain't that the truth. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 4/20/07, 9:02 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suspended Concrete Floor

If the flanges were at the bottom, that would mean that whatever the floor is made of would be supported only on the thin edge of the web. Usually when tees are used as beams, they are used with the flange on top. They are just not used a beams that often...occasionally as lintels.

A beam that depth with no bottom flange spanning 20 feet with a concrete floor above it had best have a couple of posts. Someone took a wild guess at this one and missed the mark.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 7:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 10:26 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM


All times are GMT -4. The time now is 11:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts