Default Wall Call

I was suprised that the interior didnt show major water damage or movement by the driveway settiling at least 6 inches.

My question is at the bottom of the concrete wall it appeared the wall was moving. This wall wasnt the driveway side but there was moisture and a vertical crack.

Looks like the drain tile may be plugged and this may be causing some movement. It is hard to see from the picture but at the moisture stain it look like the block was seperated. Isnt the term called shearing.

This house has some settlement issues. Driveway/porch/steps/walks/walls

This house has issues.

Dave

Last edited by dmacy; 1/9/08 at 4:21 PM..
Reply With Quote
  #2  
Old 3/6/06, 7:41 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Wall Call

Hi. David;

From the photos you supplied, I would imagine the all this settling at the exterior, would be disturbing for anyone.
I personally think that the settling is due to improper compaction of the soils around the foundation, or the foundation drainage is washing away all the fines from the backfill due to no stone or fabric installed over the perimeter drains.

Sagging or settling of the exterior grade will not necessarily mean that movement will occur on the foundation of the structure itself.

Water penetration through the soils and settlement could, although induce unnecessary pressures to the foundation, and any inferior structural deficiencies in the wall could eventually promote leaks in the basement.

I would strongly suggest site evaluations by an Expert and have the perimeter drains evaluated as to functional or not.

Considering, that this foundation is of CMU, it is not very tolerable to undue pain.

Hope this helps.

Marcel
</IMG></IMG>
Reply With Quote
  #3  
Old 3/7/06, 5:08 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Wall Call

What's with the salt in the pictures? Or is that cocaine? A drug house?
Reply With Quote
  #4  
Old 3/7/06, 6:15 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Wall Call

Quote:
Originally Posted by dmacy
Looks like the drain tile may be plugged and this may be causing some movement. It is hard to see from the picture but at the moisture stain it look like the block was seperated. Isnt the term called shearing.
It's usually better to just describe what you see, than guessing at terminology for whats happening ... which is hard to access from just photo's. Observe and Report, thats the job ...

Also be careful attributing a cause to a possible problem as there are all kinds of reasons it may be happening. If they fix the drain tile and the cause is actually a weak wall or soil issue, what then? ... and who is going to be getting out the checkbook?

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 3/7/06, 10:57 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Wall Call

Don't you just [U]love[U] it when the stupid driveway and/or concrete people put the concrete right up against the outside wall? 70% of the time, with a negative slope.

What are they thinking?

Guess they are not.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 3/7/06, 11:05 AM
Adam J. Slimack Adam J. Slimack is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Clarence, NY
Posts: 162
Default Re: Wall Call

Quote:
Originally Posted by wdecker
Don't you just [u]love[u] it when the stupid driveway and/or concrete people put the concrete right up against the outside wall? 70% of the time, with a negative slope.

What are they thinking?

Guess they are not.
See that around my area alot. You'll see a 15-20 year old subdivision with a row of homes with all of the driveways settled before the garage resulting in a 3 inch step up into the garage. Looks as though the same co. installed all of them.

My assumtion is that when they back-fill next to the foundation, they are careful not to put too much pressure against the wall and in doing so, don't adequately compact the area nearest the home. The only solution i could think of to avoid this wound be to more allow for settling of the base material, prior to installing the finished driveway.

Adam, A Plus

Last edited by aslimack; 3/7/06 at 11:10 AM..
Reply With Quote
  #7  
Old 3/8/06, 5:49 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Wall Call

Quote:
Originally Posted by aslimack
My assumtion is that when they back-fill next to the foundation, they are careful not to put too much pressure against the wall and in doing so, don't adequately compact the area nearest the home.
It's also a lot easier to just dump the soil and walk away, as opposed to using light plate compactors on thinner soil lifts to adequately compact the backfill ...

I can't remember the last time it was done right, but I don't think isn't a real serious issue as long as there isn't a driveway adjacent to the foundation.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 3/8/06, 3:59 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Wall Call

"Excessive settling of soil visible around home perimeter. Foundation appeared sound, indicating that the problem is limited to the area of backfill. Cause of apparent backfill settling will require evaluation by a qualified soils engineer."
-Kent
Reply With Quote
  #9  
Old 3/8/06, 4:09 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wall Call

Subsidence.

As to the porch, would this be a fruitcellar? It is common in 1940-50's homes to have a porch like this which is a fruit cellar, most commonly buit with concrete block. It is also typical in my area to see them settle away from the house. Then again maybe this is just a porch with improper footings (i.e. not below the frost line, and or drainage issues)
Reply With Quote
  #10  
Old 3/9/06, 6:18 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Wall Call

Quote:
Originally Posted by kshepard
"Excessive settling of soil visible around home perimeter. Foundation appeared sound, indicating that the problem is limited to the area of backfill. Cause of apparent backfill settling will require evaluation by a qualified soils engineer."
-Kent
Although as an engineer also I don't like giving away referrals, that type of situation may not need an engineer. A good sitework contractor can look at it, and simply raise the grade around the house and at the driveway ... pretty simple, unless you also suspect settlement of the foundation. Then the SE call is better.

The designs/repairs I have done, and what the better builders do, it to bring the top of foundation up a little and increases the grade/slope away from the foundations above the minimum (6" in 10 feet). Then when (not if ... lol) the backfill settles, you don't end up with a negative grade towards the house ...

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 3/9/06, 10:12 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wall Call

Quote:
Originally Posted by rray
What's with the salt in the pictures? Or is that cocaine? A drug house?
RR. when water vaper from ecumulus nimbus (clowds) cools and falls back to earth, we call that SNOW. or salt for your margaritas if it's in your yard.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 10:48 AM
No Brick Ties - Wall Buldge Stew Structural Inspections 1 4/22/06 6:56 AM


All times are GMT -4. The time now is 3:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts