Default Top Plate Bore

New construction, load-bearing common interior wall (Master bed/master bath), 3" stack installed. What do you think of this workmanship?

Last edited by cradan; 1/16/06 at 10:07 AM..
Reply With Quote
  #2  
Old 1/2/06, 12:17 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Top Plate Bore

A 2x6 wet wall would have been a better idea to run a 3" pipe through.
More attention should have been given to that issue.
Many times when a 2x4 wall is indicated on a blue print a more aware builder would notice that a 3" pipe would be better served by a 2x6 wall and make the proper changes.

Proper Bocca plates are installed.It could have been better but I don't really think it is an issue.
Reply With Quote
  #3  
Old 1/2/06, 1:15 PM
ccoombs's Avatar
ccoombs ccoombs is offline
Active Poster
 
Join Date: Jul 2004
Location: Corona, CA
Posts: 121
Please Note: ccoombs is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Top Plate Bore

Because the wall is not a shear wall, I don't see any issues. The only concern would be a bearing member sitting on the plate between the adjacent studs and the pipe.

When shear walls are involved I don’t feel that a 2x6 wall is structurally acceptable. I push architects and developers to provide a double 2x4 wall at such conditions. That way one wall is plumbing only and one is structural only. The grant my request most of the time…..
Reply With Quote
  #4  
Old 1/2/06, 1:35 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Top Plate Bore

What Cheremie said. We've always used a 2 X 6 wall usually in the vicinity of the laundry/utility room to accomidate (sp) the 3" plumbing vent.
Reply With Quote
  #5  
Old 1/2/06, 6:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Top Plate Bore

Christopher;

I do not see anything wrong with this picture.
You can cretique the home building all you want, but what you see is what you get. Hind sight is 20/20, for some and the building techniques won't change until the designers and builders in the Home Building Trade get educated a little more than where they are.

The plumbing pipe dose fit within the confines of the space, was protected with nail/screw plate, and this is seen everywhere and a Code Officer would say it is alright.

Curtis;

Having chase walls and space to create the mechanical and plumbing, is not always available and have to improvise with the available space.

Achitecs and designers are not what they used to be, so be prepared. Structural Engineers are not as bad, due the liability, 85% saftey factor, OK, that should work, and I will surelly save some design work. ha. ha.

Commen sense will go a long way if you have been in the Construction Industry for a while.

Some time, commen sense will tell you that a certain thing can fly along with the current standard, but wait, is there a standard on this one yet.?

Maybe no one has caught on yet, it's coming.
Take care and inpect with a short finger and note everything.

Most Clients need an education.

Marcel


Reply With Quote
  #6  
Old 1/2/06, 11:05 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Top Plate Bore

If that is a bearing wall the installation is WRONG.

If the top plate on a bearing wall (exterior or interior) is cut more than 50% it would need more that the typical protection plate shown. It would need a longer 16 gage by 1-1/2" wide metal tie strap extending past the cut on each side, with 6 nails on each side. Reference IRC R602.6.1 as a "guide" ...

Even with 2x6 construction the actual width is 5-1/2", and a 3" drain pipe needs a cut a little greater than the 3-1/2" pipe OD ... and the longer tie plates are still needed. Here is a link to one type of top plate tie made by Simpson that meets IRC R602.6.1 ... http://www.strongtie.com/products/connectors/RPS.html

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 1/2/06 at 11:31 PM..
Reply With Quote
  #7  
Old 1/3/06, 4:37 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Top Plate Bore

Here in earthquake country, I don't like it. I would have called it out and let a structural engineer sign off on it so that he has the liability and not me.
Reply With Quote
  #8  
Old 1/3/06, 7:13 AM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Top Plate Bore

I'll take back some of what I said.

Longer straps would be much better as indicated by Robert and IRC.Thanks Robert.
Reply With Quote
  #9  
Old 1/3/06, 12:17 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Top Plate Bore

I have seen many 2 x 4 framed walls where the plumbers ran 4" drain / vent pipes in them.

Then the drywallers have to deal with it.

But, it was right there in the plans. The Architect just didn't think.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 1/3/06, 2:08 PM
cradan cradan is offline
Active Poster
 
Join Date: Aug 2003
Location: Minooka, IL
Posts: 236
Please Note: cradan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Top Plate Bore

It is very, very common. The rule, actually, rather than the exception in local production housing. Little, if any forethought; blind adherence to plans without a minor (and inexpensive) modification to install a 6" wall. We've performed quite a few inspections in this particular jurisdiction, and we're certain the AHJ will not redline it. We did call it-out for the Client, but did not characterize it as a critical safety or functionality issue. The internal wall section where the bore was made has several truss sections bearing on it, but the interior wall is fairly close to the home's exterior wall, where all of the same trusses bear-fully, perhaps 9 feet away.

Our report recommended steel straps across the top plate faces on both sides. Thanks to all for the comments.
Reply With Quote
  #11  
Old 1/3/06, 6:47 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Top Plate Bore

Robert;

The reference to the IRC you noted is for bearing walls.

It is obvious to me in the picture that was supplied that this one is not.

The top of the walls depicts nailers for the drywall ceiling and therefore indicates to me it is an interior partion running parallel to the floor or ceiling members, therefore this situation is standard of practice for framing of the interior and plumbing procedures.
I even noticed evidence of a primer cleaner was used on the plumbing.

An no. A 4" stack or soil pipe will not fit in a 3&1/2" stud. This photo was a 3" PVC soil pipe.
I have not seen a new home yet that did not have this condition. But of course, this is Maine.

Marcel
Reply With Quote
  #12  
Old 1/4/06, 10:51 AM
NWJon NWJon is offline
New User
 
Join Date: Jan 2006
Posts: 14
Please Note: NWJon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Top Plate Bore

Quote:
Originally Posted by mcyr
Robert;

The reference to the IRC you noted is for bearing walls.

It is obvious to me in the picture that was supplied that this one is not.

The top of the walls depicts nailers for the drywall ceiling and therefore indicates to me it is an interior partion running parallel to the floor or ceiling members, therefore this situation is standard of practice for framing of the interior and plumbing procedures.
I even noticed evidence of a primer cleaner was used on the plumbing.

An no. A 4" stack or soil pipe will not fit in a 3&1/2" stud. This photo was a 3" PVC soil pipe.
I have not seen a new home yet that did not have this condition. But of course, this is Maine.

Marcel
I agree with you 100% Marcel and on the west coast where I build, there would be no other requirements. However, being a hands-on contractor for 26 years, I would typically put a 24 to 26 inch simpson strap on this situation... just to help with any possible future movement from earthquakes, wind or any other unexpected stress put on the home.

Cheers,
Jon
Reply With Quote
  #13  
Old 1/4/06, 8:25 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Top Plate Bore

Quote:
Originally Posted by mcyr
Robert;

The reference to the IRC you noted is for bearing walls.

It is obvious to me in the picture that was supplied that this one is not.
I agree the picture looks unusual for a bearing wall, but the original post stated it was a bearing wall ... so I indicated "if" it was a bearing wall the longer tension straps would be required ..

It's a common mistake to leave out the longer straps with adequate nails at large cuts in the exterior/interior bearing wall top plates, which has an impact on the hurricane/earthquake resistance of the building.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 1/4/06, 8:56 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Top Plate Bore


Sorry guys, I am from Maine, remember?, no hurricanes, no earthquakes, no rattle snakes, no floods, but cold.

Their was a time in my life where Simpson ties did not exist, and all the buildings I can remember, are still up.

When my father built a barn in his younger years which would be in the arena of th 1940's, there was no nails and the barn I am talking about is still upright and strong.
Have Structural Engineers relaxed to much over the years to use and specify hardware that has been engineered by others for them to save time and money on their commision to design, or have we got to the point that we are using these products because it has been proven to be better and more reliable? Are we at this point using Engineered products to provide insurance on the reliability of that product or products, to compensate for the inadequacy of the builders and us as Home Inspectors can not relate to how buildings were built in prior years?

I would imagine at this day and age that one could relate to todays' codes and what is adequate Inspecting a Home of 100 years old. Some Inspections will definetly show inadequacy in Code Compliance and not show signs of todays' Standards.
I personnally believe that a pipe going through a 2x4 stud does not have to go through the extreme of having these fancy straps and hangers or what not to be adequate, especially if it is not a bearing wall , regardless if it is in a Siesmic location or not.

For Inspection purposes, I would not the observation, and explain to the Client what the whole story is about.

Marcel








Reply With Quote
  #15  
Old 1/4/06, 9:29 PM
John Nosworthy John Nosworthy is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Delmar, MD
Posts: 148
Default Re: Top Plate Bore

You've got me thinking about how all too common this detail really is, and I'm adding this condition to my probably overlooked possible new construction flaws checklist to take a closer peak.
thanks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Faded name plate rstufflebeem Inspecting HVAC Systems 4 5/18/07 2:02 PM
EIFS bulge/cracks at top plate transition kshepard Exterior Inspections 11 4/27/07 10:06 AM
Cover plate dmacy Electrical Inspections 1 12/5/06 6:43 PM
Free NACHI license plate covers. gromicko Special Discounts for InterNACHI Inspectors 15 10/25/06 10:04 AM


All times are GMT -4. The time now is 3:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts