Default Vertical crack with leak in cinder block foundation wall

Hello,

I am new to this message board and looking for some advice. I am looking at purchasing a home and in taking photos of the home I realized that in the basement there is a noticeable crack in the cinder block foundation. I definitely plan to have a proper inspection of the home, but was hoping to get some insight and a second opinion.

The crack appears to be slightly wider near the top than bottom, it spans several feet, but doesnt appear to go to the top of the wall. There appears to be staining near the bottom of the crack as if water has leaked through.

The house is on a hill and the side of the house left of the crack in the photo is on the downslope of a hill.

The home was built in 1925 and is located in New Jersey.

Thank you for any help you can offer, photo attached.

Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/31/11, 11:39 AM
Darren Tews, P.E. Darren Tews, P.E. is offline
InterNACHI Member
 
Join Date: May 2011
Posts: 47
Default Re: Vertical crack with leak in cinder block foundation wall

Start with a proper home inspection. I can't begin to come to any conclusions based on one photo, plus a typical consultation on foundation cracks involves a discussion of the client's own tolerance of the potential future scenarios (maintenance, monitoring, etc). It could have happened 5 years ago, or during construction 86 years ago. One photo won't tell the story.

And to top if off, there is such a thing as allowable settlement, and standards exist whereby cracks are graded in severity according to their physical characteristics. And some structures are more tolerant to settlement than others.

Here are some good resources for foundation cracks:
Forensic Geotechnical and Foundation Engineering, Day
Geotechnical and Foundation Engineering: Design and Construction, Day
www.foundationperformance.org

With that said, my general comment here is that you should communicate your concerns to the inspector or engineer that you hire. Have a discussion and communicate your position and concerns, along the lines of one or more of the following (and this isn't a complete list):

1. I don't want to buy something that ends up sliding down the hill.
2. I can live with cracks, as long as it doesn't end up progressing into a train wreck.
3. I can't live in a house with cracks.
4. I see the cracks, why are they there, and I want you to tell me if this is going to be a problem, and how much will that problem cost.

The unfortunate side of this is that no one will have 100% of the information. It will be an assessment of conditions at the time of the inspection. And information on the level of compaction of the soil, design of the footer, quality of materials and methods, etc, won't be completely known.



Licensed Engineer (NJ)
Licensed Home Inspector
Oak Ridge Engineering
Reply With Quote
  #3  
Old 7/31/11, 12:19 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Vertical crack with leak in cinder block foundation wall

Good response Darren.
Also a crack in that location could simply have been caused by weakening the wall switching from 12" blocks to 8" blocks and the window above.
Full evaluation of the exterior foundation and landscape would be in order to speculate what caused it.
The crack could have evolved early in the first year of construction also.
Too many variables to the cause of the crack and from just a picture as was said.
Then of course, I am not a big advocate on block foundations, unless properly built.

Is that a radon mitigation vent in the left of the picture?

Reply With Quote
  #4  
Old 7/31/11, 12:38 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Vertical crack with leak in cinder block foundation wall

All concrete cracks ... but different cracks mean different things

If it's really a concern hire a home inspector that is also a structural engineer who can do an evaluation ... it will usually cost more, but may be worth it to you.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 7/31/11, 12:47 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Vertical crack with leak in cinder block foundation wall

That it does Robert.
Reply With Quote
  #6  
Old 7/31/11, 9:22 PM
Peter Kozo Peter Kozo is offline
New User
 
Join Date: Jul 2011
Posts: 3
Please Note: Peter Kozo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vertical crack with leak in cinder block foundation wall

Thank you for your responses, I have an inspector going in there tomorrow. The home is exactly what I wanted, but now along with the active underground oil tank, this crack and leak makes me a bit weary of it ...

Marcel, with regards to your mention of radon mitigation vent, is that something positive or negative? Apologies for my ignorance, much of this is a new world to me

Thank you all again
Reply With Quote
  #7  
Old 8/1/11, 10:26 PM
Peter Kozo Peter Kozo is offline
New User
 
Join Date: Jul 2011
Posts: 3
Please Note: Peter Kozo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Unhappy Re: Vertical crack with leak in cinder block foundation wall

Had the inspection today... The inspector noted the crack and leak/moisture on the bottom of the crack.He also noted that the left side of the house, which sits on a steep downslope has settled down lower than the right side, you can see this in the photos below, which has made the house lean slightly. He mentioned that the crack was painted over and the paint did not look fresh and has not cracked which may imply that it is not recent.

He also noted that one of the main beams has dropped off the foundation and has sagged down (same side of the house on the downslope. Please take a look at the below photos I took. Any feedback/comments are very welcome... The inspector recommended sealing the crack from the outside to prevent moisture from entering and recommended putting a support pole to add support for the sagging beam.

Wall on left is on the downslope, note the tilt in the wall at the junction of the crack:



Here is the main beam that sags down, the right in this picture corresponds to the left in previous (the wall with crack is where i took the photo from)



Beam where it meets the foundation wall, it is not supporting on the foundation:



Thank you all!
Reply With Quote
  #8  
Old 8/2/11, 9:30 AM
Darren Tews, P.E. Darren Tews, P.E. is offline
InterNACHI Member
 
Join Date: May 2011
Posts: 47
Default Re: Vertical crack with leak in cinder block foundation wall

I see some angular displacement of the foundation in the photos, with what appears to be a displaced beam (apparently due to the angular displacement of the foundation). I'm certainly not going to say everything is hunky dory, but it's a good example of an 86 year old wood frame structure's tolerance to foundation movement.

There are buildings in Europe that look like funhouses, with much worse issues, that have been standing for centuries. One of my favorites is a place called the Crooked House Pub, near Birmingham, UK. Way back when, they dug a coal mine under the town, and the building started sliding into it. 150 years later, it's still standing (but at a pretty good tilt). However, it took some mitigation work to save it. I'm not saying at all that this is the future of the home you're looking at. I am saying that mitigation of pretty bad situations is possible.

It sounds like you truly like the home. My advice to you is to find out as much as you can regarding the foundation issue and the surrounding soils. Get as complete a picture as you can, one that you totally understand and trust. Pop for an engineer to look at it. Then get a good idea of what the cost would be to mitigate it, and work that into your decision making. Talk to the neighbors. They probably have issues as well. Go to the town and check permit records. Maybe work has already been done (it certainly looks like something has been done). Also keep in mind that you can mitigate it now, and if it's not done properly, you might have to return to the issue at some point.



Licensed Engineer (NJ)
Licensed Home Inspector
Oak Ridge Engineering
Reply With Quote
  #9  
Old 8/2/11, 5:02 PM
Gary Farnsworth Gary Farnsworth is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,718
Default Re: Vertical crack with leak in cinder block foundation wall

If the home was built in 1925, most where stone or brick foundations. The pictures appears to be an addition, perhaps two with the improper block stack. Here in KC, concrete blocks were not used for foundations until WWII.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #10  
Old 8/3/11, 10:12 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Vertical crack with leak in cinder block foundation wall

That crack is a warning to have an evaluation done.
In my opinion CMI Cement Masonry Units where not meant for underground foundation placement. They do not provide the same amount of protection as a monolithic pour of concrete.
That being said.
Under certain conditions CMU's can last a long time.
A proper barrier in place and proper drainage.
Footing dainage. http://www.inspectapedia.com/exterio...ing_Drains.htm
Dimple board for foundations. http://www.waterproofmag.com/back_is..._membranes.php
Geo fabric as a barrier before land or back-fill. http://www.boddingtons.us/civils/geo...ion-fabric.htm.
Maintenance. Drainage checked tri-yearly by a drainage professional.

I see a lateral load and or uplift .
Suspect Uplift.
Recommend a structural engineer or foundation specialist to report on the issue...



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 8/3/11, 10:35 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Vertical crack with leak in cinder block foundation wall

Attachment 47106
Attachment 47105
It seems to be leaking or wicking moisture. ( paint scaling )
The crack is uniform not at the butt joints or masonry and straight up and down. ( that is my observation )
It looks like it has had a repair.
I suspect lift.
The CMU's size change may be where the unit ( foundation ) is exposed to the land, at grade.
Ether way, changing from one size to another should not allow for load bearing deferential to crack in that manner. It would put horizontal pressure to lean outwards on the footer slightly if not centered. ( my opinion )( no evidence )
Vertical cracks in CMI's can be caucused by load, lift and settlement.
The top being wider will mean lift.
If the bottom is wider then settlement maybe the cause.
With horizontal ( side loading ) la tendency for serpentine cracking and bulging inward, being a basement. Staggered to one side and carry for xx number of feet at first.

• Foundation wall cracks that are of uniform width – As this implies that the footing is broken, this poses a major risk that cannot be ignored and must be dealt with as soon as possible.
Foundation cracks mean different thing and you must be a seasoned inspector to know what is happening, or trained in foundation repair.

http://www.onlinetips.org/vertical-cracks-foundation



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Horizontal and vertical cracks in CMU foundation Brandon Jasionowski Structural Inspections 19 7/26/11 4:22 PM
Vertical crack through block foundation mdeacon Structural Inspections 12 2/24/10 10:18 AM
Brick veneer flashing mklein Exterior Inspections 6 2/21/10 4:20 PM
Large wall cracks mmerino Interior Inspections 28 1/26/10 1:51 AM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM


All times are GMT -4. The time now is 3:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts