Quote:
Originally Posted by jfunderburk View Post
Can you quote that section please. Give the context...the section heading too. Thanks.
Joe,
Your testing my typing skills but at any rate here is the complete quoted text of the section

BCSI edition published 2006
pg. 39

Permanent Bracing For The Bottom Cord Plane

Permanent Bracing for the bottom cords of metal plate connected wood trusses is typically provided by attaching either gypsum wallboard or continuous lumber lateral restraint properly braced against lateral movement

Lateral restraint shall be applied in combination with diagonal bracing spaced at intervals along the length of the building or other means that will provide stability and transfer the forces from the lateral restraint to a lateral force resisting system

Lumber used for lateral restraint and/or diagonal bracing shall be stress rated

Bottom chord permanent lateral restraint shall be installed at the spacing indicated on the TDD and/or by the building designer with a maximum of 10' on center

The TDD provides information on the assumed support for the bottom chord based on the load conditions for which the truss has been designed. This typically includes a directly applied rigid ceiling or Lateral Restraint at a specified maximum on center spacing



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #47  
Old 9/29/10, 2:26 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by mtyson View Post
Kenton,
...When referencing the manual it states that Bottom cord Permanent Lateral Restraint shall be installed at the spacing indicated on the TDD and or by the Building Designer with a maximum of 10' on center.
What's TDD?
Also if the trusses have been designed and signed off on by a building designer, doesn't that negate any need for compliance with the TDD?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #48  
Old 9/29/10, 2:33 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by mcyr View Post
Bracing

There are two types of lateral bracing used in truss construction, temporary and permanent. Temporary bracing holds the trusses vertical during construction.
Permanent bracing is used where required by the engineering analysis. The type and location of required bracing is indicated in the information provided by the truss manufacturer to the field when the trusses are delivered to the job site.


BCSI-B1 SUMMARY SHEET
Guide for Handling, Installing and Bracing of Metal Plate Connected Wood Trusses


General Notes

Trusses are not marked in any way to indentifiy the frequency or location of temporary bracing. Follow the recommendations for handling, installing and temporary bracing of trusses. Refer to BCSI 1-03 Guide to Good Practice for Handling, Installing & Bracing of Metal Plate Connected Wood Trusses for more detailed information.

Truss Design Drawings may specify locations of permanent bracing on individual compression members. Refer to the BCSI-B3 Summary Sheet - Web member Permanent Bracing/Web Reinforcement for more information. All permanent bracing design is the responsibility of the Building Designer.

Permanent bracing is clearly shown on any shipment drawings supplied by the Manufacturer upon delivery.

If permanent lateral bracing is not observed in an attic, they were either not specified by the Manufacturer, or the bracing was omitted, and the tags showing location of the bracing were torn off on purpose.


http://www.woodtruss.com/projects/woodtruss/bcsi.php

I think Marcel's got it (black text my addition).




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #49  
Old 9/29/10, 8:46 AM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Trusses...anything wrong here?

Quote:
Originally Posted by kshepard View Post
What's TDD?
Also if the trusses have been designed and signed off on by a building designer, doesn't that negate any need for compliance with the TDD?
TDD, Truss Design Drawing
Excellent point the sign off used to be a big gray area in that the TDD and the actual construction documents were submitted to the building department as separate documents.
If memory serves correctly that loop hole was eliminated with the Florida code cycle in 1997 and now requires the Building Designer to review and sign each sheet of the TDD acknowledging acceptance
Then with the code cycle of 2001 they finally got it right. Typically the TDD will only provide the reaction pressures that the trusses must be braced for such as uplift and lateral movement and not the method for bracing or attachment. Now the building designer must include all reaction, bracing, and the method of attachment, the connector manufacturer, and the size and number of nails to be used and must include that information on the plan view of the roof plan
So currently at least here in Florida all attachments and permanent bracing is included on the actual blue print with the exception of the permanent bracing for the web plane which is still the responsibility of the Truss Designer



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #50  
Old 9/29/10, 9:12 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Trusses...anything wrong here?

Works the same way here Mark. For Commercial, anyways.

Residential, the lumber yard sends the truss Manufacture the size of the house and their in-house engineers design the system.
Everything required is on the TDD.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cut Trusses msylvester Structural Inspections 10 2/21/09 2:33 PM
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
What's Wrong Here? jtedesco1 Electrical Inspections 10 12/9/07 9:36 PM
Trusses Laura Line Exterior Inspections 0 8/24/06 11:12 PM
Cut and burned trusses dmccauley Interior Inspections 6 7/13/06 9:56 PM


All times are GMT -4. The time now is 3:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts