Default Ventilation required?

Scenario: Two story home, two car garage, front 1/2 of garage has attic space above it that is not shared with anything else...just 200 sf or so of dead space. Attic wall on back side that is shared with livable space is insulated. There's soffit vents on two sides but no gable vent, ridge vent or other passive venting up high to discharge the hot air. Is there a requirement for ventilating that size & type of attic space? The IRC seems to be silent on it. I'm sure many of us would recommend it but is there any requirement?

ventilation-required-p7100259.jpg
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #2  
Old 7/10/09, 4:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Ventilation required?

Generally, the attic space above a garage does not require ventilation.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/10/09, 5:33 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Ventilation required?

Quote:
Originally Posted by jpope View Post
Generally, the attic space above a garage does not require ventilation.
Jeff...is that a personal opinion or can it be backed up anywhere? I thought there was a size, i.e a square footage minimum, but I can't find it anywhere. This is just for my own and another inspector's curiosity and future reference.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #4  
Old 7/10/09, 7:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Ventilation required?

Opinion based on experience and research in the UBC. I can't say whether this also applies to the IRC.

The UBC classifies a garage (attached or detached) as a Type U Occupancy. Basically, the UBC defines a Type U Occupancy as a "utility" type room/space, which includes garages and other "non-living" spaces.

I have never seen attic-ventilation requirements that apply to Type U Occupancies.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 7/10/09 at 7:09 PM..
Reply With Quote
  #5  
Old 7/10/09, 7:42 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Ventilation required?

OK, good deal...I'll drill down some on the UBC and IBC.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #6  
Old 7/10/09, 7:54 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Ventilation required?

that still doesn't address the excessive shingle wear and curl in the un-vented space...imho....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #7  
Old 7/10/09, 8:20 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Ventilation required?

Yes, I agree..the inspector that had originally asked my opinion on this noted exactly that on his report today. There's definitely reasons to add ventilation but I was/am hoping for something tangible that a builder can relate to. As I investigate the IBC I see and agree with Jeff....maybe. One section, 1203.2, of the 2003 IBC that is not Occupancy specific says that ventilation is required. So, I don't have the final answer from a code standpoint just yet.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #8  
Old 7/10/09, 8:31 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Ventilation required?

I like all roof cavities to be vented, but if the attic is not insulated (such as...above a garage) I don't make a big deal out of it. It's the insulation application that will cause attic cavities to become ovens.

IBC-2003 & 2006 Section 1203
- Ventilation

1203.2 Attic spaces. Enclosed attics and enclosed rafter spaces formed where ceilings are applied directly to the underside of roof framing members shall have cross ventilation for each separate space by ventilating openings protected against the entrance of rain and snow.

Blocking and bridging shall be arranged so as not to interfere with the movement of air. A minimum of 1 inch (25 mm) of airspace shall be provided between the insulation and the roof sheathing. The net free ventilating area shall not be loss than 1/150 of the area of the space ventilated, with 50 percent of the required ventilating area provided by ventilators located in the upper portion of the space to be ventilated at least 3 feet (914 mm) above eave or cornice vents with the balance of the required ventilation provided by eave or cornice vents.

http://www.southface.org/web/resourc...lings_4pdf.pdf

Last edited by dvalley; 7/10/09 at 8:38 PM..
Reply With Quote
  #9  
Old 7/10/09, 8:31 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Ventilation required?

sorry Mike i'm not a code inspector ...just use my experience in construction since 1968



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #10  
Old 7/11/09, 2:59 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ventilation required?

Quote:
Yes, I agree..the inspector that had originally asked my opinion on this noted exactly that on his report today. There's definitely reasons to add ventilation but I was/am hoping for something tangible that a builder can relate to.
There is such a thing, and it's called "good practice"! A building code, as many have said here, is only a minimum standard, and not necessarily a primer of good practice. One should not need a code to realize that any enclosed wood structure needs ventilation. However, ventilation is more art than science, and perhaps the soffit vents are enough, or perhaps there is a ventilation path to a ridge vent above the insulated space.
Reply With Quote
  #11  
Old 7/11/09, 6:44 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,033
Default Re: Ventilation required?

From a practical standpoint it should be vented......if for no other reason because of the heat that builds up from underneath which in turn will diminish the service life of the shingles.

Amazes me why a builder would spend an extra $600.00 on architectural shingles yet save $40.00 by not adding ridge vent over the garage......what a moron.

What alarms me is where the right slope of the garage roof dumps into vertical wall over the foyer.................amazes me why architects design homes to fail.

Is this a vinyl sided home with a brick veneer on the front.

regards

Jeff
Reply With Quote
  #12  
Old 7/11/09, 7:02 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,024
Default Re: Ventilation required?

code is the minimum, the shingle manufacture will want to see ventalation or there will be no warranty, not that it is easy to work through a roofing warranty.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #13  
Old 7/11/09, 8:54 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Ventilation required?

Quote:
Originally Posted by jhaynes View Post
Is this a vinyl sided home with a brick veneer on the front.
No, not exactly. This is a Hardie sided home with a brick veneer on three sides.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #14  
Old 7/11/09, 9:01 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Ventilation required?

Quote:
Originally Posted by bgraham View Post
....the shingle manufacture will want to see ventalation or there will be no warranty....
Now, there's an interesting angle. Owens-Corning literature states "Regardless of the deck used, the roofing installer must ensure that the attic ventilation meets or exceeds FHA Minimum Property Standards." Now, if I knew what that standard stated...



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #15  
Old 7/11/09, 11:13 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Ventilation required?

Quote:
Originally Posted by jhaynes View Post
From a practical standpoint it should be vented......if for no other reason because of the heat that builds up from underneath which in turn will diminish the service life of the shingles.
Agreed. And the garage will be a sauna. The IRC doesn't distinguish between attic types to my knowledge. Venting is required per the IRC. I write it up recommending ventilation when I see it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Inspection Services & Additional Topics 17 7/12/11 7:31 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 11:06 AM