View Poll Results: Stucco over Timber framing needs a control joint for every _______ sqft
100 10 43.48%
120 2 8.70%
144 9 39.13%
150 2 8.70%
Voters: 23. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 11/21/06, 1:11 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default QOD for 11/21/06 Stucco

Hi to all,

Here's todays question

Picture courtesy Carl "Mr BadStucco" Brown

Regards

Gerry
Attached Images
File Type: jpg side-smallCarlBrown (Small).jpg (53.3 KB, 91 views)



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106


Last edited by gbeaumont; 11/21/06 at 1:14 PM..
Reply With Quote
  #2  
Old 11/21/06, 1:38 PM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 351
Default Re: QOD for 11/21/06 Stucco

Gerry;
Not everyone can have a wall like that !!!!!!!!
Thank god;
Reply With Quote
  #3  
Old 11/21/06, 9:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: QOD for 11/21/06 Stucco

I think you are asking for the maximum typical spacing, no?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 11/22/06, 12:13 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/21/06 Stucco

Quote:
Originally Posted by lkage
I think you are asking for the maximum typical spacing, no?
Larry, there are several criteria to be taken into account with stucco, there is a maximum sqft area and also maximum height or width dimensions.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 11/22/06, 12:16 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/21/06 Stucco

Quote:
Originally Posted by lungar
Gerry;
Not everyone can have a wall like that !!!!!!!!
Thank god;
I hear you Len, unfortunately there are just not enough bad installers to go around, some people actually end up with stucco installed by people who know what the hell they are doing

Good god and I thought my humor was a bit on the dry side

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 11/22/06, 10:16 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: QOD for 11/21/06 Stucco

Quote:
Originally Posted by gbeaumont
Larry, there are several criteria to be taken into account with stucco, there is a maximum sqft area and also maximum height or width dimensions.

Regards

Gerry

Yes, your question asks about square footage, which is typically area, so one would want the maximum...that's my thinking.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 11/22/06, 5:19 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: QOD for 11/21/06 Stucco

I'm sooooo glad I don't have to deal with EIFS anymore!!!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #8  
Old 11/23/06, 10:04 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/21/06 Stucco

Hi to all,

The correct answer to this is:

144 square feet

Also no single dimension should be more than 18ft in length

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 11/23/06, 10:24 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: QOD for 11/21/06 Stucco

Quote:
Originally Posted by gbeaumont
Hi to all,

The correct answer to this is:

144 square feet

Also no single dimension should be more than 18ft in length

Regards

Gerry
For what types of stucco are you referencing?

Is there a Code or Standard that references the 144 square feet requirement?



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 11/23/06, 11:08 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/21/06 Stucco

Hi Joe,

the requirement is for cementatious stucco installed over timber framed walls a nd come from the ASTM std for stucco as referenced by most if not all cementatious stucco manufacturers installation instructions.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #11  
Old 11/23/06, 3:12 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: QOD for 11/21/06 Stucco

Just for Reference:



Designation: C 1063 – 03


Standard Specification for
Installation of Lathing and Furring to Receive Interior and Exterior Portland Cement-Based Plaster1



7.11.4.1
Control Joints—Control (expansion and contraction)
joints shall be installed in walls to delineate areas not
more than 144 ft
2(13.4 m2) and to delineate areas not more than
100 ft
2(9.30 m2) for all horizontal applications, that is, ceilings,
curves, or angle type structures.
7.11.4.2 The distance between control joints shall not exceed
18 ft (5.5 m) in either direction or a length-to-width ratio
of 2
12 to 1. A control joint shall be installed where the ceiling
framing or furring changes direction.





**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #12  
Old 11/23/06, 4:28 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: QOD for 11/21/06 Stucco

Thanks



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #13  
Old 11/23/06, 7:30 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,638
Default Re: QOD for 11/21/06 Stucco

What the heck it is just stucco. Thats the least of the problems!
Reply With Quote
  #14  
Old 11/25/06, 1:43 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,580
Default Re: QOD for 11/21/06 Stucco

The texture is very nicely done. We're seeing a lot of that here lately. They must have a new training class - You see so few quality installations like this.
Reply With Quote
  #15  
Old 11/25/06, 8:49 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: QOD for 11/21/06 Stucco

Quote:
Originally Posted by dbowers
The texture is very nicely done. We're seeing a lot of that here lately. They must have a new training class - You see so few quality installations like this.
Dan,

This quality piece was done by "Wreckham & Skarper Installations" and is titled "Relief map of the moon" It was done in thier friday afternoon on the way back from the pub period, which is recognised as one of the best periods for random application art.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need to ID type of stucco cdewitt Exterior Inspections 20 12/4/06 11:39 PM
Stucco course badair Inspection Education & Training 2 11/21/06 6:51 PM
Wisconsin stucco problem dnice Exterior Inspections 6 10/17/06 9:03 AM
Stucco and Building Wrap eyerise Exterior Inspections 5 6/29/06 9:35 AM
Stucco Inspection dlee2 General Inspection Discussion 7 4/3/06 9:17 PM


All times are GMT -4. The time now is 10:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts