Default Voids in ICF's: thermal imaging?

Will concrete voids in Insulating Concrete Forms (ICF's) show up using thermal imaging? Some types of ICF's have a real problem with this.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #2  
Old 6/9/07, 11:27 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by kshepard
Will concrete voids in Insulating Concrete Forms (ICF's) show up using thermal imaging? Some types of ICF's have a real problem with this.
Not likely, unless they are very large. Also too much insulation. Check with ITC or FLIR. They probably (likely) know something I don't



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #3  
Old 6/12/07, 9:38 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by kshepard
Will concrete voids in Insulating Concrete Forms (ICF's) show up using thermal imaging? Some types of ICF's have a real problem with this.
ken:
where are you getting this info on icf's?

a
Reply With Quote
  #4  
Old 6/12/07, 10:12 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by kshepard
Will concrete voids in Insulating Concrete Forms (ICF's) show up using thermal imaging? Some types of ICF's have a real problem with this.
From my experience it is not a problem with the forms, it's usually the installers.

My 2c's



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #5  
Old 6/12/07, 10:28 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by sfalvey
From my experience it is not a problem with the forms, it's usually the installers.

My 2c's
it would always be the installers. the icf's are engineered ok. alot of the icf's are more narrow and have obstructions, so placing and vibrating and coming up in lifts are more difficult to control than in "regular" forms. which means that the worker-bees will get careless if unsupervised or untrained.

i'm wondering where the information is coming from saying that voids are a common problem. says who? i'm not being sarcastic, but am wondering if some organization has really looked into this or is it anecdotal?
Reply With Quote
  #6  
Old 6/12/07, 10:53 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Voids in ICF's: thermal imaging?

It would also be the slump that is used. Too dry of a mix won't vibrate down properly through all the supports and rebar creating voids, too wet of a mix and all the aggregate falls to the bottom and you lose your strength. Vibrate the ICF's too much and watch a couple of yards of concrete blow out through your forms.

ICF's are great (in my opinion) but its all in the installation (as is the case with many materials).



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #7  
Old 6/12/07, 10:58 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by sfalvey
It would also be the slump that is used. Too dry of a mix won't vibrate down properly through all the supports and rebar creating voids, too wet of a mix and all the aggregate falls to the bottom and you lose your strength. Vibrate the ICF's too much and watch a couple of yards of concrete blow out through your forms.

ICF's are great (in my opinion) but its all in the installation (as is the case with many materials).
why do you think over vibrating would blow the form?
it's a pretty rare day when a crew will pour a mix that is too dry!
Reply With Quote
  #8  
Old 6/12/07, 11:28 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by afrost
why do you think over vibrating would blow the form?
it's a pretty rare day when a crew will pour a mix that is too dry!
I've seen it happen



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #9  
Old 6/13/07, 12:14 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by afrost
ken:
where are you getting this info on icf's?

a
I knew the job supervisor. He and I and the general had all worked with ICF's before wtih no problem. The rep for this ICF company lived accross the street from the job. Slump was the first thing I brought up when I stopped by the job to say hello and saw them tearing off foam. They were not happy campers.

I've forgotten what the slump was but he had paid particular attention when ordering it. I saw the general at a meeting this spring and he didn't even want to hear about it.

That said, I think most ICF's are relatively problem free and are a good product.

The first LEED for Homes home in Boulder, even got a brick ledge...




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 1:39 AM..
Reply With Quote
  #10  
Old 6/13/07, 8:32 AM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by kshepard
I knew the job supervisor. He and I and the general had all worked with ICF's before wtih no problem. The rep for this ICF company lived accross the street from the job. Slump was the first thing I brought up when I stopped by the job to say hello and saw them tearing off foam. They were not happy campers.

I've forgotten what the slump was but he had paid particular attention when ordering it. I saw the general at a meeting this spring and he didn't even want to hear about it.

That said, I think most ICF's are relatively problem free and are a good product.

The first LEED for Homes home in Boulder, even got a brick ledge...
so it was just this one incident? your first post says "some icfs have this problem" & it sounded like you had info about a trend.

why were they "tearing off foam"?

didn't they pump this in? if it went thru the pump it should have been able to fill the icf cavity.
Reply With Quote
  #11  
Old 6/14/07, 12:10 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Voids in ICF's: thermal imaging?

Quote:
Originally Posted by afrost
so it was just this one incident? your first post says "some icfs have this problem" & it sounded like you had info about a trend.

why were they "tearing off foam"?

didn't they pump this in? if it went thru the pump it should have been able to fill the icf cavity.
Poor description on my part. One incident, pumped mud, they were tearing off foam where they found voids (probing I think) and were going to form across the inside face with plywood forms and fill the area with concrete. This was about two years ago and I was there for 20 minutes. I can call the foreman and find out more if anyone really wants to know.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermal Imaging for Home Inspectors Milwaukee Tuesday September 25th dnice General Inspection Discussion 7 9/10/07 11:28 PM
Thermal Imaging for Home Inspectors Milwaukee Tuesday September 25th dnice Inspection Education & Training 5 9/10/07 11:26 PM
Thermal Imaging for Home Inspectors Milwaukee Tuesday September 25th dnice General Inspection Discussion 14 9/6/07 12:55 PM
Thermal Imaging for Home Inspectors Milwaukee Tuesday September 25th dnice Miscellaneous Discussion for Inspectors 0 8/29/07 11:06 PM
Thermal Imaging for Home Inspectors Milwaukee Tuesday September 25th dnice Miscellaneous Discussion for Inspectors 0 8/22/07 6:28 PM


All times are GMT -4. The time now is 3:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts