  #16  
Old 11/16/08, 7:28 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,789
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by badair View Post
teaser + or minus shoe size
Hey, don't forget to hit the lug with hammer to make sure it don't come loose.
Reply With Quote
  #17  
Old 11/17/08, 9:56 AM
John A. Sopher's Avatar
John A. Sopher John A. Sopher is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Oklahoma City, OK
Posts: 240
Default Re: QOD for 11/16/08 Electrical

You got me on this one... As I hit the vote button I'm thinking AL wire..... Ohhhhhh too late.



HLC Home Inspections



Okla. Lic. #776


I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708
Reply With Quote
  #18  
Old 11/17/08, 9:58 AM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

It looks like the cable could have a rating of anywhere from 125 A to 170 amp (e.g. TW vs. THHW vs. THHN).

It needs a main breaker rated to the lower of the cable rating or the panel rating.
Reply With Quote
  #19  
Old 11/17/08, 9:32 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by rbrady View Post
It needs a main breaker rated to the lower of the cable rating or the panel rating.
Hi Ralph, you sure??

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #20  
Old 11/17/08, 10:45 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Wow, over 200 views and only 25 answers????

Strange

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #21  
Old 11/17/08, 10:55 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by gbeaumont View Post
Hi Ralph, you sure??

Regards

Gerry
After your comment, I zoomed in and it looks like it may be a split bus with 5 throws to disconnect all power. In that case, I guess it does not need a main shut-off/breaker, except that there should be a shut-off at the exterior (if it is not an exterior mounted panel).
Reply With Quote
  #22  
Old 11/18/08, 12:05 AM
mjohnson6's Avatar
mjohnson6 mjohnson6 is offline
Active Poster
 
Join Date: Aug 2007
Location: NH
Posts: 175
Send a message via Yahoo to mjohnson6
Please Note: mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

The answer was 125 Amps.

200 amp meter
1/0 AL SECs<------------ big key. "This is the lowest capacity component"
Panel rated @ 150 amp

1/0 "Aluminum" service entrance cable is only rated for 125amps

Reply With Quote
  #23  
Old 11/18/08, 12:09 AM
mjohnson6's Avatar
mjohnson6 mjohnson6 is offline
Active Poster
 
Join Date: Aug 2007
Location: NH
Posts: 175
Send a message via Yahoo to mjohnson6
Please Note: mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by gbeaumont View Post
Wow, over 200 views and only 25 answers????

Strange

Gerry
I guess they didn't want to look bad?~

My excuse??... I'm either so darn good looking...
or.... I just don't know any better!
LOL
Reply With Quote
  #24  
Old 11/18/08, 1:25 AM
John A. Sopher's Avatar
John A. Sopher John A. Sopher is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Oklahoma City, OK
Posts: 240
Default Re: QOD for 11/16/08 Electrical

I'm glad to know I got it right. The second time.... lol I voted for 150A but then clued into it being AL. I keep a note book full of cheat sheets, went and looked it up and saw it should be 125A.

I don't need to remember everything, I just need to know where to look for the answers to everything!



HLC Home Inspections



Okla. Lic. #776


I am licensed Realtor with Keller Williams. Office Phone # 405-691-2708

Last edited by jsopher; 11/19/08 at 9:53 PM.. Reason: type-o
Reply With Quote
  #25  
Old 11/19/08, 6:44 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Hi to all,

OK here's the answer

The meter is 200 amp
The SECs (1/0 AL) are good for 125 amps
The panel has no single disconnect (split bus) but has fewer than 6 moves to shut the home down.
The panel is rated at 150 amp.

I'd be reporting this as a 125 amp supply, in fact I did, this is from one of my inspections.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #26  
Old 11/19/08, 6:55 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

The way I understand it, there are different types of cables, as I stated in one of the early posts. I think the main difference is the type of insulation. Cable insulated with teflon has a higher rating than PVC.
For 1/0 Aluminum, my code check book shows a rating of 100A for TW or UF, 120 for XHHW or USE and 135A for USE-2 or XHHW-2.

I had an electrician on site at an inspection one time and I know he was trying to figure out the rating based on the type of wire, not just size.
Reply With Quote
  #27  
Old 11/19/08, 7:05 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,789
Default Re: QOD for 11/16/08 Electrical

Hey Gerry, got it right. Not bad for a hammer Eh!

Well, I did get some inside undercover assistance.
Reply With Quote
  #28  
Old 11/19/08, 7:44 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/16/08 Electrical

Quote:
Originally Posted by rbrady View Post
The way I understand it, there are different types of cables, as I stated in one of the early posts. I think the main difference is the type of insulation. Cable insulated with teflon has a higher rating than PVC.
For 1/0 Aluminum, my code check book shows a rating of 100A for TW or UF, 120 for XHHW or USE and 135A for USE-2 or XHHW-2.

I had an electrician on site at an inspection one time and I know he was trying to figure out the rating based on the type of wire, not just size.
Hi Ralph,

I definately agree on the differences in cable types however my code book shows the following for service entrances.

2 AL = 100 amps
1 AL = 110 amps
1/0 AL = 125 amps

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #29  
Old 11/23/08, 1:22 AM
rsummers rsummers is offline
New User
 
Join Date: Oct 2003
Location: 13302 Cabin Hollow Court Suite 110 Chico, CA 95973
Posts: 35
Please Note: rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD for 11/16/08 Electrical

Looks to be upside down?
Reply With Quote
  #30  
Old 11/24/08, 7:51 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD for 11/16/08 Electrical

lol......guess not enough people watched my sizing video before I removed it from the web....lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 1:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts