View Poll Results: Is this forced air gas furnace flue properly installed?
Yes 4 17.39%
No 19 82.61%
Voters: 23. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #16  
Old 11/26/08, 4:27 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

How many think it will ever get fixed, if it is such a concern?

I vote it will remain the same for the next 20+ years.

Last edited by bdoles2; 11/26/08 at 5:43 PM..
Reply With Quote
  #17  
Old 11/26/08, 4:36 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

I have a good graphic but my upload link seems to be missing on here.
I only have the URL option.

�������������������������������������������������� ��������������������������

gas vent systems using vent caps listed by underwriter
s

laboratories may terminate in accordance with this vent

termination table

roof pitch minimum height
feet meters
flat to 7/12 1 0.3
over 7/12 to 8/12 1.5 0.46
over 8/12 to 9/12 2 0.61
over 9/12 to 10/12 2.5 0.76
over 10/12 to 11/12 3.25 0.99
over 11/12 to 12/12 4 1.22
over 12/12 to 14/12 5 1.52
over 14/12 to 16/12 6 1.83
over 16/12 to 18/12 7 2.13
over 18/12 to 20/12 7.5 2.29





over 20/12 to 21/12 8 2.44

�������������������������������������������������� ��������������������������


gas vent systems using vent caps listed by underwriter




s


laboratories may terminate in accordance with this vent

termination table

roof pitch minimum height
feet meters
flat to 7/12 1 0.3
over 7/12 to 8/12 1.5 0.46
over 8/12 to 9/12 2 0.61
over 9/12 to 10/12 2.5 0.76
over 10/12 to 11/12 3.25 0.99
over 11/12 to 12/12 4 1.22
over 12/12 to 14/12 5 1.52
over 14/12 to 16/12 6 1.83
over 16/12 to 18/12 7 2.13
over 18/12 to 20/12 7.5 2.29





over 20/12 to 21/12 8 2.44
[IMG]file:///C:/Documents%20and%20Settings/bob%20elliott/Application%20Data/M8%20Software/Spartan_Data/Clips/OL12.jpg[/IMG]

Last edited by relliott; 11/26/08 at 4:43 PM..
Reply With Quote
  #18  
Old 11/26/08, 4:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
NO NO Mike

Bob, I did compliance to standards engineering for years. It's not as black and white as you imagine.

You are answering a question with a question.

Yes, to clarify the issue. So?

Your installation guides are all over the internet.
Argue with, them.

I stated from the beginning that the installation guide rules. You did read that right?

Find one that is different from what I referenced.

Irrelevant. Do you have all of them?

Why does a brick veneer wall need a one inch space rather than a 3/4 inch space? I do not know that either.

Because that's why.

Ever hear of the 3-2-10 rule.? Me too, but I just write it up.


Yes, but that is for the building structure. Ever hear of NFPA 54?

Gee ,am I being hard on this.

Yes, you are being a hard *****


Seriously I would imagine there is something called back drafting , which may come into play.
Explain your back drafting comment please.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 11/26/08 at 5:00 PM..
Reply With Quote
  #19  
Old 11/26/08, 4:58 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by bdoles2 View Post
How many think it will ever get fixed, if it is such a concern?

I vote it will remain the same for the next 20+ years.

Personally I couldn't find anything in my code books that state it has to be 2' above. It does say it has to be 2' above a wall/roof edge within an 8' range - that turbine does not look like a wall. I'd have to say this one would depend on the manufacturer suggestions.
You and me both.
It will be there 20 years from now unless someone replaces the flue or removes the ineffective turbine vent but that's another discussion.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 11/26/08 at 5:02 PM..
Reply With Quote
  #20  
Old 11/26/08, 4:59 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

Mike if it is close to the roof vent , the exhaust may backdraft into the living space.

But you already know this.Now who is giving the hard time.

Do you guys have a problem with uploading pics off your files right now ,as my graphic will explain.
The little paper clip thingy is missing.
Reply With Quote
  #21  
Old 11/26/08, 5:02 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
Mike if it is close to the roof vent , the exhaust may backdraft into the living space.

But you already know this.Now who is giving the hard time.

Do you guys have a problem with uploading pics off your files right now ,as my graphic will explain.
The little paper clip thingy is missing.
How will it defy the laws of physics?

The clip thingy is missing on mine too.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #22  
Old 11/26/08, 5:07 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue



Enough said


Reply With Quote
  #23  
Old 11/26/08, 5:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
Trouble is NFPA doesn't use the term "anything".

12.6.2.1

A chimney for residential-type or low-heat appliances shall extend at least 3 ft. above the highest point where it passes through the roof of a building and at least 2 ft. higher than any potion of a building within a horizontal distance of 10 ft.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 11/26/08 at 5:17 PM..
Reply With Quote
  #24  
Old 11/26/08, 5:15 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

Quote:
Originally Posted by mlarson View Post
Trouble is NFPA doesn't use the term "anything".
This is not from NFPA and not a fire issue.
Reply With Quote
  #25  
Old 11/26/08, 5:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
This is not from NFPA and not a fire issue.
Then explain the "issue" please.

And yes NFPA 54 is relevant for this installation.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 11/26/08 at 5:26 PM..
Reply With Quote
  #26  
Old 11/26/08, 5:28 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

Quote:
Originally Posted by mlarson View Post
Then explain the "issue" please.

And yes NFPA 54 is relevant for this installation.
This code originates from the CABO.

Ye sit is to prevent backdrafting, and no nothing is perfect, but those with more knowledge than you or I have determined this to be the optimum height requirement.
Reply With Quote
  #27  
Old 11/26/08, 5:36 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
This code originates from the CABO.

Ye sit is to prevent backdrafting, and no nothing is perfect, but those with more knowledge than you or I have determined this to be the optimum height requirement.
You haven't explained how the turbine vent proximity will promote backdrafting.

Just seeking clarity Bob. Not picking on you.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #28  
Old 11/26/08, 5:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Quote:
Originally Posted by relliott View Post
This code originates from the CABO.
What is CABO?

Cabo Cabo San Lucas (BCS, Mexico)
CABO Council of American Building Officials ???
CABO Canadian Association of Basketball Officials
CABO Cisplatin, Methotrexate, Bleomycin, & Vincristine (chemotherapy regimen)
CABO Chemical Agents and Agents of Biological OriginCABOChemical And Biological Ordnance



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #29  
Old 11/26/08, 6:12 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue

Quote:
Originally Posted by mlarson View Post
What is CABO?

Cabo Cabo San Lucas (BCS, Mexico)
CABO Council of American Building Officials ???
CABO Canadian Association of Basketball Officials
CABO Cisplatin, Methotrexate, Bleomycin, & Vincristine (chemotherapy regimen)
CABO Chemical Agents and Agents of Biological OriginCABOChemical And Biological Ordnance
Must be the Basketball officials , since it has to do with drafting

Comon Mike, I guess you would argue that a flue vent can hit at a reverse angle , since it will just always rise naturally right?
Reply With Quote
  #30  
Old 11/26/08, 6:20 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Furnace Flue

Bob, you made the claim that back drafting was the issue.

I'm only asking you to explain why.

Am I to believe that heated flue gas will sucked into the discharging turbine and then the attic space or that the the discharge of the turbine will be sucked into the furnace vent by some means?

Again, I am mot claiming it is a good install only that a reason is lackin to hang one's hat on if challenged.

Personally I think it is in a gray area.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 7:11 PM
Furnace flue abolt Inspecting HVAC Systems 3 9/7/08 4:36 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Furnace Flue Skip Erwin Inspecting HVAC Systems 10 3/8/08 11:54 AM
Oil Furnace Flue Clearance jfunderburk Inspecting HVAC Systems 3 2/28/06 8:17 PM