View Poll Results: What would you report the sevice amperage to be??
100 amps 7 26.92%
125 amps 12 46.15%
150 amps 5 19.23%
175 amps 0 0%
200 amps 0 0%
Cannot be determined 2 7.69%
Voters: 26. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 11/16/08, 4:02 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default QOD for 11/16/08 Electrical

Hi to all,,

I still see alot of questions on this subject both on the BB and at my seminars.

Take a look at the image first:

IMG_0082 (Small) (2).JPG

I can give you the following information:
  • 200 amp meter
  • 1/0 AL SECs
  • Panel rated @ 150 amp
Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #2  
Old 11/16/08, 4:12 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: QOD for 11/16/08 Electrical

Gerry,

Don't I just add up all those breakers in the panel to get my Amperage?
Reply With Quote
  #3  
Old 11/16/08, 4:21 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by dvalley View Post
Gerry,

Don't I just add up all those breakers in the panel to get my Amperage?
You can do it that way Dave, but only if you remember to divide the total by the square root of your shoe size (or hat size of course if it's a Leap year)

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 11/16/08, 4:23 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by gbeaumont View Post
You can do it that way Dave, but only if you remember to divide the total by the square root of your shoe size (or hat size of course if it's a Leap year)

Regards

Gerry

I've always divided the total breaker amount by square footage of the home.

No wonder why I'm getting so many calls from Electricians stating that I'm an idiot.
Reply With Quote
  #5  
Old 11/16/08, 5:32 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: QOD for 11/16/08 Electrical

I am not an electrical Guru by far, but would not the rating be as much as the main breaker and the rating of the meter and wire size.?

Known facts;

Meter= 200 amps

Panel= 150

Breaker= ?

Wire size and make Copper or Allum. = ?

How can we guess on the answer.?

Since the amp rating of the panel is 150 that is the maximum it should be, not.?
Can't tell from anything else, but then, I am just a dump hammer swinger

Marcel
Reply With Quote
  #6  
Old 11/16/08, 5:49 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by mcyr View Post
I am not an electrical Guru by far, but would not the rating be as much as the main breaker and the rating of the meter and wire size.?

Known facts;

Meter= 200 amps

Panel= 150

Breaker= ? (yes isn't it!!)

Wire size and make Copper or Allum. = ? (I gave this out 1/0 AL)

How can we guess on the answer.?

Since the amp rating of the panel is 150 that is the maximum it should be, not.?
Can't tell from anything else, but then, I am just a dump hammer swinger

Marcel
I guess you need to stick with the hammer Marcel



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 11/16/08, 5:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by gbeaumont View Post
I guess you need to stick with the hammer Marcel

Thanks, I will remember that one Coon,

Marcel
Reply With Quote
  #8  
Old 11/16/08, 6:03 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by dvalley View Post
I've always divided the total breaker amount by square footage of the home.

No wonder why I'm getting so many calls from Electricians stating that I'm an idiot.

David I have done most of the calculations but I need to plug your shoe size into my equation. Please post your shoe size ASAP.
Reply With Quote
  #9  
Old 11/16/08, 6:44 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: QOD for 11/16/08 Electrical

Alright Gerry, I voted, and now we see how this hammer did. ha. ha.

Hint; I am in the top percentile range right now so is that good or bad. ?

Must be other hammers around.
Reply With Quote
  #10  
Old 11/16/08, 7:53 PM
mjohnson6's Avatar
mjohnson6 mjohnson6 is offline
Active Poster
 
Join Date: Aug 2007
Location: NH
Posts: 175
Send a message via Yahoo to mjohnson6
Please Note: mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

Good one~
The big tip should be 1/0 AL.
Reply With Quote
  #11  
Old 11/16/08, 8:17 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by mcyr View Post
Alright Gerry, I voted, and now we see how this hammer did. ha. ha.

Hint; I am in the top percentile range right now so is that good or bad. ?

Must be other hammers around.
What can I tell you Marcel, take your pick from these 2 quotes
  • Great minds think alike
  • Fools seldom differ
The way to think about this issue is, which component is the lowest rated, as that is the one that becomes the fuse, whether intended to be or not

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #12  
Old 11/16/08, 8:22 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by gbeaumont View Post
What can I tell you Marcel, take your pick from these 2 quotes
  • Great minds think alike
  • Fools seldom differ
The way to think about this issue is, which component is the lowest rated, as that is the one that becomes the fuse, whether intended to be or not

Regards

Gerry
Hey, Gerry, I think I am winning.

What do I win.???

Reply With Quote
  #13  
Old 11/16/08, 8:23 PM
mjohnson6's Avatar
mjohnson6 mjohnson6 is offline
Active Poster
 
Join Date: Aug 2007
Location: NH
Posts: 175
Send a message via Yahoo to mjohnson6
Please Note: mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

I forget are we hammer swingers or blockies?
Reply With Quote
  #14  
Old 11/16/08, 8:24 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: QOD for 11/16/08 Electrical

teaser + or minus shoe size



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 11/16/08, 8:25 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by mjohnson6 View Post
I forget are we hammer swingers or blockies?
Well it sure does look like I am no Sparky Matt.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 2:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM