Inspection Question of the Day These are inspection questions posted daily by members of InterNACHI's Educational Committee.

 
View Poll Results: The device shown in the photograph is a _________ ?
Induction damper 12 16.67%
Draft hood 6 8.33%
Barometric damper 51 70.83%
Blow-by duct 3 4.17%
Voters: 72. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 1/16/06, 6:30 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default QOD for 1/16/2006 HVAC

Hi to all,

Here's todays question.

Regards

Gerry

Picture courtesy Joe Griffin
Attached Images
File Type: jpg nowthatsjuststupidgriffin (Small).jpg (40.7 KB, 116 views)



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #2  
Old 1/16/06, 8:22 AM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/16/2006 HVAC

Gerry I really like the copper pipe across the front of it restricting it's movement.
Larry
Reply With Quote
  #3  
Old 1/16/06, 8:22 AM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/16/2006 HVAC

Or was I not supposed to notice that?
Larry
Reply With Quote
  #4  
Old 1/16/06, 10:11 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 1/16/2006 HVAC

Quote:
Originally Posted by lewens
Or was I not supposed to notice that?
Larry
Hi Larry,

No that is fine, in fact I encourage the discussion of what is wrong in the pictures so long as the correct answer is not given until the following day

BTW for my friends in the South this item is part of a piece of equipment designed for heating water so it can be pumped around the house to warm it up, it's called a B-O-I-L-E-R.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106


Last edited by gbeaumont; 1/16/06 at 10:14 AM..
Reply With Quote
  #5  
Old 1/16/06, 2:51 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: QOD for 1/16/2006 HVAC

Never seen one in Sunny South Carolina (not in the Low Country anyhow!)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 1/16/06, 5:46 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: QOD for 1/16/2006 HVAC

Quote:
Originally Posted by gbeaumont
Hi Larry,

No that is fine, in fact I encourage the discussion of what is wrong in the pictures so long as the correct answer is not given until the following day

BTW for my friends in the South this item is part of a piece of equipment designed for heating water so it can be pumped around the house to warm it up, it's called a B-O-I-L-E-R.

Regards

Gerry
Boiler rings a bell Gerry, but where is the south?
Reply With Quote
  #7  
Old 1/16/06, 7:04 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 1/16/2006 HVAC

Quote:
Originally Posted by bkelly2
Boiler rings a bell Gerry, but where is the south?
Brian, in your case that would be Tuscon

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #8  
Old 1/16/06, 8:56 PM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 243
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/16/2006 HVAC

Gerry, I remember those things called boilers. They had them on the first two U.S. Navy ships I was on, we used them there for heat too, as well as propulsion to make the big thing go through the water.
Reply With Quote
  #9  
Old 1/16/06, 10:40 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/16/2006 HVAC

i vote for...
D) a copper pipe.
Reply With Quote
  #10  
Old 1/16/06, 11:54 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: QOD for 1/16/2006 HVAC

Quote:
Originally Posted by gbeaumont
Brian, in your case that would be Tuscon

Regards

Gerry
In that case, I'm not too fond of the South Gerry.
Reply With Quote
  #11  
Old 1/17/06, 5:25 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: QOD for 1/16/2006 HVAC

The word draft is visible in the picture
Reply With Quote
  #12  
Old 1/17/06, 6:28 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 1/16/2006 HVAC

Ooooopps

Nearly forgot, the correct answer to this question is:

Barometric damper

Regards

gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 1/17/06, 9:31 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: QOD for 1/16/2006 HVAC

Ok fine. Give me a Hartford Loop, I'm sure I'll get that right.
Reply With Quote
  #14  
Old 1/19/06, 9:00 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: QOD for 1/16/2006 HVAC

The damper is installed upside down. The adjustable weight is suppose to be on the bottom.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Room size requirement for HVAC supply kweiss Inspecting HVAC Systems 3 6/9/07 6:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
HVAC..definitely my weakness..any help? tneumann Inspecting HVAC Systems 3 1/30/06 5:37 PM


All times are GMT -4. The time now is 1:26 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts