Default Trusses...anything wrong here?

This is not a competition. It's only an exhibition.

Anyone see anything wrong?

trusses-anything-wrong-here-090910-089.jpg trusses-anything-wrong-here-090910-090.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/10/10, 1:01 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Trusses...anything wrong here?

maybe, I have seen engineered house plans that did not show any of what you are looking for in certain areas but did in other areas of the same house.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 9/10/10, 1:37 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Trusses...anything wrong here?

No bracing, but bracing is different with every set of trusses and this engineer may not have required them.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #4  
Old 9/10/10, 12:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by kshepard View Post
No bracing, but bracing is different with every set of trusses and this engineer may not have required them.
IRC R802.10.3 Bracing. “Trusses shall be braced to prevent rotation and provide lateral stability in accordance with the requirements specified in the construction documents for the building and on the individual truss design drawings. In the absence of specific bracing requirements, trusses shall be braced in accordance with TPI/HIB.”

I say it's required by "today's commonly accepted construction standards" unless an engineer says it isn't necessary.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 9/10/10, 2:44 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Trusses...anything wrong here?

Thanks for the explanation Joe, cause I did not see anything wrong with those pictures.

Can you define TPI/MPC?

Design requirements and engineering of lateral requirements is usually left up to the engineer of record. We can not call out a deficiency based on what said in the IRC. It can not be applied to all situations we may encounter.

Consideration of permanent and temporary bracing of (MPC) wood trusses is critical for safety during erection and for reliable performance of a roof structure in service.
Temporary bracing is used to position and stabilize trusses until permanent bracing or other building components can be installed.
Permanent bracing is required to stabilize specific members of each truss throughout the life of the roof structure, when so required by design.

Based on truss design assumptions, various chords and webs require lateral support. The chords that require sheathing or the members that require lateral support at a specified interval are indicated on the truss design drawing.
Unfortunately, these design drawings are seldom available to the Inspector at the time of the Home Inspections.

Bracing, whether it is temporary or permanent, is required to help prevent the trusses from deflecting laterally and potentially causing the trusses to topple over or collapse.
The standard of practice is to leave the temporary lateral bracing that is used during the erection. Must of the time that is adequate unless the truss drawings have the lateral bracing tags afixed to the truss chords that indicate permanent bracing locations. When none of those tags are visible, during an inspection, chances are none were required.

Permanent truss bracing can include several different components, but are typically designed using one of the following options:

(CLBs) at required brace locations in conjunction with diagonals;
or properly nailed sheathing, either oriented strand board (OSB) or plywood. If carefully designed, some elements of temporary bracing can serve dual roles and become permanent bracing also.

It is also a known standard of practice for truss erection on some limited sized homes, that no lateral bracing is required for lateral stability. Once the sheathing is installed, at times, a complete diaphragm and is enough to provide the lateral stability of the design.

For all our readers, here are some links that might come in useful.

http://www.mcvicker.com/twd/gwdi05/page011.htm

Reply With Quote
  #6  
Old 9/10/10, 2:57 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Trusses...anything wrong here?

Also, once the roof sheathing is nailed off, there's no way those trusses are going to rotate without help from a hurricane or tornado, especially if ridge blocks are installed and nailed to. The bottom chords are tied off at the walls... how would the trusses fail due to lack of bracing?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 9/10/10, 3:05 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Trusses...anything wrong here?

Even in this area, the design rating on houses varies from 80 to 90 mph.
With roof truss lateral bracing you have to report it as either something to investigate or an upgrade, you can't say its flat out wrong unless you have the plans that show it.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 9/10/10, 3:52 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by kshepard View Post
Also, once the roof sheathing is nailed off, there's no way those trusses are going to rotate without help from a hurricane or tornado, especially if ridge blocks are installed and nailed to. The bottom chords are tied off at the walls... how would the trusses fail due to lack of bracing?
Kenton, do the nails through the sheathing always hit the truss? What happens if a piece or two of the sheathing is blown away in a storm?

I plan to keep to my practice of recommending lateral bracing unless an engineer states it isn't necessary. Most new construction has horizontal or diagonal bracing. I conclude it's a construction defect, that the ones that that don't.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 9/10/10, 10:47 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Today's inspection made me happy.

trusses-anything-wrong-here-091010-086.jpg trusses-anything-wrong-here-091010-084.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 9/10/10, 11:15 PM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: Trusses...anything wrong here?

Joe

Making any kind of statement on truss bracing is outside the SOP and would put you in a position to either prove it, if your an engineer, or be prepared to pay for the engineer the owner hired if it was designed correctly. You can get by on stick built roofs making comments on over spanning of rafters and joists if you use the code tables correctly, but bracing is a totally different matter.

The individual trusses in the picture would not require permanent bracing on the longest diagonal web member because they are in tension. However you have to also look at the entire roof/truss system as a whole when considering wind or seismic loading. Outside of reporting a broken or cut truss member or a damaged or missing connection plate I would state the stability and load capacity of the engineered trusses are outside the scope of the inspection. Even as an engineer after I checked the design I would have to disclaim any damage caused by forces that are outside the acceptable standards for your location.





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #11  
Old 9/10/10, 11:23 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by rmayo View Post
Joe

Making any kind of statement on truss bracing is outside the SOP and would put you in a position to either prove it, if your an engineer, or be prepared to pay for the engineer the owner hired if it was designed correctly.
How is commenting about a home's perceived framing deficiency outside the SOP?

SC's SOP:

4) VISIBLE FRAMING:
A) Report if not visible.
B) Inspect and report the observed condition of the visible materials and structural components.
C) Describe and report defects and/or deficiencies.


Quote:
Originally Posted by rmayo View Post
The individual trusses in the picture would not require permanent bracing on the longest diagonal web member because they are in tension.
Please explain the meaning of this building requirement. Does it say anywhere trusses do not need to be braced?

"IRC R802.10.3 Bracing. “Trusses shall be braced to prevent rotation and provide lateral stability in accordance with the requirements specified in the construction documents for the building and on the individual truss design drawings. In the absence of specific bracing requirements, trusses shall be braced in accordance with TPI/HIB.”



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 9/10/10, 11:34 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

"Section 2.2.2 (d) and (e) of ANSI/TPI 1-1995 specifically addresses permanent truss bracing:

2.2.2 As this Standard does not cover the design for the complete
structural system of a building, the Building Designer shall provide for the
following in the design and detailing of the building:
(a) Truss deflections
(b) Truss movement due to moisture and temperature change
(c) Truss supports and anchorage accommodating horizontal, vertical or
other reactions or displacements
(d) Permanent truss bracing to resist wind, seismic and any other lateral forces acting perpendicular to the plane of the truss
(e) Permanent lateral bracing as specified by the Truss Designer, to
prevent buckling of the individual truss members due to design loads."

Source: http://www.woodscience.vt.edu/resear...rs/bracing.pdf



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 9/11/10, 12:10 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Randy, please explain page 41 to me. That part that says: "Always Diagonally Brace the Permanent Continuous Lateral Restraint"

http://www.sbcindustry.com/docs/06_B...mj9fks9hj3rpb7



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 9/11/10 at 12:17 AM..
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/11/10, 12:20 AM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: Trusses...anything wrong here?

Joe

Your quoting IRC code and TPI construction requirements. Are you doing code inspections or home inspections? I don't know of any home inspection SOP that indicates a home inspector is to act as a code inspector. Just so we are on the same page my previous comments were limited to truss bracing. The fact you don't see any does not mean they are required. I can say with confidence the truss manufacturer followed the design & bracing requirements and I am sure they were sent with the trusses. The only people that need them were the contractor and the local building code official. The TPI guide tells the designer they should check for the listed forces and design accordingly if the roof configuration does not warrant a permanent brace you don't have to use one. As a home inspector you are not required to verify the need for bracing for engineered trusses. Making a statement that would indicate a defect in the truss system when you do not know for a fact if it complies with the original design will make you liable for any cost incurred if you are proven wrong. You are not reporting a visual defect you are making a design assumption. Hey I am not trying to pick a fight I am just trying to reduce your liability.





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #15  
Old 9/11/10, 12:29 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Trusses...anything wrong here?

Randy, I'm not an engineer. And I appreciate your input.

Here's what I struggle with: 95% of the time the bracing is present, the IRC seems to say bracing is required, my research these past few hours seems to say bracing is required. But you say it isn't? That's what I don't understand.

Code is the basis for a lot of the calls we make. It's a resource to back up logic. I'm not quoting code in my inspections. But when I have a question about something, I certainly use it to see what industry experts across the country have implemented as standard practice. All home inspectors do it; from citing cutting and notching of joists, to calling out a defect in water heater TPR piping. This issue is no different.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cut Trusses msylvester Structural Inspections 10 2/21/09 2:33 PM
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
What's Wrong Here? jtedesco1 Electrical Inspections 10 12/9/07 9:36 PM
Trusses Laura Line Exterior Inspections 0 8/24/06 11:12 PM
Cut and burned trusses dmccauley Interior Inspections 6 7/13/06 9:56 PM


All times are GMT -4. The time now is 3:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts