| View Poll Results: What is the maximum resistance of a homes gronding system to earth | |||
| 5 ohms |
|
23 | 46.00% |
| 10 ohms |
|
4 | 8.00% |
| 15 ohms |
|
8 | 16.00% |
| 20 ohms |
|
4 | 8.00% |
| 25 ohms |
|
11 | 22.00% |
| Voters: 50. You may not vote on this poll | |||
![]() |
|
|
LinkBack | Thread Tools |
|
#16
|
|||
|
|||
|
This is one of the real problems that I have with the NEC and codes
In general everything works but the real issue is not that it is legal but is it a good ground Sorry Glad as HI we don't have to go this deep rlb |
|
#17
|
||||
|
||||
|
Richard,
Because you CAN'T......you simply can't argue with a local AHJ about what they demand. They demand a reliable testing method to determine 25 OHMS or less or simply install the 2nd ground rod. Now...if you are saying using a volt meter and doing OHMS is reliable to a AHJ inspector....I need to introduce you to some AHJ's...and some very well known AHJ's ( they help write CODE rulings) Ok....I will take it you are not an electrical contractor.....no problem but their are standards for what testing and requirements will be allowed and most AHJ's have already set up mandates that say regardless of testing they would like (2) ground rods....now I can't tell you why they simply say (2) and then no need to check for OHMS......it is all a matter of "SAFER" is always better with the AHJ.....and 2 is always better than 1 senerio. Also..look........while I DO care.....I am a contractor and the CODE says I have to do this and that...so I do what the code says I have to do...we always drive (2) rods now....1.) because by the time I pay to spend the extra time debating it...our LARGE hammer drill can drive a ROD down in about 3 minutes.....without me lifting a single sledge hammer... I do hear ya......but in the scheme of things it takes too much time, not as accurate as the local AHJ would like as it contains to many varibles that can go wrong and in nearly 100% of the cases now the AHJ will still simply say...BUT I WANT TWO RODS.....so it SHALL BE....... Also......if the building inspector comes and wants (2) rods...do you think me telling him..."Sir, I tested the one and it was fine " will make him happy. Been Their...lol....Done...That....My Brother tries it all the time.....he even has the tester ( which again you can get for about $ 180.00 )...but because the AHJ comes at different times and he is not always their....he is not going to come back to save a few bucks on a ground rod....and the AHJ's atleast here in VA....all demand (2) rods now.....so no point in testing them... Not jumpin on ya brother.....just telling you how it is in the field everyday UPDATE- I am editing this because I wanted to place the link to the earth ground resistance test kit my brother has.....he got it on e-bay for around 180.00 but I see they sell for 199.00 new anyway.. http://www.globaltestsupply.com/test...Tester_Kit.cfm P.S.....He just informed me he DID use it for a local AHJ in Nelson County and the AHJ said he still would not accept it.....he MUST install the 2nd Rod.......just wanted to post that for ya. Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. Last edited by pabernathy; 4/13/06 at 10:05 AM.. |
|
#18
|
||||
|
||||
|
Here in the great state of WV, the three largest electricity providers REQUIRE two ground rods (1/2" copper or 5/8" copper clad) be installed within 6' of one another. All of us who inspect electrical services for connection do not have the liability of measuring resistance to ground, because that utility companies supercede the NEC, which keeps me from being just another a--hole AHJ. Of course, the contractors find other reasons to dislike me
InterNACHI "The HI Organization" |
|
#19
|
|||
|
|||
|
10-4 Paul and Dave
When God speaks we have got to do what he says I am still thinking about older homes where the grounding system is broke If we SEE a problem we will note it -- Just thinking and that is dangerous If it is broke as noted in the inspection (just like an outlet) -- noted and call the electrical contractor Just thinking I find that digging a hole looking for a ground rod INVACEIVE and too much work -- I know in my heart that the rod and clamp are history but I am not going to go that far. I do note that could not find the ground rod and if I can pull the wire out of the dirt I note that it was not attached to a ground rod - safety issue I also note if the phone and cable TV is connected to grounded I think we are all on the same page here -- IS IT SAFE?? Paul the electrical storms are so bad down here we are seeing TVSS units installed outside at the main electrical disconnect point and at the disconnect for the HVAC. I have also seen them blown up like someone shot them with a rifle Good grounding is a very good thing rlb Last edited by rbennett; 4/13/06 at 4:17 PM.. |
|
#20
|
||||
|
||||
|
Richard,
Since someone whom we all KNOW....must have cried and moaned about a post from EC & M online....here is the link for everyone on the 25 ohms or less story I thought you all would like..... Gesssh OLD PEOPLE..... http://www.ecmweb.com/mag/electric_c...ess/index.html Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#21
|
||||
|
||||
|
Hi to all,
why would anyone have an issue with a web page available in the public domain with both a save and print function on it?? Quote:
Gerry "Never underestimate the difficulty of changing beliefs with false facts." (some RWNJ not called Mike) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 Last edited by gbeaumont; 4/13/06 at 8:48 PM.. |
|
#22
|
||||
|
||||
|
EXACTLY.....I tell you why.....because BOOK NERDS know nothing about working electricity in the REAL WORLD so they complain and cry and whine to get posts removed........
I tell you...the NEXT post of mine that is removed because an old man does not like it.......Can KISS my butt goodbye from helping NACHI at all.... Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#23
|
||||
|
||||
|
Amazing.......Truly Amazing the level some will drop....
Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#24
|
|||
|
|||
|
Paul
Some how I have lost the objective -- I thought we were on the same page Have I posted something that you think is out of line.? I agree that the building inspector is god and if he wants 3 ground rods hey lets pound them in. Where I am still thinking is on older homes and I am still thinking. Gerrys posting about DC or AC testing of ground resistance or impedance is another subject. My posting on another thread is more related to your own home as a weekend home owner trying to make your home a safe place to live Install or repair your ground system Hay if I said something wrong I am sorry -- and if your can't take the apologize then KM***** Do we understand each other?? I really would like to keep this to fact and not to emotion Am I on the same page that you are on or should I be on a different thread??? BTW I thank your again to the test equipment link -- I think is is better than a SURETEST rlb |
|
#25
|
||||
|
||||
|
lol....NOOOOOO...not you Richard.........
I posted a interesting article for you......JUST for you and SOMEONE ..I wont call names cried and complained to NACHI to have it removed because of copyright fears...BUT it was NOTHING to fear...hell anyone could download it.... lol.....I dont want to kiss you ***** fella........if I dont like something you say TRUST me I will tell ya.......lol....had nothing to do with you...lol Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#26
|
|||
|
|||
|
10-4 Paul
Have a good day I understand Thanks for the PM -- It made my day rlb |
|
#27
|
||||
|
||||
|
What is scary...is even though HI's dont test it......should know it when looking at the grounding system...and over 40% got this one wrong......OUCH....
Ok........guys come to OHIO.....thehehehehe......WE gonna learn some stuff...and Git Er Done...... Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#28
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
AEMC
Ground resistance Earth testers www.omnicontrols.comMegabras High-end megohmmeters at affordable prices. Up to 20kV test voltages. www.megabras.comGrounding Systems CADWELD grounding materials, ERITECH ground rods, accessories www.erico.com |
|
#29
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey Paul
Who complained? Probably was someone from Arizona or California? I post most of my articles from EC&M and no one has a problem with that so far why here are a few: NACHI electrical trainer's latest articles. NACHI electrical trainer Joe Tedesco has written some great articles. Enjoy: http://www.nachi.org/documents/304ecm15.pdf http://www.nachi.org/documents/305ecm15.pdf http://www.nachi.org/documents/305ecm30.pdf http://www.nachi.org/documents/306ecm15.pdf http://www.nachi.org/documents/306ecm30.pdf http://www.nachi.org/documents/308ecm15.pdf http://www.nachi.org/documents/308ecm30.pdf http://www.nachi.org/tenguidelines.htm About NACHI's Joe Tedesco. Thanks Joe! |
|
#30
|
|||
|
|||
|
Paul,
I sometimes answer wrong to see if I can suck someone in that views the poll before voting. OOOPS, did I say that? tg |
![]() |