Default tolerances for floors/walls

I would imagine that this comes up in both new and existing construction, but what building code reference material would one utilize concerning acceptable measures of levelness in floors and plumbness in walls?

For example, I was contacted by someone in the construction field today who wanted to know what was acceptable regarding floors and where that reference could be found. How much fraction of an inch off per foot, etc. The floor in question was framed with manufactured I-joists. The difference in height over an 18' span was reported as 1.5".

Any input would be appreciated.
Reply With Quote
  #2  
Old 6/27/06, 12:46 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,688
Default Re: tolerances for floors/walls

Hank,

In Arizona using the UBC as a standard (with local changes).

Floors--1/2" in 12' or 3/16" in 4'

Wall Corners--Perpendicular within 1/4" in 10'

Wall Construction Flat--or no more than 3/8" in 8' (bulge)

But none of the contractors abide by the framing codes, nor do the city officials.

Unless something is so out of whack shimming in back of the sheetrock won't suffice it's OK here.

Last edited by dduffy; 6/27/06 at 1:40 AM..
Reply With Quote
  #3  
Old 6/27/06, 9:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: tolerances for floors/walls

Quote:
Originally Posted by hspinnler
existing The floor in question was framed with manufactured I-joists. .


Are you saying the house is out of level by 1 1/2" ? Don't sound right to me, not acceptable.

As to a standard, there must me one somewhere that states My house will be constructed plumb and level to tolerances of 1/4" +/-.

Marcel
Reply With Quote
  #4  
Old 6/27/06, 9:06 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tolerances for floors/walls

My house is not only plumb its better then plumb.
Roy sr
Reply With Quote
  #5  
Old 6/27/06, 9:30 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: tolerances for floors/walls

Hi. Roy;

How can it be better than plumb?? Did you buy a new laser level?? ha. ha.
Some guys on my job can mess that up too!!

Marcel
Reply With Quote
  #6  
Old 6/27/06, 9:48 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tolerances for floors/walls

Quote:
Originally Posted by mcyr
Hi. Roy;

How can it be better than plumb?? Did you buy a new laser level?? ha. ha.
Some guys on my job can mess that up too!!

Marcel
This came from My brother 40 years ago and I liked it so saved it to use .
The guy asked is it plumb and brother said Plumb why shes better then plumb and every body lost it.
Humour from the past .
It improves the day.
Another I rarely use but had my client last week crying .
Thats Ungood ,
We were talking about a section of floor that needed changing from dogs P
After he was able to talk he turned to the agent and said I like this guy he is the greatest.
You have to know you client before you do these things .
Roy sr
Reply With Quote
  #7  
Old 6/27/06, 10:13 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: tolerances for floors/walls

Now that you mention it, I faintly remember that same saying.

Thanks Roy for the Mental block refresher.

Marcel
Reply With Quote
  #8  
Old 6/28/06, 12:01 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,756
Default Re: tolerances for floors/walls

Buy the "Residential Construction Performance Guidelines" from the NHBA Bookstore, most of the code related book sites or ITA. About 100 pages spiral bound and gives building tolerances for professional builders and remodelers, and the recommended repair for the issue.

Good reference book. We use it for construction monitorings & expert witness in addition to mfg installation guides, codes, etc.
Reply With Quote
  #9  
Old 6/28/06, 1:05 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: tolerances for floors/walls



Is this it Dan?



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 6/29/06, 8:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: tolerances for floors/walls

Flatness/Levelness; Finished concrete surfaces of slabs on grade and wood floors should neet the following minimum tolerances for flatness F(F) and Levelness F(L) in areas with finish flooring materials.

ASTM E 1155/E 1155M for a randomly trafficked floor surface, except meet or exceed finish flooring manufacturer's required substrate tolerances where they are more stringent than the following:

Linoleum flooring and Cork flooring:
Flatness, F(F):35
Carpet:
Levelness F(F)20

These are just examples.

Similar levels would be appropriate for walls.

Marcel
Reply With Quote
  #11  
Old 6/29/06, 9:33 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: tolerances for floors/walls

Quote:
Originally Posted by hspinnler
... I was contacted by someone in the construction field today who wanted to know what was acceptable regarding floors and where that reference could be found.
The first place to look is in the locally adopted construction codes (and the reference standards like AWC, ACI and AISC documents), and if ya strike out there or you really don't need a mandatory standard then ya go to industry references like the NAHB Guidelines.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 6/29/06, 9:45 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: tolerances for floors/walls

Robert;

Now we sure are all confused.

Marcel
Reply With Quote
  #13  
Old 6/30/06, 2:40 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,756
Default Re: tolerances for floors/walls

Brian - You got it!!
Reply With Quote
  #14  
Old 6/30/06, 8:27 AM
Larry Ewens's Avatar
Larry Ewens Larry Ewens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 778
Send a message via AIM to lewens
Default Re: tolerances for floors/walls

If the floor is out of level 1 1/2" in 18' the whole building is racked. Absolutly unacceptable. If the carpenter can't read a level he shouldn't be a carpenter. With the lazer levels available today there should be no deviation from level and plumb. We did it with a water level for years and our structures were never out of level. But then again a water level doesn't lie.
Larry



Larry Ewens
1578 Colborne St
Brantford On
Nachi ID #05022485
Just my usual 12.5 cents


http://acissbrant.blogspot.com/

Reply With Quote
  #15  
Old 6/30/06, 2:14 PM
David E. Helm's Avatar
David E. Helm David E. Helm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 689
Default Re: tolerances for floors/walls

What planet are you guys writing from? I have never seen a code inspector carrying a level. Never seen one even try to eyeball level and plumb. Seldom will one find a plumb and level house (new or old). The builder tries (hopefully) but with changes in moisture level, settling and a myriad of other factors working on the structure, things don't stay plumb and level. Having said all this, 1 1/2 inches in 18 feet is a bit much!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:21 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts