View Poll Results: What is the ALLOWED size GEC to a Ground Rod Electrodes
a.) #10 AWG 5 11.63%
b.) # 4 AWG 3 6.98%
c.) # 6 AWG 26 60.47%
d.) # 8 AWG 9 20.93%
Voters: 43. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 1/9/07, 10:07 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default QOD -1/9/2007 - Electrical

Easy one for today guys....ENJOY !

P.S.... When I am refering to "ALLOWED" we are talking about the one that is ALLOWED to go to the Ground Rods as reference....not the fact it can be LARGER than the allowed.......lets not make this complicated with a bunch of WHAT IF things...simple electrical question....we know the GEC could be larger.....but what is the ALLOWED size it can be.

lol.....let be remove the previous debate thing...I really DO want you guys thinking outside the normal BOX.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 1/9/07 at 5:08 PM..
Reply With Quote
  #2  
Old 1/9/07, 11:15 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

seventeen lookers and five answers . Wonder why .
Roy Cooke
Reply With Quote
  #3  
Old 1/9/07, 11:28 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: QOD -1/9/2007 - Electrical

Paul scared them with this note. ha. ha.

Anyone sho debates otherwise is only doing it to be a smart *****...lol

Marcel

Right or wrong, I'm not going to debate it, hell I am just a dumb carpenter. ha. ha.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 1/9/07, 11:35 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,642
Default Re: QOD -1/9/2007 - Electrical

I believe that would be the minimum allowed size Mr. sho debate.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #5  
Old 1/9/07, 4:47 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: QOD -1/9/2007 - Electrical

Is this gec to a ground rod that is considered a supplemental grounding electrode?

Also, copper right?

tom
Reply With Quote
  #6  
Old 1/9/07, 5:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD -1/9/2007 - Electrical

lol......Yes...also should ALWAYS assume copper and never assume aluminum when doing questions in this type of nature....lol....not the DEBATE I was looking for...I will explain at the end...lol...

OH I welcome debate...but on this question their is one listed answer and their is ONE issue that could be debated....so I was actually doing reverse psychology...lol

Thomas.....Yes..supplimental or primary....does not really matter if it is a supplimental or not.....we are speaking of the ground rods as the sole electrodes in this example...but then again when we are really dealing with the ground rod in normal installations we are dealing with either the primary electrode or supplimental.........not talking about supplimentary...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 1/9/07, 5:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD -1/9/2007 - Electrical

lol.....don't let the debate thing scare away comments....just teasing ya guys...man dont you all KNOW me by now....geesshhh



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 1/9/07, 6:39 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

If I remember correctly #8 is the largest solid copper conductor, and I know I always installed #8 as the grounding conductor. So, I is gona guess #8
Reply With Quote
  #9  
Old 1/9/07, 7:00 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

The question is sorely flawed.

It does not state the conductor material type, although you cleared that up by stating later that it is copper.

The question states what is the ALLOWED, but does not clarify what ALLOWED means. Do you mean what is the minimum allowed copper GEC to a ground rod? Without clarification, there are two answers.

No matter the size of the service, the grounding electrode conductor to a rod electrode is not required to be bigger than a #6 copper. If that conductor is exposed to physical damage, the smallest conductor that can be run where exposed to physical damage is a #4 copper.

If this GEC is for an article 800 installation, there are even more answers.

Solid copper is, indeed, available in many gauges, including #4 and #6. These are sold on 25lb. rolls normally, and not a certain "footage" length roll.
Reply With Quote
  #10  
Old 1/9/07, 7:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD -1/9/2007 - Electrical

Oh for the LOVE of GOD....give it a BREAK Mac.....that is the intent of the QUESTION to encure debate and question.

The question did EXACTLY what it was supposted to do.....chances of the GEC running to a ground rod that has a connection that should be buried in all normal situations could NOT be aluminum.....we wont get into protection if not buried..then again aluminum should not come within HOW many inches of the ground......I'll let YOU answer that one.....and if it did..would it not be a IMPALEMENT issue or safety hazard.

IN an attempt to discredit the question you did not READ the question....

Here is the QUESTION....:
What is the ALLOWED size GEC to a Ground Rod Electrodes?

Now.....I guess we will NOT wait until the end of the day to clarrify this one.....this is for one a Home Inspector website...not a lets confuse the inspector website....so in the question above...

The ALLOWED size to the Ground Rod as stated in the NEC is # 6 AWG and it does not have to be larger....however the point of the debate was to have someone like an HI say.....can't # 4 AWG be used......yep...sure it can...but you are ALLOWED to only run # 6 AWG per the NEC's allowance.

These questions are to make you THINK...not to be an end all......and they will not be ALL enclusive...you only have so much space it will ALLOW you to enter a question....so it has to be brief.....and simple...and make you think...

It can't be a situation where it contains EVERY senerio...just not possible.

Damn I just don't know WHY I keep trying to do this.........I want answers not debate on why I might be WRONG...I am NOT wrong.....I can sit and talk about the varibles for HOURS....we only have short time to go over this...so it has to be brief.

Todd.......that WAS something I was looking for...Great Point.....and the intent of the question as well.......if the service is lets say 125A or smaller it indeed can be # 8 AWG.....as long as it is protected against damage in conduit.

Please before a debate is logged to try and impress and find me wrong.....wait to see what the intent of the QUESTION is.

P.S. Home Inspectors do not inspect for Article 800 or items within that article and associated sections, Not relavant to this question.

I will NOW skip the educational portion of this question..because I am not in the mood now........Have a nice day !



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 1/9/07, 7:23 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

I spose I could run #6 alu. Or is that wrong????
Reply With Quote
  #12  
Old 1/9/07, 7:25 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

Quote:
Originally Posted by Marc D. Shunk
The question is sorely flawed.

It does not state the conductor material type, although you cleared that up by stating later that it is copper.

The question states what is the ALLOWED, but does not clarify what ALLOWED means. Do you mean what is the minimum allowed copper GEC to a ground rod? Without clarification, there are two answers.

No matter the size of the service, the grounding electrode conductor to a rod electrode is not required to be bigger than a #6 copper. If that conductor is exposed to physical damage, the smallest conductor that can be run where exposed to physical damage is a #4 copper.

If this GEC is for an article 800 installation, there are even more answers.

Solid copper is, indeed, available in many gauges, including #4 and #6. These are sold on 25lb. rolls normally, and not a certain "footage" length roll.
I would ask how often this is used in a residential application that may pertain to a Home Inspector?
Reply With Quote
  #13  
Old 1/9/07, 7:30 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,494
Default Re: QOD -1/9/2007 - Electrical

I love reading this BB. Someones asks what time it is and 12 people will try to tell them how to make a watch. Its like watching a herd of BSers. The first liar ain't got a chance.
Reply With Quote
  #14  
Old 1/9/07, 7:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD -1/9/2007 - Electrical

No *****.....so I pass the torch......take it away...whom ever...I am OFF to another engagement.......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/9/07, 7:48 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD -1/9/2007 - Electrical

Quote:
Originally Posted by tallen
I would ask how often this is used in a residential application that may pertain to a Home Inspector?
I have no idea. My head is full of useless trivia. I'd tear 'em up on Jeopardy. Consider it free information.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 3:13 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts