Default Commercial Inspection - Panic Bars

When installed panic hardware shall be mounted at a height not less than ____ inches?
a. 44 inches
b. 24 inches
c. 30 inches
d. 42 inches
e. 36 inches
Reply With Quote
  #2  
Old 11/9/07, 9:42 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,791
Default Re: Commercial Inspection - Panic Bars

John

I have to go with 42" Our building code only specifies NOT higher than 47" and I guess they forgot to talk about min height.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #3  
Old 11/9/07, 11:45 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: Commercial Inspection - Panic Bars

Good trick question John.

Code minimum allowed and standard mounting heights are two different answers that are not easily interchangeable for Commercial hardware.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 12/16/07, 9:31 PM
jbowman's Avatar
jbowman jbowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,270
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Inspection - Panic Bars

Under normal construction techniques those that selected 36" would be correct. However special considerations are made for Day Care centers and facilities that provide services or housing to shorter individuals. In these facilities a minimum may be as low as 24-inches.



Quote:

APPROVED PANIC HARDWARE

The USBC requires that panic hardware consist of a door-latching assembly incorporating an activating device (typically a horizontal bar or push pad) that causes the door to unlatch when a force is applied in the direction of egress travel. Approved panic hardware must meet the following specifications:
  1. 1. Have a maximum unlatching force of 15 pounds and be capable of one handed operation without special effort or knowledge.
  2. 2. On standard swinging exit doors the activating portion of the releasing device shall extend at least one-half (½) the width of the door leaf (see example below).
  3. 3. On balanced exit doors the activating device must be of the push-pad type and shall
  1. not extend more than one-half (½) the width of the door leaf from the latch side.
  2. 4. The activating device must be mounted at a height greater than 36 inches but less than 48 inches above the finished floor.




http://hisearch.org has over 1,000 hits per month and climbing. Currently ranked #1 in many search engines for determing the age of HVAC equipment. Check it out at http://hisearch.org/hvac.aspx Feel free to bookmark and use our site at any time.

List your business in our Home Inspector Registry with a link exchange. Check out your state now at http://hisearch.org/homeinspectorregistry.aspx Are you listed???
Reply With Quote
  #5  
Old 12/17/07, 11:17 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: Commercial Inspection - Panic Bars

Just thought I would add this in to not cause any confusion.

Although fact that a minimum mounting height for panic devices may be 36",
Most all Commercial Hardware is installed at 41" to the center of the push bars.

Where a vertical rod device may be used, the centerline height would be at 39 & 13/16 off of finish floor. Any other height would cause the top rod or bottom rod to be short or too long.

Residential and light Commercial usually have hardware preparations on the frames and doors set up for 36" centers.

Full commercial hardware, doors and frames are always preped for 41" center hardware mounting.
Commercial hardware will not mix with Residential doors and frames unless custome ordered. Everything from templateing and mounting are usually different.

TOUCH BAR EXIT DEVICES

TH1100EDTBAR - TOUCH BAR


Global Series TH1100EDTBAR “touch bar” style exit devices are suitable for all doors (aluminum, hollow metal, or wood) where there is no projection on the face. Manufactured of extruded anodized aluminum, the TH1100EDTBAR is durable enough for the most demanding applications. A rim cylinder is included, and the EDTBAR can also be used in conjunction with any of the exit device trims listed below.



Specifications
  • MATERIAL: Extruded anodized aluminum push bar, stainless steel springs
  • LATCH: Stainless Steel, 3/4” throw - 5/8” deadlatch
  • BACKSET: 2 3/4” Covers 161 prep, includes latch & strike filler plates
  • STRIKE: Surface mounted for 5/8” stop with shim
  • PROJECTION: 2 1/2” – 1 7/8” dogged
  • STILE: 4 1/4” minimum
  • HANDING: Reversible, non-handed
  • DOOR THICKNESS: 1 3/4” standard
  • DOOR WIDTH: 36”, can be field sized to 30”
  • MOUNTING HEIGHT: Recommended installation at 41" from finished floor to center line of push rail.
  • FASTENERS: Furnished with sheet metal and machine screws
  • CYLINDER: Rim included, all key trims cylinder included except PLED
  • DOGGING: 1/2 turn hex key
  • FIRE RATED: Available - please specify
  • FINISHES: Aluminum, Duronotic, and Stainless Steel
Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 12/26/07, 10:44 AM
sblayney's Avatar
sblayney sblayney is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Mississauga, ON
Posts: 106
Default Re: Commercial Inspection - Panic Bars

Higher the better, not exceeding the recommended code in your area.
44" on center of the bar.



Steve Blayney
Certified Home Inspector
Certified Energy Advisor
NACHI

Property Systems Inspection
416 886-2PSI (774)
sblayney@p-S-i.ca
www.Nachi.org

Remember, no home is perfect!
Reply With Quote
  #7  
Old 12/26/07, 7:38 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,277
Default Re: Commercial Inspection - Panic Bars

24"is also recommended for people confined to Wheelchairs.
Reply With Quote
  #8  
Old 12/27/07, 7:27 AM
jbowman's Avatar
jbowman jbowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,270
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Commercial Inspection - Panic Bars

Quote:
Originally Posted by klott
24"is also recommended for people confined to Wheelchairs.
Ken,

I've been looking for this information. If you don't mind would you share your reference?



http://hisearch.org has over 1,000 hits per month and climbing. Currently ranked #1 in many search engines for determing the age of HVAC equipment. Check it out at http://hisearch.org/hvac.aspx Feel free to bookmark and use our site at any time.

List your business in our Home Inspector Registry with a link exchange. Check out your state now at http://hisearch.org/homeinspectorregistry.aspx Are you listed???
Reply With Quote
  #9  
Old 12/27/07, 10:41 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: Commercial Inspection - Panic Bars

Quote:
Originally Posted by jbowman
Ken,

I've been looking for this information. If you don't mind would you share your reference?
I would be curious also John, for I have never heard of a panic device installed at 2'-0" AFF..

Mounting Heights

Allowable mounting heights for exit devices are the same in each model code: not less than 30" nor more than 44" above the floor. While design may dictate where the push bar is located, consideration should be given in assigning a mounting height to either the lower or upper limits. The lower height is suggested for grade schools, while the upper height may be better suited for adult use, i.e. colleges. Consider where the trim is located on the opposite side of the door, as some manufacturers may have as much as 8"-10" differences between the centerline of the push bar and the centerline of pull trim. This height difference varies, depending on locking functions and type of exit device. Also consider applicable regulations for the physically disabled, as height requirements may vary. ADA (Americans with Disabilities Act) regulations permit 48" maximum height for accessible door hardware, while some state codes have a 42" limit. Some states also require the ends of lever trim to return to within 1/2" of the door face.


NFPA 101 34"-48"
NFPA 5000 same
IBC same
BOCA SBC, UBC 30"-44"

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #10  
Old 12/31/07, 12:44 PM
sblayney's Avatar
sblayney sblayney is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Mississauga, ON
Posts: 106
Default Re: Commercial Inspection - Panic Bars

That's a very good point regarding wheelchair accessiblity! Achieving the best of two worlds is the real challenge. The current bar design does not favor those in the chair, unless the door opens automatically for them. You could almost throw the codes out the window and inspect using our practical and common senses.

I would still stand behind my initial answer of 44" but include an automatic push button between 30"-36" from the ground as a secondary opener for those in wheel chairs.



Steve Blayney
Certified Home Inspector
Certified Energy Advisor
NACHI

Property Systems Inspection
416 886-2PSI (774)
sblayney@p-S-i.ca
www.Nachi.org

Remember, no home is perfect!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Holiday cookie recipes - Enjoy! jonofrey Misc. Discussion 11 11/7/07 9:42 AM
Commercial Real Estate Doing Better than Housing jbushart Misc. Discussion 3 10/23/07 10:34 AM
Commercial Building & Thermal Imaging Course Coming to New Hampshire fcarrio Commercial 1 8/13/07 1:47 AM


All times are GMT -4. The time now is 9:13 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts