Default Re: QOD for 1/26/07 - AFCI's

Quote:
Originally Posted by jbowman
2008 NEC Language. (Thank-you Joe Tedesco)

210.12(B)Dwelling Units.

All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways , or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type installed to provide protection of the branch circuit.
Oh yeah...He's the man........



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #17  
Old 4/30/07, 4:25 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: QOD for 1/26/07 - AFCI's

Quote:
Originally Posted by jbowman
2008 NEC Language. (Thank-you Joe Tedesco)
210.12(B)Dwelling Units.
All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways , or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type installed to provide protection of the branch circuit.
I don't think anyone is on the 2008 NEC yet ... but good to keep in mind for the future ...

Quote:
Originally Posted by jfarsetta
Here in NY, I have yet to see smoke alarms on AFCIs. Come to think of it, I dont see AFCIS on any newly constructed home bedroom circuits, either.
In NY the Residential Code of New York State (RCNYS) controls the design/construction of homes, which is based on the 2000 IRC that did not have any AFCI requirements (AFCI for BR receptacles added with a 2000 IRC Supplement that NY did not adopt). However I have heard that some inspectors still like to see the circuits to BR receptacles on AFCI's as an interpretation. Probably will be required after the next code revisions ... unless NY makes an exception for dedicated smoke alarm circuits (some talk of that locally).

Also if you get bumped out of the RCNYS into the BCNYS which directly references the 1999 NEC (unusually large/tall or commercial multi-units) it's a different story as AFCI in BR's would then be required.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 4/30/07 at 10:30 PM..
Reply With Quote
  #18  
Old 5/1/07, 6:52 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: QOD for 1/26/07 - AFCI's

Rob,

Is it also true that, for an inspector or municipality in NY State to have a more restrictive interpretation, or requirement, than what the State has adopted, that the municipality needs to submit that interpretation to the DOS for approval first, or it is not enforcable?
Reply With Quote
  #19  
Old 5/1/07, 9:32 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: QOD for 1/26/07 - AFCI's

Quote:
Originally Posted by jfarsetta
Is it also true that, for an inspector or municipality in NY State to have a more restrictive interpretation, or requirement, than what the State has adopted, that the municipality needs to submit that interpretation to the DOS for approval first, or it is not enforcable?
My understanding is that they need to submit whats called an MRLS to the NYSDOS from a local law the municipality passes. They can enforce the local law until the DOS reviews the proposed MRLS and either accepts or rejects it. It's usually pretty hard to get unless there are unusual local circumstances (the state wants everyone on the same page as much as possible ... and I think thats a good thing).

But I have heard that occasionally an inspector wants to see the AFCI's on BR receptacles since it's in the 1999 NEC (used in NY for commercial construction ... and optional for homes), even though it's not a requirement of the RCNYS ... which does not mandate using the NEC for homes if the simplified RCNYS provisions are followed.

And sometimes the code is not whats written in the book ... the code is what the inspector says in written in the book ...

[I still think the whole AFCI issue is a very sticky one for HI's]



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 5/1/07 at 9:39 PM..
Reply With Quote
  #20  
Old 5/2/07, 8:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 1/26/07 - AFCI's

Nah..........if it's 2002NEC to 2005NEC and no AFCI's in the bedrooms....call it out as a safety concern and let the client deal with it.

No arguement on IF they work...WHY they work....should they work.....if the CODE is enforcing it.....just know they are an additional safety measure...call it out as such and move on.

Not a defect..........but could be a safety enhancement...even IF some do not believe AFCI's work.......the life you save MIGHT be your own.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #21  
Old 8/9/07, 3:46 PM
dmoore3's Avatar
dmoore3 dmoore3 is offline
Active Poster
 
Join Date: Feb 2007
Location: Seymour, TN
Posts: 447
Please Note: dmoore3 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/26/07 - AFCI's

Quote:
Originally Posted by jbowman
Is the following statement True or False?

A proposal was accepted for the 2008 NEC requiring AFCI
protection on all 15- and 20-ampere residential circuits. It appears
that this proposal will survive the entire Code process and will be a
part of the 2008 NEC.

Hint: The answer ends with the letter "e".

I think the answer is self evident with the inclusion of the word "all".

I'm not so sure that 'all' 15 and 20 amp residential curcuits COULD be included as AFCI capable.

IMHO
Reply With Quote
  #22  
Old 8/9/07, 4:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 1/26/07 - AFCI's

What it tells me is this....Kitchen Counters.....you will have to place either a GFCI receptacle at the counter top and an AFCI in the panel...or a AFCI/GFCI Breaker in the panel.....either way it does say ALL.....no exceptions I see written otherwise.

Seems to me us code proposal guys now need to inform them that in future additions when talking about GFCI requirements on a counter top...they should just say....GFCI/AFCI's are required...lol

Ok..Ok....I will leave the 2008 NEC® alone for now.....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #23  
Old 8/25/07, 3:23 AM
Justice W. Pitts Justice W. Pitts is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Encino, CA
Posts: 1
Default Re: QOD for 1/26/07 - AFCI's

TRU?E
Reply With Quote
  #24  
Old 1/30/08, 11:36 AM
Steven C. Meyer Steven C. Meyer is offline
Active Poster
 
Join Date: Jan 2008
Location: California/Washington
Posts: 577
Please Note: Steven C. Meyer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/26/07 - AFCI's

Great (and inexpensive) way for manufactures to get their product out on the market!!!! Make it code, and the money rolls in!!! Much of the NEC is items pushed by the industry.
Maybe we should make home inspections mandatory!!!!
Reply With Quote
  #25  
Old 1/31/08, 3:07 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: QOD for 1/26/07 - AFCI's

Where does it say kitchens and bathrooms need AFCI protection?


http://www.afcisafety.org/codes.html#NEC2008



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #26  
Old 2/1/08, 2:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD for 1/26/07 - AFCI's

It doesn't....it almost said that but was revised at the last moment (kinda) to exclude those areas for the 2008 NEC. Read my previous posts a few back of the new virbiage.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #27  
Old 2/2/08, 1:40 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: QOD for 1/26/07 - AFCI's

Thanks Paul



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #28  
Old 3/8/08, 7:16 AM
Ricky K. Kie's Avatar
Ricky K. Kie Ricky K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 358
Default Re: QOD for 1/26/07 - AFCI's

Did they come up with a main disconnect yet that would be cheaper than replacing all the breakers? Lots of wiring. The Electricians are going to have to raise their prices again.
I do think its a good idea though, it could potentally save a lot of lives.
Reply With Quote
  #29  
Old 3/15/08, 7:26 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 1/26/07 - AFCI's

210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Definition: Arc-Fault Circuit Interrupter (AFCI).
A
device intended to provide protection from the effects of
arc faults by recognizing characteristics unique to arcing
and by functioning to de-energize the circuit when an arc
fault is detected.

(B) Dwelling Units.
All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.

FPN No. 1: For information on types of arc-fault circuit
interrupters, see UL 1699-1999,
Standard for Arc-Fault
Circuit Interrupters
.
FPN No. 2: See 11.6.3(5) of
NFPA 72®-2007, National
Fire Alarm Code
®, for information related to secondary
power supply requirements for smoke alarms installed in
dwelling units.
FPN No. 3: See 760.41(B) and 760.121(B) for powersupply
requirements for fire alarm systems.

Exception No. 1: Where RMC, IMC, EMT or steel armored
cable, Type AC, meeting the requirements of 250.118 using
metal outlet and junction boxes is installed for the portion
of the branch circuit between the branch-circuit overcurrent
device and the first outlet, it shall be permitted to
install a combination AFCI at the first outlet to provide
protection for the remaining portion of the branch circuit.
Exception No. 2: Where a branch circuit to a fire alarm
system installed in accordance with 760.41(B) and
760.121(B) is installed in RMC, IMC, EMT, or steel armored
cable, Type AC, meeting the requirements of
250.118, with metal outlet and junction boxes, AFCI protection
shall be permitted to be omitted.

Last edited by jtedesco1; 3/16/08 at 7:24 PM..
Reply With Quote
  #30  
Old 5/2/08, 3:07 PM
Jack R. Robnett Jack R. Robnett is offline
InterNACHI Member
 
Join Date: May 2004
Location: Lubbock, TX
Posts: 47
Default Re: QOD for 1/26/07 - AFCI's

The information below came from our local Square D Rep. off subject for this topic, but I thought it was interesting.

There is only one true way to field test an AFCI and that is by using the test button on the AFCI itself. The Ideal Sure Test units are UL listed as AFCI indicators (not testers). AFCI indicators may not recognize all AFCI breakers, and should not be relied on to determine functionality of an AFCI circuit breaker.
The UL approved method of testing an AFCI circuit breaker is to press the push-to-test button when installed in an energized load center or panel. This test injects a signal into the AFCIs sensor that looks like an arc to the AFCI. A properly functioning AFCI will trip when the test button is pushed.

Paragraph 31.8.1 of the UL 1436 standard requires the AFCI Indicator instructions to effectively state that the test button on the AFCI circuit breaker demonstrates proper operation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Questions with regard to GFCI's and AFCI's and how they work/test. dmull1 Electrical 13 5/17/07 12:13 PM
AFCI's jlomonaco Electrical 10 3/15/07 6:09 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical 19 2/15/07 1:05 PM
Does NACHI still support AFCI's? jtedesco1 Electrical 6 7/28/06 12:38 AM
AFCI's, are they working and saving lives yet? jtedesco1 Electrical 10 4/10/06 9:38 AM


All times are GMT -4. The time now is 8:50 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts