This is one of three wood supports (6x6) but the only one warped. House built in the mid 80s. How significant is this? Would a SE be necessary to determine if correction is necessary? I found no other issues.
Attached Thumbnails
warped-support-042.jpg   warped-support-049.jpg   warped-support-051.jpg  



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/21/11, 6:24 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Warped support

It will probably get worse, just recommend replacement.
When lumber bows like this and is holding up a lot of weight, it will bow even more, causing what ever it is holding up to be more unlevel.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks

Last edited by jbraun; 9/21/11 at 8:24 PM..
Reply With Quote
  #3  
Old 9/21/11, 6:59 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Warped support

I don't see failure due to the bowing of the 6x6 member, but due to aesthetics, you might want to replace.
What I do see, is that they installed the post on underground sonotubes or some sort of footing and poured the slab around the post.
Even though the PT posts are rated for ground contact at .4 retention, I would recommend that the post be installed on top of the slab above the pier footing with the proper post base as manufactured by Simpson.
The expansion of the wood and the concrete cause the slab to break due to the narrow slab edge around the post.
The post should be removed, with the hole filled down to its foundation support, slab edge repaired and new post installed on top of the slab with proper post base support.
No need to recommend an SE here. Just recommend a qualified builder to correct.
Reply With Quote
  #4  
Old 9/21/11, 7:13 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Warped support

Thanks for the help. I'll recommend replacement with Marcel's recommendation.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 9/21/11, 7:30 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Warped support

Marcel:

I do not agree with this not having catastrophic failure. There is a great deal of weight in that over hang being supported by 6x6. This should be either changed to two or one 8 inch round.
I do agree with the break out on the slab and no you do not need a PE.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 9/21/11 at 7:34 PM..
Reply With Quote
  #6  
Old 9/21/11, 7:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Warped support

David, I would not comment on how it should be repaired. Leave that up to the qualified builder.
Recommend replacement.
Reply With Quote
  #7  
Old 9/21/11, 7:36 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Warped support

Agreed.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 9/21/11, 7:37 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Warped support

Quote:
Originally Posted by kwood View Post
Marcel:

I do not agree with this not having catastrophic failure. There is a great deal of weight in that over hang being supported by 6x6. This should be either changed to two or one 8 inch round.
I do agree with the break out on the slab and no you do not need a PE.
You are allowed to voice your opinion, but in mine oppinion, I do not see a problem here unless there is a 90 mile wind. The weight on those post from what I see is miniscul for a 6x6 post.
Reply With Quote
  #9  
Old 9/21/11, 7:49 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Warped support

It all depends on what that overhang is made of. From what I can see there is one 6x6 supporting 10-15 feet of over hang. If it was not bent I would not make any mention of it.
Since it is holding the whole section and may be attached by nails this makes it even worse.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 9/21/11, 7:54 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Warped support

Kevin, again that is an opion and mine is that it should be left to a qualified builder to assess and evaluate the condition. We do not see the whole picture from those pics.
Do you know how many kips a 6x6 x8' high can support?
Reply With Quote
  #11  
Old 9/21/11, 9:25 PM
Pete Campbell's Avatar
Pete Campbell Pete Campbell is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: Fort Pierce, FL
Posts: 592
Default Re: Warped support

Quote:
Originally Posted by dokeefe View Post
This is one of three wood supports (6x6) but the only one warped. House built in the mid 80s. How significant is this? Would a SE be necessary to determine if correction is necessary? I found no other issues.
Good question, David. No SE needed (and try not to rec. SE too much, after all, that is what you have been hired to do).

Remove and replace. The bowing post cannot possibly get any better on it's own, and its effects on the slab are showing. With the wild weather this year, no one will question your call.





Pete Campbell

pete4545@comcast.net
http://www.PortStLucieInspections.com
http://www.ChooseGI.com
http://ifwemissitwewillfixit.com


Inspecting Fort Pierce, St. Lucie Village, Lakewood Park, Vero Beach, Indian River Shores, Sebastian, Fellsmere, Fort Drum, Okeechobee, Jensen Beach, Stuart, Palm City, Hobe Sound and Indiantown, Florida.
Reply With Quote
  #12  
Old 9/22/11, 8:45 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Warped support

That column is unstable and needs to be replaced. And because it is already bowed, it could completely fail very suddenly.

Columns fail by buckling, and anytime the load is outside the middle third of the column it's considered unstable. That one is out of plumb by way more than 1/3 the width. The bowing also creates eccentric loading on the column which increases the stresses and the likelihood of failure.

JMO & 2-Nickels ...
.
Attached Thumbnails
warped-support-column-instability.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 9/22/11 at 8:52 AM..
Reply With Quote
  #13  
Old 9/22/11, 9:05 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Warped support

Was there a footing beneath the columns? I carry a 2' long screw driver and probe areas like that. Probably not based on the cracking I saw. Warped column is a structural issue.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another way to support a house dvalley Exterior Inspections 3 10/30/09 3:45 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM


All times are GMT -4. The time now is 3:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts