Inspection Education & Training This is a general forum for inspectors to discuss their educational experience, and to ask questions of InterNACHI's Education Committee. This forum is dedicated to the memory of InterNACHI member and educator Gerry Beaumont. Gerry was an avid proponent of education for inspectors and will be sorely missed.

 
Reply
 
LinkBack Thread Tools
  #1  
Old 11/2/09, 6:50 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

http://www.nachi.org/wind-mitigation...ion-course.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America)
  #2  
Old 11/2/09, 7:14 PM
Ed Bancroft Ed Bancroft is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Brooksville, FL
Posts: 748
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Thanks Nick........!
Reply With Quote
  #3  
Old 11/2/09, 9:00 PM
jnieblas's Avatar
jnieblas jnieblas is offline
Active Poster
 
Join Date: Oct 2009
Location: Miami Lakes
Posts: 188
Please Note: jnieblas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Thank you Nick you always come thru for us...
Reply With Quote
  #4  
Old 11/2/09, 10:06 PM
Christopher B. Thomas Christopher B. Thomas is offline
InterNACHI Member
 
Join Date: May 2005
Posts: 176
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quiz H question 2 does not appear to be correct.

Roof deck attachments must be strengthened and a secondary water barrier must be installed – regardless of the house value.
??



Thomas Enterprising, Inc. President
Wind Certification Entity
http://MySafeHomeInspection.com
1-888-My-Safe-1
1-888-697-2331
Reply With Quote
  #5  
Old 11/2/09, 10:08 PM
Christopher B. Thomas Christopher B. Thomas is offline
InterNACHI Member
 
Join Date: May 2005
Posts: 176
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Also any plans to add training on the completion of the OIR-1802 form?



Thomas Enterprising, Inc. President
Wind Certification Entity
http://MySafeHomeInspection.com
1-888-My-Safe-1
1-888-697-2331
Reply With Quote
  #6  
Old 11/2/09, 10:11 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Yes, once we know it is the final adopted form.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #7  
Old 11/3/09, 9:24 AM
Steve Taylor Steve Taylor is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Atlantic Beach, Fl
Posts: 321
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quiz C Question 7 appears to have a misspeled word. retrained should be restrained?

Sec. 6 Egress & shutters appears to have a misspelled word. swelling should be dwelling?
Reply With Quote
  #8  
Old 11/3/09, 11:10 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quote:
Originally Posted by cthomas View Post
Quiz H question 2 does not appear to be correct.

Roof deck attachments must be strengthened and a secondary water barrier must be installed – regardless of the house value.
??
Christopher,
It's in reference to a summary of the 2007 Florida Mitigation Requirements

When A Roof Is REPLACED: Everywhere in the state of Florida:
Roof deck attachments and fasteners must be strengthened or corrected and a secondary water barrier must be installed as required by Rule 9B-3.0475 F.A.C. as amended 4-6-08 and section 553.844 of the Florida Statutes. This applies regardless of house value.

I'll tweek the question a little. Thanks for your help. How about a free home maintenance book? http://www.nachi.org/now.htm



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
  #9  
Old 11/3/09, 3:31 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quote:
Originally Posted by bgromicko View Post
Christopher,
It's in reference to a summary of the 2007 Florida Mitigation Requirements

When A Roof Is REPLACED: Everywhere in the state of Florida:
Roof deck attachments and fasteners must be strengthened or corrected and a secondary water barrier must be installed as required by Rule 9B-3.0475 F.A.C. as amended 4-6-08 and section 553.844 of the Florida Statutes. This applies regardless of house value.

I'll tweek the question a little. Thanks for your help. How about a free home maintenance book? http://www.nachi.org/now.htm
Ben, the rule that you are refering to has been superceeded by a further ammendment dated 7/17/09 (see below)

Regards

Gerry
Attached Files
File Type: pdf Hurricane Retrofit[1].pdf (23.9 KB, 115 views)



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106


Last edited by gbeaumont; 11/3/09 at 3:39 PM..
Reply With Quote
  #10  
Old 11/3/09, 5:48 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quote:
Originally Posted by gbeaumont View Post
Ben, the rule that you are refering to has been superceeded by a further ammendment dated 7/17/09 (see below)

Regards

Gerry
Gerry,
Hmmm... I admit... It's hard to follow all these changes and amendments, rules and statutes in Florida. There are so many.

However, I believe that the document to which you refer is written by and for Broward County. The Statute that the course refers to is for all of Florida (including Broward).

The Florida Building Commission approved a number of new regulations that inspectors should be aware of.

Pursuant to Section 553.833 of Florida Statutes, strengthening of existing site-built, single-family homes is now required under certain conditions - such as when a roof on an existing site-built, single family residential structure is replaced. Roof-decking attachment and fasteners must be strengthened and corrected as required by the 2007 Manual of Hurricane Mitigation Retrofits for Existing Site-Built Single Family Residential Structures (The Guide,) Section 201.1. A secondary water barrier should be provided as required by section 201.2 of The Guide.


Generally stated: All re-roofing permits for single-family residential structures applied for on or after October 1, 2007 require a secondary water barrier as defined in section 201.2.

Amendments to the ruling 9B-3.0475 Mitigation Retrofits Required has been repealed twice. Once in 4/6/2008 and again in 7/29/2009.

All that being said... The course material teaches that: (a) roof deck attachments must be strengthened and (b) a secondary water barrier must be installed on all retrofits (re-roofings). Which is in agreement with the Broward County document to which you refer.

Thanks, Gerry.

How to Perform Wind Mitigation Inspections
international-association-certified-home-inspectors-releases-online-perfom-wind-mitigation-inspections-course-wind-mitigation-internachi-ben-gromicko.jpg



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book

Last edited by bgromicko; 11/3/09 at 7:09 PM..
Reply With Quote
  #11  
Old 11/3/09, 7:33 PM
Christopher B. Thomas Christopher B. Thomas is offline
InterNACHI Member
 
Join Date: May 2005
Posts: 176
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Also important to note that while the current roofing code requires a SWR be installed on all new roofs many counties allow two layers or 50% overlapped roofing felt to count as a SWR where as the My Safe Florida Home does not consider this a SWR.

Glad to help anytime the end result helps inspectors.



Thomas Enterprising, Inc. President
Wind Certification Entity
http://MySafeHomeInspection.com
1-888-My-Safe-1
1-888-697-2331
Reply With Quote
  #12  
Old 11/3/09, 9:01 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Red face Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quote:
Originally Posted by staylor7 View Post
Quiz C Question 7 appears to have a misspeled word. retrained should be restrained?

Sec. 6 Egress & shutters appears to have a misspelled word. swelling should be dwelling?
Fixed. Thanks!

international-association-certified-home-inspectors-releases-online-perfom-wind-mitigation-inspections-course-roof-edge-damage-wind-mitigation-internachi-ben-gromicko.jpg



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
  #13  
Old 11/3/09, 10:08 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: InterNACHI releases online How to Perfom Wind Mitigation Inspections course.

Quote:
Originally Posted by bgromicko View Post
Gerry,
Hmmm... I admit... It's hard to follow all these changes and amendments, rules and statutes in Florida. There are so many.

However, I believe that the document to which you refer is written by and for Broward County. The Statute that the course refers to is for all of Florida (including Broward).

Sorry Ben posted the wrong .pdf, here's the one you need.

Gerry
Attached Files
File Type: pdf ReferenceDocumentRuleSettlementrev0117081[1].pdf (56.9 KB, 88 views)



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:08 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts