  #1  
Old 4/23/07, 3:59 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default You make the call?

Explain why.

Last edited by dmacy; 6/26/07 at 7:46 PM..
Reply With Quote
  #2  
Old 4/23/07, 4:03 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: You make the call?

Here is an additional photo.

Last edited by dmacy; 5/11/07 at 2:39 PM..
Reply With Quote
  #3  
Old 4/23/07, 4:09 PM
jkormos's Avatar
jkormos jkormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 641
Default Re: You make the call?

What did the footing look like for the chimney, I would definitely call this out. The separation just from the point of the photos is rather scary,. What did this look like from the inside? A call out at minimum for a qualified masonry contractor or Structural PE.



Joe Kormos
A-1st Look Home Inspectors Inc.
630-201-0933
Your 1st Choice in Property Inspection Professionals
www.a-1stlookhomeinspectors.com
www.a-1stlook.com
Let us look before you buy...for peace of mind
“Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford
Reply With Quote
  #4  
Old 4/23/07, 4:15 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: You make the call?

Quote:
Originally Posted by jkormos
What did the footing look like for the chimney, I would definitely call this out. The separation just from the point of the photos is rather scary,. What did this look like from the inside? A call out at minimum for a qualified masonry contractor or Structural PE.
Footing seemed OK. This is an exterior chimney how can you check from the inside.

The added picture is not the one in the post. I had to make sure this was no longer in use. As you can see it doesnt vent to the outside.

What are the requirements when an exterior chimney is used for the HVAC/Tank? Does it have to have a liner?

Last edited by dmacy; 5/11/07 at 2:39 PM..
Reply With Quote
  #5  
Old 4/23/07, 5:03 PM
jkormos's Avatar
jkormos jkormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 641
Default Re: You make the call?

If it was for an FP you could look up the flue, but since it is for HVAC, a flue liner would help. But first it will need to be determined as to why it is pulling away from the building, if that were to collapse, not to be an alarmist, it could kill someone if it were to fall.



Joe Kormos
A-1st Look Home Inspectors Inc.
630-201-0933
Your 1st Choice in Property Inspection Professionals
www.a-1stlookhomeinspectors.com
www.a-1stlook.com
Let us look before you buy...for peace of mind
“Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford
Reply With Quote
  #6  
Old 4/23/07, 5:28 PM
Dave Morris Dave Morris is offline
New User
 
Join Date: May 2005
Posts: 32
Please Note: Dave Morris is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

you would be asking for it if you didnt call it out. It may have been this way for 30 years but that isnt for us to decide. at any rate, I wouldnt want the gap between the house and chimney even if it fine structurally.
Reply With Quote
  #7  
Old 4/23/07, 7:54 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

are those brick ties in photo #2? if so, it looks like the ties stayed fastened to the house and slid out from the masonry!
call it out. the masonry should have been tied back to the wood studs with metal brick ties. movement is unacceptable. (fix might include tear down and rebuild) hardhat area.
Reply With Quote
  #8  
Old 4/23/07, 11:16 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: You make the call?

Be careful reporting "chimney pulled away from house" unless you are sure that it is not the house that moved.

Especially on log homes, the most frequent cause is that the house pulls away from the chimney as the logs dry out.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 4/24/07, 7:38 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: You make the call?

Further review needed.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 4/24/07, 7:58 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

Building codes require that masonry chimneys be constructed with at least a 1-2" clearance to combustible materials. Clapboard siding is a combustible material and the clearance from the chimney to its surface is mandatory.

R1001.15 of the 2003 International Residential Code and R1003.18 of the 2006 International Residential Code both state:

Quote:
"Any portion of a masonry chimney located in the interior of the building or within the exterior wall shall have a minimum air space clearance to combustibles of 2 inches (51mm). Chimneys located entirely outside the exterior walls of the building, including chimneys that pass through the soffit or cornice, shall have a minimum air space clearance of 1 inch (25.44mm)."
The 'ties' you see are likely for horizontal anchorage of the chimney.

Seems to me that the chimney is constructed properly and that the 'gap' to the structure is intentional and required to be there.

Nothing wrong with the chimney.

I voted 'satisfactory'.

Last edited by homebild; 4/24/07 at 8:28 AM..
Reply With Quote
  #11  
Old 4/24/07, 9:39 AM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

the soffit should also have the 1" space.

the gap needs to be closed, tho. i'm unsure how that is typically done.

Last edited by afrost; 4/24/07 at 10:05 AM..
Reply With Quote
  #12  
Old 4/24/07, 10:50 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

If the gap were larger at the top than at the bottom, or if the chimney itself were not perfectly straight, I would be concerned. If the chimney is tied to the house at certain intervals, then I see nothing wrong with it as shown. One might want to close the gap for cosmetic reasons, and there are several ways to do that...wood trim, metal angles, etc.
Reply With Quote
  #13  
Old 4/24/07, 12:07 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

trim is allowed to cover gap
Attached Thumbnails
you-make-call-chimney-space.jpg  
Reply With Quote
  #14  
Old 4/24/07, 2:27 PM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

Quote:
Originally Posted by homebild
Building codes require that masonry chimneys be constructed with at least a 1-2" clearance to combustible materials. Clapboard siding is a combustible material and the clearance from the chimney to its surface is mandatory.

R1001.15 of the 2003 International Residential Code and R1003.18 of the 2006 International Residential Code both state:



The 'ties' you see are likely for horizontal anchorage of the chimney.

Seems to me that the chimney is constructed properly and that the 'gap' to the structure is intentional and required to be there.

Nothing wrong with the chimney.

I voted 'satisfactory'.
How in the world can you quote code on something that was probably built before the code came into effect?
Larry
Reply With Quote
  #15  
Old 4/24/07, 7:31 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: You make the call?

Quote:
Originally Posted by lewens
How in the world can you quote code on something that was probably built before the code came into effect?
Larry
How in the world can you ASSUME that 'code' was not in effect at the time of construction?

Simple answer: You can't.

But since this case study occurs in Ohio, and since Ohio utilizes the International Residential Codes, it's a pretty safe bet there has been some code oversight over the construction of this chimney even if that oversight was under the obsolete BOCA codes.

Irrespective of 'Code', however, what is captured in the initial photos iabove is very 'normal' and a standard practice for masonry chimney construction anywhere.

Clearances need to be maintained to combustible surfaces from masonry chimneys as shown in the photos no matter what the local 'code' requires and regardless of jurisdication.

Masonry chimneys should also be anchored to the structure every so many feet vertically to stabilize them. More anchorage in active seismic zones.

Bottom line:

There is absolutely NOTHING "wrong" or "unusual" about the construction of this chimney apart from what the codes say.

What appears is common, safe, and normal masonry chimney construction practice.

Last edited by homebild; 4/24/07 at 7:37 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Artist or Incompetent, You make the call. bkelly2 Plumbing Inspections 21 3/18/06 6:18 AM
Call centers jcordell General Inspection Discussion 13 1/25/06 11:12 AM
Cell phone "do not call registry" sspradling Miscellaneous Discussion for Inspectors 2 1/11/06 5:35 PM


All times are GMT -4. The time now is 3:40 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts