Question of the Day These are inspection questions posted daily by members of InterNACHI's Educational Committee.

View Poll Results: The tripping breaker shut down, the bathroom, exterior and dining room outlets.
The circuit was overloaded 24 66.67%
The Dining room should not be on the GFCI circuit 18 50.00%
The bathroom should be on a dedicated circuit 23 63.89%
The exterior outlet should not be GFCI protected 0 0%
Multiple Choice Poll. Voters: 36. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 7/30/06, 10:47 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default QOD for 07/30/06 Electrical

Hi to all,

Todays question is ased on yesterdays new construction inspection.

Where the pool guy was trying to run, a pump, an large fan and a wet vac all of an exterior outlet.

Please click all that apply

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Last edited by gbeaumont; 7/30/06 at 10:51 AM..
Reply With Quote
  #2  
Old 7/30/06, 11:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

lol...I like it when you do electrical questions....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 7/30/06, 11:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

oooohhhhh.......actually I can SPIN this very easy.....lets see what the people answer before I thrown in another possibility.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 7/30/06, 11:18 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: QOD for 07/30/06 Electrical

Dining room has a wet bar sink in it and one of those LARGE water falls from Home Depo thus a wet location.

The breaker did not trip because of a GF but because too much current was drawn

rlb
Reply With Quote
  #5  
Old 7/30/06, 11:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

lol....while the we know if most certainly was NOT up to todays wiring requirements.....I found an interesting image come to my mind as an add on question...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 7/31/06, 8:28 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 07/30/06 Electrical

"The tripping breaker"
Reply With Quote
  #7  
Old 7/31/06, 10:01 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

Quote:
Originally Posted by rwand1
"The tripping breaker"
Yep......was doing the MOONWALK and well.....Tripped !



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 8/3/06, 9:45 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 07/30/06 Electrical

How many of you know that you use to be be able to put the bathroom outlets (all), the front and back door outlets, the basement outlet, and the garage outlet on the same gfci protected circuit?

Yes this was code compliant.
Reply With Quote
  #9  
Old 8/3/06, 11:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

Sure was prior to 1999 NEC.....However they are not CODE officials they are safety officials....and anything that has a potential safety aspect CODE or not will need to be reflected in a report even if it makes the electrician who has to deal with it unhappy.

They are not here to kiss the Electrical Contractors *****.....or the AGENT for that matter...

Yes in the past even the GFCI NOT being on the counter top was CODE....but if the HI does not put it in the report when GFCI is NOT on the counter...past or present construction they are opening themselves up for a potential HEADACHE.......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 8/3/06, 11:44 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 07/30/06 Electrical

Paul

Please reread my post.

Nothing about safety there. Just an example of what they may find.

Like bathrooms must be on their own circuit. Now yes but it is not a big deal unless you have 4 girls using hairdryers at the same time.
Reply With Quote
  #11  
Old 8/3/06, 11:46 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

ahhh......well I know I caught local guys doing it up as far as 2004 without the other AHJ catching it.....now my tactic was to trip the GFCI usually at the panel receptacle.....then LEAVE it off and go to the bathrooms and CHECK THEM....lol.......Find It...and REJECT it....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 8/10/06, 1:50 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: QOD for 07/30/06 Electrical

Paul,

I beg to differ with you on one of your points. First off, if you are inspecting a home, say constructed in 1954, and see no GFCIs on the counter, thenn technically it is NOT a defect.

That is not to say that the inspector should not recommend the installations of ground fault circuit interrupters in any numberr of locations, includng bathrooms, all counter and kitchen island receptacle locations, garages, unfinished basements, damp locations, and exterior receptacle locations.

My point is that there is a difference between a defect and a recommendation. On most residential purchases, there is absolutely no requirement to bring the home up to current standards, unless by specific guidelines, such as with 203K financing.

Sometimes calling out as a defect what is not can lead to headaches as well.

Where the contractor disputes my recommendations or findings, I never argue. I simply ask them to but their rebuttal or recommendation in writing, and on their letter head with license number included.
Reply With Quote
  #13  
Old 8/10/06, 2:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

Quote:
Originally Posted by jfarsetta
Paul,

I beg to differ with you on one of your points. First off, if you are inspecting a home, say constructed in 1954, and see no GFCIs on the counter, thenn technically it is NOT a defect.

That is not to say that the inspector should not recommend the installations of ground fault circuit interrupters in any numberr of locations, includng bathrooms, all counter and kitchen island receptacle locations, garages, unfinished basements, damp locations, and exterior receptacle locations.

My point is that there is a difference between a defect and a recommendation. On most residential purchases, there is absolutely no requirement to bring the home up to current standards, unless by specific guidelines, such as with 203K financing.

Sometimes calling out as a defect what is not can lead to headaches as well.

Where the contractor disputes my recommendations or findings, I never argue. I simply ask them to but their rebuttal or recommendation in writing, and on their letter head with license number included.
Firstly, I do not see anywhere in my POST that I called it a "DEFECT" and we are not speaking of CODE here.....any home that today would require a GFCI at the location is a STRONG recommendation to a client who does not have one....FOR safety reasons...not CODE reasons...

Secondly, Are you not agreeing that suggesting a GFCI is something the HI should do when " STATS" and "PROOF" over the years suggests it is a SAFETY enhancement to suggest it....?



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 8/10/06, 2:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 07/30/06 Electrical

Joe,

You failed to READ my posts.........If the house is after a certain date I listed and the problem is their...it is wrong......in the event of suggesting GFCI's in all cases...I did not mention ANYWHERE that it is a defect....simply a safety enhancement that the HI should suggest....to avoid a possible HEADACHE in the event someone DIES.....the courts could come back and say.....should you have NOT suggested it in light of the changes to code which reflect a concern for the safety......seems to me you agree it SHOULD be suggested.....I never said anything otherwise...

Please do not put words in my mouth fella........I have been doing this TOO many years...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 8/16/06, 7:55 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 07/30/06 Electrical

IMHO making recommendations could come back to bite you.

Are you not looking for defects? Or are you saying "I know what is safe or required now"??????

Where do you stop when making recommendations? Once you make one recommendation are your clients going to assume that you will make "all" the recommendations that this home needs?

Does this make you think?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 9:46 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts