| View Poll Results: What would you report the sevice amperage to be?? | |||
| 100 amps |
|
7 | 26.92% |
| 125 amps |
|
12 | 46.15% |
| 150 amps |
|
5 | 19.23% |
| 175 amps |
|
0 | 0% |
| 200 amps |
|
0 | 0% |
| Cannot be determined |
|
2 | 7.69% |
| Voters: 26. You may not vote on this poll | |||
![]() |
|
|
LinkBack | Thread Tools |
|
#16
|
||||
|
||||
|
Quote:
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#17
|
||||
|
||||
|
You got me on this one... As I hit the vote button I'm thinking AL wire..... Ohhhhhh too late.
HLC Home Inspections Okla. Lic. #776 I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
|
|
#18
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
It looks like the cable could have a rating of anywhere from 125 A to 170 amp (e.g. TW vs. THHW vs. THHN).
It needs a main breaker rated to the lower of the cable rating or the panel rating. |
|
#19
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#20
|
||||
|
||||
|
Wow, over 200 views and only 25 answers????
Strange Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#21
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
After your comment, I zoomed in and it looks like it may be a split bus with 5 throws to disconnect all power. In that case, I guess it does not need a main shut-off/breaker, except that there should be a shut-off at the exterior (if it is not an exterior mounted panel).
|
|
#22
|
||||
|
||||
|
Please Note:
mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
The answer was 125 Amps.
200 amp meter 1/0 AL SECs<------------ big key. "This is the lowest capacity component" Panel rated @ 150 amp 1/0 "Aluminum" service entrance cable is only rated for 125amps
|
|
#23
|
||||
|
||||
|
Please Note:
mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I guess they didn't want to look bad?~ LOL
My excuse??... I'm either so darn good looking... or.... I just don't know any better! |
|
#24
|
||||
|
||||
|
I'm glad to know I got it right. The second time.... lol I voted for 150A but then clued into it being AL. I keep a note book full of cheat sheets, went and looked it up and saw it should be 125A.
I don't need to remember everything, I just need to know where to look for the answers to everything! HLC Home Inspections Okla. Lic. #776 I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
Last edited by jsopher; 11/19/08 at 9:53 PM.. Reason: type-o |
|
#25
|
||||
|
||||
|
Hi to all,
OK here's the answer The meter is 200 amp The SECs (1/0 AL) are good for 125 amps The panel has no single disconnect (split bus) but has fewer than 6 moves to shut the home down. The panel is rated at 150 amp. I'd be reporting this as a 125 amp supply, in fact I did, this is from one of my inspections. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#26
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
The way I understand it, there are different types of cables, as I stated in one of the early posts. I think the main difference is the type of insulation. Cable insulated with teflon has a higher rating than PVC.
For 1/0 Aluminum, my code check book shows a rating of 100A for TW or UF, 120 for XHHW or USE and 135A for USE-2 or XHHW-2. I had an electrician on site at an inspection one time and I know he was trying to figure out the rating based on the type of wire, not just size. |
|
#27
|
||||
|
||||
|
Hey Gerry, got it right. Not bad for a hammer Eh!
Well, I did get some inside undercover assistance. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#28
|
||||
|
||||
|
Quote:
I definately agree on the differences in cable types however my code book shows the following for service entrances. 2 AL = 100 amps 1 AL = 110 amps 1/0 AL = 125 amps Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#29
|
|||
|
|||
|
Please Note:
rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks to be upside down?
|
|
#30
|
|||
|
|||
|
lol......guess not enough people watched my sizing video before I removed it from the web....lol
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Handbook for Electrical Safety | pabernathy | Electrical Inspections | 1 | 1/1/07 1:14 PM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |