Default QOD 11-1-2006 Electrical

Lets try some electrical questions for the rest of the week.

This is an easy one.
Attached Images
File Type: jpg PANEL.jpg (70.8 KB, 90 views)



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #2  
Old 11/1/06, 11:15 AM
Andrew Rook Andrew Rook is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 202
Default Re: QOD 11-1-2006 Electrical

Grounding Issues - defer to electrician for further evaluation.

--

Andrew Rook
Rook Home Inspections LLC
New Jersey Home Inspector
Hamilton, NJ

Be Smart, Be Sure, Be Inspected TM
Reply With Quote
  #3  
Old 11/1/06, 11:45 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: QOD 11-1-2006 Electrical

I'd probably check the panel with a voltage meter simply because my non contact "pen" goes off within a few inches of a panel. If I rub it on my arm it goes off too. Must be my electric personality.

If all else fails, I'd answer "d". lol



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 11/1/06, 12:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

Defer to the Electrical Experts on the Board...I take the 5th !


NO actually I would call Gerry.......he could tell me what to do....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 11/1/06, 6:03 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: QOD 11-1-2006 Electrical

The problem is that the panel is at ground and the inspector is standing on a electric blanket that is wet

This is the WRONG way to test a panel.

Paul tell them how it is to be done and also give a guess of how many professional electricians test a panel before removing it

rlb
Reply With Quote
  #6  
Old 11/1/06, 9:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

lol....again Richard I defer to the Electrical Experts...I am just an electrician from Virginia......I defer...defer...defer......

On the comment about how many electricians test before removing...I take the 5th....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 11/1/06, 9:52 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

lol...actually one of my helpers ticked me off today so I would probably have HIM go remove the cover....BUT give me 5 minutes with it privatly before I allow him to mess with it........



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 11/1/06, 9:56 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: QOD 11-1-2006 Electrical

Paul

Ok I sort gave you a slider on this one

But lets look at Ohms law -- Panel face plate hot -- that means that screws are connected to the main panel that are connected to a hot box and or a hot wire and no other bolts are connected to the box which are connected to ground or neutral.

In short it is hard to create a hot panel - thus very seldom is it even checked -- Sort of like checking for a gas leak in an all electric home or 120 volts on a phone line.

Yes I could happen but lets get back to reality -- The time to check with the risk = to many 1,000,000 to one does not equate to something that would be even put into an SOP or a MOP

Greg Bell is posting questions and situations that are good for the BB but not something that is close to the real world

If checking to see if a DP should be checked to be hot as part of a MOP then so be it but I would like to see any industry published statement to say do so.

If so I will change my ways

And trust me I am 100% for safety

Paul -- your are in both the HI and the Electrical profession what is your call ??

If Mr Bell off base then call it --- his background is not ohms law

rlb

Last edited by rbennett; 11/1/06 at 10:10 PM..
Reply With Quote
  #9  
Old 11/1/06, 10:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

ahhh........yeah...what RLB said....lol...

Wait.....hell man...I deal in OHMS LAW all the time.....I did not see any MATH on that page...tehehhehehe

HOWEVER........if the panel is IMPROPERLY BONDED and their is a high enough resistance...it is QUITE possible......

WE know that using OHMS LAW.......even a short to a ground rod that lets say for argument sake is 25 OHMS......and apply 120V to it...what is the AMPS....4.8 AMPS on an improperly grounded system will NOT remove stray voltage and could possible cause the equipment ( in this example a street pole for example ) to become energized and NEVER cause a fault situation....

yeah...it could happen...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 11/1/06, 10:23 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

You make some great points Richard......

If the panel itself is not bonded properly, and the system is is missing a GEC for that matter....we loose the balanced potentil argument....so...is it possible for a panel to TICK without tripping the breaker or faulting out....

Personally I think it is quite possible.....

If the panel becomes energized due to lets say a sheetrock screw being used as a panel cover screw......and the panel has not been bonded correctly.....

What is quite scary is that people think the ground rod actually will save them in a situation where they are getting shocked.....

The surface voltage gradients are going to be progressivly less the furthur you are away from the ground rod...IF one was present.....so if one is not present.......the ground rod is useless in this anyway.....where was I...oh sorry....I digressed...

Ok....earth itself is not a good effective ground fault path.....neither is a concrete floor for that matter if you are thinking hell I will just shock myself on a floor......other than earth...

Point is........it is quite possible for a panel that is improperly bonded....and if in the main means no connection between the grounded conductors and the case............now the screw gets in contact with a LIVE ungrounded conductor...the panel COULD possibly hold that voltage and not fault anything out........very possible...

Not sure however as Richard stated that was the intent of the image...heck If I know........personally guys if a panel causes a ticker to light up....I would defer it.........ahhh......have Richard come look at it...lol...

Sorry richard I could not resist



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 11/1/06, 10:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

lol...are you trying to tease me tonight richard...lol...man I am in some kinda pissy mood...lol......in fact half the stuff I say tonight may be wrong because of my mood...lol......but I love ya brother......been a LONG day..lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 11/1/06, 10:40 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

Because the resistance of the earth is so great ( 10-500 OHMS ), very little current will return to the power supply via the earth if the earth is the only ground fault return path...and floor as well in this case. The result is that the circuit OCPD will never trip....metal parts will and could become energized at a lethal touch point known as "Touch Voltage" and just waiting for someone to come in contact with it....

What is touch voltage- it is the potential difference between a grounded ( bonded ) metal structure ( ie:Panel ) and a point on the earth 3 feet from the structure.

Many again think a ground rod can be used to reduce touch voltage, that is proven not true by the research done by the IEEE and NFPA.

1 Foot ( shell 1) has 68% resistance and touch voltage of 82V on a standard 120V connection.....so.....can 82 volts kill ya....

so we know if it is 82 Volts....and the resistance is say 25 OHMS......the amps would be potentially 3.28 AMPS....only takes 1/10th of an AMP to kill......if you are GROUNDED right.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 11/1/06, 10:40 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: QOD 11-1-2006 Electrical

Paul

You and I are the experts

Without going into my background - you have the NACHI blessing as the expert in electrical and as well as Joe T

I can not put my trust in Mr Bell in this area - I can not see changing MOP for electricians and HI's to make this check

Once again if I am wrong I will change my ways and I will start to require that all MOP that I sign off on have a check to see it the panels are hot

Your call Pall -- is Mr Bell off base or not?

rlb
Reply With Quote
  #14  
Old 11/1/06, 10:40 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: QOD 11-1-2006 Electrical

Tell the real estate agent there is a problem with the panel box. He will promptly tell you that you do not know what you are doing and just to show you how smart he is, he will remove the cover panel for you.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #15  
Old 11/1/06, 10:45 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD 11-1-2006 Electrical

Quote:
Originally Posted by rbennett
Paul

You and I are the experts

Without going into my background - you have the NACHI blessing as the expert in electrical and as well as Joe T

I can not put my trust in Mr Bell in this area - I can not see changing MOP for electricians and HI's to make this check

Once again if I am wrong I will change my ways and I will start to require that all MOP that I sign off on have a check to see it the panels are hot

Your call Pall -- is Mr Bell off base or not?

rlb
I am not sure of your question......to be honest with you as I gave my version of "Is is possible "

As for being an expert for NACHI....I think with the removal of me as a paid electrical speaker that your image of my position at NACHI is incorrect...

I will leave JOE T as the only expert.....I am just here to give info....

SO what is your question for me again...I am getting LOST in my own posts tonight...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What happened to the daily... klott Misc. Discussion 25 5/21/07 12:44 PM
Tidbits from the ASHI Message Board jbushart Misc. Discussion 124 4/27/07 12:05 PM
Is the daily doorprize now a "once in a while" doorprize ? jthalmann Misc. Discussion 7 12/1/06 12:34 AM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 8:51 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts