Inspection Education & Training This is a general forum for inspectors to discuss their educational experience, and to ask questions of InterNACHI's Education Committee. This forum is dedicated to the memory of InterNACHI member and educator Gerry Beaumont. Gerry was an avid proponent of education for inspectors and will be sorely missed.

 
Reply
 
LinkBack Thread Tools
  #1  
Old 9/21/06, 10:09 PM
abain abain is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Toronto, ON
Posts: 5
Default Knob and tube

Good day, Nick, Nachi .......
I've just joined this fine group of people and have enjoyed taking several of the online exams.
During the electrical exam there was small chapter on Knob and Tube wiring. Working in Toronto Ontario as a construction site superviser/manager (soon to be home inspecter) doing residential renovations we come across it a lot. One thing this chapter did not discuss was the shared neutral. Perhaps it's a difference of US vs Canadian standards. Your questions did seem to be geared towards US building code requirements. As an example, min height of a railing 5' 11" above grade is 3'6" in Ontario. I do not believe it's the same in the US.
Here in Ontario when Knob and Tube was enjoying its install heyday, there was only one neutral wire installed in the house. In today's modern home, it is all too easy to overload the that lone heavily branched wire. This is the reason Knob and Tube is unsafe and should be replaced in Ontario. Now perhaps in the US Knob and Tube had a neutral for each circuit?
I think you are remiss in not including this information.

Last edited by abain; 9/21/06 at 10:14 PM..
Reply With Quote
  #2  
Old 9/21/06, 10:23 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Knob and tube

Hi to all,

Quote:
Here in Ontario when Knob and Tube was enjoying its install heyday, there was only one neutral wire installed in the house. In today's modern home, it is all too easy to overload the that lone heavily branched wire. This is the reason Knob and Tube is unsafe and should be replaced in Ontario. Now perhaps in the US Knob and Tube had a neutral for each conductor?
I think you are remiss in not including this information.
Alan, as author of this course, I feel equiped to answer your questions.

All my classes are based on US codes in particular IRC 2003 and common sections of NEC, yest there are differences between US and Canadian codes. I am not familiar with CBC. If any Canadian member wants to help me edit any of the on line courses to reflect Canadian codes I would be happy to work with them to do so, and would produce a Canadian version of my classes.

As to the common neutral issue, in the US I have never seen that, in fact with wiring of that period fused neutrals is the bigger issue down here.

Certainly if the system is using a common neutral, it is unsafe and in need of upgrade, whether you live in the US, Canada, or Russia. The neutral is a current carrying component.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 9/22/06, 12:36 AM
abain abain is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Toronto, ON
Posts: 5
Default Re: Knob and tube

Thanks Gerry for the quick reply.
Any Canadian references from me will be from the Ontario Building Code.
I do not presume to know the OBC as well as I think I should. But I would enjoy helping wherever I can. I will subscribe to apropriate threads as I find them or perhaps you can add me to an email list? or some such.
If you would like to warm up to the OBC, it's available (free) online at the Ontario Government website. Although it is buried very deep. I have it as a single file. 14+mb. Just tell me where to post.

Last edited by abain; 9/22/06 at 7:44 AM..
Reply With Quote
  #4  
Old 9/28/06, 8:44 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube

Please provide the link for the material you mentioned.
Reply With Quote
  #5  
Old 9/28/06, 11:32 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Knob and tube

Quote:
Originally Posted by abain
Good day, Nick, Nachi .......
Here in Ontario when Knob and Tube was enjoying its install heyday, there was only one neutral wire installed in the house. In today's modern home, it is all too easy to overload the that lone heavily branched wire. This is the reason Knob and Tube is unsafe and should be replaced in Ontario. Now perhaps in the US Knob and Tube had a neutral for each circuit?
I think you are remiss in not including this information.
Sorry I have never seen two hots run through the home in Canada and only one neutral .
Roy Cooke
Reply With Quote
  #6  
Old 9/28/06, 1:50 PM
abain abain is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Toronto, ON
Posts: 5
Default Re: Knob and tube

http://www.obc.mah.gov.on.ca/userfil..._4_7724_1.html

http://www.e-laws.gov.on.ca/DBLaws/R.../970403a_e.htm

This is not the site I downloaded my files from but it appears to be here as a word doc.
Alan

Last edited by abain; 9/28/06 at 2:00 PM..
Reply With Quote
  #7  
Old 9/28/06, 1:57 PM
abain abain is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Toronto, ON
Posts: 5
Default Re: Knob and tube

I'm sorry, "2 Hot and 1 neutral"?
I need to clarify my statement. 1 neutral is run from the panel and is branched to every outlet and switch.
Reply With Quote
  #8  
Old 9/28/06, 2:05 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Knob and tube

Quote:
Originally Posted by abain
I'm sorry, "2 Hot and 1 neutral"?

I need to clarify my statement. 1 neutral is run from the panel and is branched to every outlet and switch.
I think I am missing some thing Are you saying that there is two hot wires and one neutral .
If this is the case and the two hot wires are 240 volts on opposite phases then the neutral will only be carring the unbalanced part of the load .
Example line one 8 amps line two 3 amps then the neutral will only be carring the unbalanced part of the load in this case 5 amps.
I can not see why the neutral would be going to the switch.
Some how I think you might just have got part of the instruction incorrect.

Roy Cooke
Reply With Quote
  #9  
Old 9/28/06, 7:35 PM
abain abain is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Toronto, ON
Posts: 5
Default Re: Knob and tube

Quote:
Originally Posted by rcooke
I think I am missing some thing Are you saying that there is two hot wires and one neutral .
No.
From the service panel there is 1 neutral wire which services ALL lights and outlets throughout the house. This neutral wire was branched at the electrician's whim, meaning the connections can now be found anywhere and everywhere. In walls, ceiling and attic spaces.
This system was usually installed with a 60 amp service. Most of these have now been upgraded to 100 amp panels, fused and or breakers. In Toronto, I do not know of any insurance company that would insure a home with Knob and Tube.
If you would like me to explain in more detail do not hesitate to ask.
Reply With Quote
  #10  
Old 9/29/06, 11:11 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Knob and tube

Quote:
Originally Posted by abain
No.
From the service panel there is 1 neutral wire which services ALL lights and outlets throughout the house. This neutral wire was branched at the electrician's whim, meaning the connections can now be found anywhere and everywhere. In walls, ceiling and attic spaces.
This system was usually installed with a 60 amp service. Most of these have now been upgraded to 100 amp panels, fused and or breakers. In Toronto, I do not know of any insurance company that would insure a home with Knob and Tube.
If you would like me to explain in more detail do not hesitate to ask.
Nice to have you on board!!Especially from Toronto!!!

Mario





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #11  
Old 9/30/06, 8:09 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube

Quote:
Originally Posted by abain
In Toronto, I do not know of any insurance company that would insure a home with Knob and Tube.
Last I heard, The Co-operators will insure it with an electrician signing off on it of course.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buried Knob & Tube brepanshek Electrical Inspections 14 2/15/07 9:12 AM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
Insulated Knob and Tube? scosta Electrical Inspections 6 2/3/07 6:22 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 7:41 PM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 25 6/27/06 9:51 AM