Default Twisting ceiling joists

These ceiling joists were twisting badly.

What would be the proper repair? Metal connectors to the top plate? Blocking?

twisting-ceiling-joists-040309-328.jpg twisting-ceiling-joists-040309-329.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 4/6/09, 9:38 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jfunderburk View Post
These ceiling joists were twisting badly.

What would be the proper repair? Metal connectors to the top plate? Blocking?

Attachment 27862 Attachment 27863
Positioning and connecting them to the side of the rafters is the best construction method by triangulating the roof and ceiling.

If some bracing was attached perpendicular to and on top of the ceiling joists and tight to the bottom of the rafter, that could help the ceiling joist from tipping over some.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 4/6/09, 9:52 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,778
Default Re: Twisting ceiling joists

Quote:
Originally Posted by lkage View Post
Positioning and connecting them to the side of the rafters is the best construction method by triangulating the roof and ceiling.
I agree with Larry, and personally, I think the workmanship in your pictures is crap. It would throw up red flags for me, and I'd be searching for the root cause of the problem. My 'spidey sense' tells me theres a bigger problem in the works. I'd be willing to bet that someone screwed up, and is not shown in the plans that way, and that is how they compensated for it. I would opt for installing blocking, as opposed to metal connectors.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #4  
Old 4/6/09, 9:59 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Twisting ceiling joists

The previous homeowner was the builder.

Take a look at the girder in the crawl space.

twisting-ceiling-joists-040309-350.jpg twisting-ceiling-joists-040309-352.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 4/6/09, 10:06 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is online now
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 555
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jfunderburk View Post
These ceiling joists were twisting badly.

What would be the proper repair? Metal connectors to the top plate? Blocking?

Attachment 27862 Attachment 27863
Was there a plywood walking surface here? If not, I'd be suprised that the joists didn't just fall over. Everyone's a "Carpenter"



Bobby Hamilton
Bloodhound Home Investigations
Youngstown Home Inspection
Austintown Ohio Home Inspection
Youngstown Home Inspector

Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #6  
Old 4/6/09, 10:07 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,778
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jfunderburk View Post
The previous homeowner was the builder.

Take a look at the girder in the crawl space.

Attachment 27864 Attachment 27865
Who was he? Mr. Magoo?
Jeez... reminds me of your photo's in post #1.
No wonder he sold/is selling.
Seems you may be getting closer to the 'root' cause.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #7  
Old 4/6/09, 10:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Twisting ceiling joists

Quote:
Originally Posted by bhamilton View Post
Was there a plywood walking surface here? If not, I'd be surprised that the joists didn't just fall over.
No decking. I walked out a little on the structure and was real uneasy about it.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 4/6/09, 2:47 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 1,395
Default Re: Twisting ceiling joists

Hey Joe,

As other have said, crap workmanship.......as far as twisting, no need for metal ties or plates.......a simple, fast and inexpensive fix is to tie all the joist together with a 1x4x___ positioning same near the rafters. Also, you may want to check the nailing of same, its hard to tell but it looks like they simply nailed the butt end of the joist and that was it.

Anyway, such repairs can be made in less than 10 minutes.
Reply With Quote
  #9  
Old 4/6/09, 2:50 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 1,395
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jfunderburk View Post
The previous homeowner was the builder.

Take a look at the girder in the crawl space.

Attachment 27864 Attachment 27865
Not good......suppose to be in the middle third........... the code official should have caught that one..............but then again so many of them don't or won't go into crawls unless they have to.
Reply With Quote
  #10  
Old 4/6/09, 4:32 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,778
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jhaynes View Post
Hey Joe,

As other have said, crap workmanship.......as far as twisting, no need for metal ties or plates.......a simple, fast and inexpensive fix is to tie all the joist together with a 1x4x___ positioning same near the rafters. Also, you may want to check the nailing of same, its hard to tell but it looks like they simply nailed the butt end of the joist and that was it.

Anyway, such repairs can be made in less than 10 minutes.
Joe,

Normally I would agree with what Jeffrey stated (and Larry before him), but without more info, I'm not sure I would endorse that corrective action. Even at 400% zoom, I cannot tell the method of attachment. I can only assume the rafters were toenailed, but cannot see evidence of that. Do you have a wider angle photo of the attic?

And before anyone says it, no, I am not trying to give definative advice based upon a photo. This type of conversation, trading thoughts, is what helps keep the mind sharp. It's all about education

Glad you made it out of there without incident.

Jeff



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #11  
Old 4/6/09, 8:14 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 483
Default Re: Twisting ceiling joists

Quote:
Originally Posted by jfunderburk View Post
The previous homeowner was the builder.

Take a look at the girder in the crawl space.

Attachment 27864 Attachment 27865
This picture expains everything and I think I got it... They put up the ceiling joists first to site in the pier. But then some jerk added the drywall and everything got messed up.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #12  
Old 4/6/09, 10:26 PM
Gordon I. Kay Gordon I. Kay is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia
Posts: 30
Default Re: Twisting ceiling joists

With a stick framed roof like that my concern would be with rafter spread. Were collar ties in place, ridge beam support by load bearing members to foundation?
Reply With Quote
  #13  
Old 4/6/09, 10:53 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Twisting ceiling joists

Quote:
Originally Posted by gkay View Post
With a stick framed roof like that my concern would be with rafter spread. Were collar ties in place, ridge beam support by load bearing members to foundation?
Honestly I should have taken more photos. I've forgotten many of the details now. I assume ties were there and I know there were some vertical braces supporting the ridge beam. I referred it out and hope that settles it.

I couldn't get to the ends to check how they were fastened because there wasn't much to hold onto and I felt uneasy about walking on that shaky structure. I suppose they were toe nailed.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 4/7/09, 5:51 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 499
Default Re: Twisting ceiling joists

Joe,

I think "Maxwell Smart said it best...missed it by that much!"

The pictures of the laminate beam in the crawl space, what a joke. I can't believe that mistake was missed, and/or left uncorrected. Lots of folks had the chance to catch that mistake, and apparently didn't.
With the roof rafters and the beam conditions you have questioned, it kind of makes you wonder what else might be hidden.
Reply With Quote
  #15  
Old 4/7/09, 11:14 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 483
Default Re: Twisting ceiling joists

I don't think anyone was purposely hiding anything except their lack of knowlege in construction methods. I would not feel comfortable with this. Was this project issued a permit? Just curious...



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is it important to get ceiling joists 16" OC? Nathan W. Swilling Structural 7 1/11/08 11:10 PM
Max load allowed on 2x2 ledger bking Structural 4 12/23/07 3:05 PM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
Ceiling discoloration from joists? dtaylor General Inspection Discussion 4 8/3/06 1:27 AM


All times are GMT -4. The time now is 8:22 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts