Default Duct Throug Fire Resitive Wall Allowances

Duct through Fire Resistive Wall Allowances



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #2  
Old 10/4/08, 7:30 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Duct Throug Fire Resitive Wall Allowances

Does this duct have dampers on both sides of the wall in question?
Reply With Quote
  #3  
Old 10/4/08, 9:58 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,140
Default Re: Duct Throug Fire Resitive Wall Allowances

deleted




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/

Last edited by mcyr; 10/4/08 at 10:42 AM.. Reason: gave answer I guess
Reply With Quote
  #4  
Old 10/4/08, 9:01 PM
Bruce Rickey Bruce Rickey is offline
InterNACHI Member
 
Join Date: Dec 2006
Posts: 3
Default Re: Duct Throug Fire Resitive Wall Allowances

This is a bit of a tricky question as the answer is to be found under IRC Section R309.1.1, Garage Seperation.

It may seem that you would find it under Dwelling Unit Seperation Section R316. Reading further you will find in section R317 that the Townhomes and other such dwellings are to be considered seperate buildings and they are to contain no plumbing or mechanical ducts or vents. This would preclude a duct passing through such wall.
Now in a commercial application depending upon the building use classification, fire and or smoke dampers would be required. The sophistication of which would be dependent upon the use and size of the building.

Last edited by brickey; 10/4/08 at 9:04 PM.. Reason: typos
Reply With Quote
  #5  
Old 10/5/08, 1:11 AM
Chris D. Duphily's Avatar
Chris D. Duphily Chris D. Duphily is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,453
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by brickey View Post
This is a bit of a tricky question as the answer is to be found under IRC Section R309.1.1, Garage Seperation.

It may seem that you would find it under Dwelling Unit Seperation Section R316. Reading further you will find in section R317 that the Townhomes and other such dwellings are to be considered seperate buildings and they are to contain no plumbing or mechanical ducts or vents. This would preclude a duct passing through such wall.
Now in a commercial application depending upon the building use classification, fire and or smoke dampers would be required. The sophistication of which would be dependent upon the use and size of the building.
Agreed - fire/smoke dampers needed.




A2Z Home Inspections
Chris Duphily
RR 1 Box 1107
Dingmans Ferry, PA 18328
Office: 570-371-6696
NACHI06092689
Proudly serving: Stroudsburg PA,Dingmans Ferry PA, Scranton PA and all of: Monroe,Pike,Wayne,lackawanna counties
http://www.a2zpa.com
http://www.a2zpainspections.com
President - Pocono-Northeast PA Chapter of interNACHI


Reply With Quote
  #6  
Old 10/5/08, 5:28 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,642
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by brickey View Post
This is a bit of a tricky question as the answer is to be found under IRC Section R309.1.1, Garage Seperation.

It may seem that you would find it under Dwelling Unit Seperation Section R316. Reading further you will find in section R317 that the Townhomes and other such dwellings are to be considered seperate buildings and they are to contain no plumbing or mechanical ducts or vents. This would preclude a duct passing through such wall.
Now in a commercial application depending upon the building use classification, fire and or smoke dampers would be required. The sophistication of which would be dependent upon the use and size of the building.

Wow no ducts or plumbing in townhomes, who knew?



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #7  
Old 10/5/08, 6:56 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by brickey View Post
This is a bit of a tricky question as the answer is to be found under IRC Section R309.1.1, Garage Seperation.

It may seem that you would find it under Dwelling Unit Seperation Section R316. Reading further you will find in section R317 that the Townhomes and other such dwellings are to be considered seperate buildings and they are to contain no plumbing or mechanical ducts or vents. This would preclude a duct passing through such wall.
Now in a commercial application depending upon the building use classification, fire and or smoke dampers would be required. The sophistication of which would be dependent upon the use and size of the building.
That's why I asked post #2.
Reply With Quote
  #8  
Old 10/5/08, 9:13 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,665
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by bkelly2 View Post
Wow no ducts or plumbing in townhomes, who knew?
Outhouses are back in style!



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 10/5/08, 9:21 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,140
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by lkage View Post
Outhouses are back in style!
Where cross-ventilation was a must without wall penatrations.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #10  
Old 10/5/08, 9:42 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 1,550
Default Re: Duct Throug Fire Resitive Wall Allowances

2 comments -
first this is more of a code question
second - the response will be different for the Canadians - eh!

otherwise - good question



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.

"It is not the strongest of the species that survives nor the most intelligent, but the one most responsive to change." -Charles Darwin
Reply With Quote
  #11  
Old 10/7/08, 8:57 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,642
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by clawrenson View Post
2 comments -
first this is more of a code question
second - the response will be different for the Canadians - eh!

otherwise - good question
Sort of a code question indeed Claude as most of what we inspect has some basis in a code somewhere.

26 gauge steel is the answer I was looking for.

As for smoke dampers David please enlighten me.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #12  
Old 10/8/08, 7:07 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Duct Throug Fire Resitive Wall Allowances

Quote:
Originally Posted by bkelly2 View Post

As for smoke dampers David please enlighten me.
Reply With Quote
  #13  
Old 10/8/08, 7:09 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Duct Throug Fire Resitive Wall Allowances

deleted
Reply With Quote
  #14  
Old 10/8/08, 7:11 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Duct Throug Fire Resitive Wall Allowances

deleted
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Moisture Management mcyr Exterior 15 9/8/08 1:11 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM


All times are GMT -4. The time now is 9:47 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts