| Question of the Day These are inspection questions posted daily by members of InterNACHI's Educational Committee. |
| View Poll Results: What would you report the sevice amperage to be?? | |||
| 100 amps |
|
7 | 26.92% |
| 125 amps |
|
12 | 46.15% |
| 150 amps |
|
5 | 19.23% |
| 175 amps |
|
0 | 0% |
| 200 amps |
|
0 | 0% |
| Cannot be determined |
|
2 | 7.69% |
| Voters: 26. You may not vote on this poll | |||
![]() |
|
|
LinkBack | Thread Tools |
|
#16
|
||||
|
||||
|
Quote:
Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#17
|
||||
|
||||
|
You got me on this one... As I hit the vote button I'm thinking AL wire..... Ohhhhhh too late.
HLC Home Inspections Okla. Lic. #776 I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
|
|
#18
|
||||
|
||||
|
It looks like the cable could have a rating of anywhere from 125 A to 170 amp (e.g. TW vs. THHW vs. THHN).
It needs a main breaker rated to the lower of the cable rating or the panel rating. "An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold Eureka, Fortuna & Arcata, CA
|
|
#19
|
||||
|
||||
|
Quote:
Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#20
|
||||
|
||||
|
Wow, over 200 views and only 25 answers????
Strange Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#21
|
||||
|
||||
|
After your comment, I zoomed in and it looks like it may be a split bus with 5 throws to disconnect all power. In that case, I guess it does not need a main shut-off/breaker, except that there should be a shut-off at the exterior (if it is not an exterior mounted panel).
"An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold Eureka, Fortuna & Arcata, CA
|
|
#22
|
||||
|
||||
|
Please Note:
mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
The answer was 125 Amps.
200 amp meter 1/0 AL SECs<------------ big key. "This is the lowest capacity component" Panel rated @ 150 amp 1/0 "Aluminum" service entrance cable is only rated for 125amps
|
|
#23
|
||||
|
||||
|
Please Note:
mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I guess they didn't want to look bad?~ LOL
My excuse??... I'm either so darn good looking... or.... I just don't know any better! |
|
#24
|
||||
|
||||
|
I'm glad to know I got it right. The second time.... lol I voted for 150A but then clued into it being AL. I keep a note book full of cheat sheets, went and looked it up and saw it should be 125A.
I don't need to remember everything, I just need to know where to look for the answers to everything! HLC Home Inspections Okla. Lic. #776 I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
Last edited by jsopher; 11/19/08 at 10:53 PM.. Reason: type-o |
|
#25
|
||||
|
||||
|
Hi to all,
OK here's the answer The meter is 200 amp The SECs (1/0 AL) are good for 125 amps The panel has no single disconnect (split bus) but has fewer than 6 moves to shut the home down. The panel is rated at 150 amp. I'd be reporting this as a 125 amp supply, in fact I did, this is from one of my inspections. Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#26
|
||||
|
||||
|
The way I understand it, there are different types of cables, as I stated in one of the early posts. I think the main difference is the type of insulation. Cable insulated with teflon has a higher rating than PVC.
For 1/0 Aluminum, my code check book shows a rating of 100A for TW or UF, 120 for XHHW or USE and 135A for USE-2 or XHHW-2. I had an electrician on site at an inspection one time and I know he was trying to figure out the rating based on the type of wire, not just size. "An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold Eureka, Fortuna & Arcata, CA
|
|
#27
|
||||
|
||||
|
Hey Gerry, got it right. Not bad for a hammer Eh!
Well, I did get some inside undercover assistance. Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#28
|
||||
|
||||
|
Quote:
I definately agree on the differences in cable types however my code book shows the following for service entrances. 2 AL = 100 amps 1 AL = 110 amps 1/0 AL = 125 amps Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#29
|
|||
|
|||
|
Please Note:
rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks to be upside down?
|
|
#30
|
||||
|
||||
|
lol......guess not enough people watched my sizing video before I removed it from the web....lol
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| What's this video worth? | jtedesco1 | Education | 5 | 4/18/08 10:24 AM |
| Handbook for Electrical Safety | pabernathy | Electrical | 1 | 1/1/07 2:14 PM |
| Electrical Safety Information | jtedesco1 | Electrical | 0 | 2/19/06 2:48 AM |