View Poll Results: What portion of a beam or joist SHOULD NOT be notched?
a.) Upper 1/3 Portion 10 25.00%
b.) Middle 1/3 Portion 22 55.00%
c.) The Lower 1/6th Portion 8 20.00%
Voters: 40. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 12/26/06, 11:22 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default QOD- 12/26/2006 - Framing ( IRC-2003)

This is a simple QOD- Please read it carefully before answering it...we are not looking for ALL the varibles...just the answer to the actual question.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #2  
Old 12/26/06, 8:27 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Upper? Is that the top of the beam?
Reply With Quote
  #3  
Old 12/26/06, 8:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

lol....man......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 12/26/06, 8:57 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

upper, lower? Can this joist be confused for a stud? Paul, I'm glad you're an electrician, I'd hate to see the houses you build.

<once again, ducking and running>

tom
Reply With Quote
  #5  
Old 12/26/06, 9:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

lol...nope the term joist is fine..........it is written this way.....you have only a limited space for the question..has to be brief and to the point...Plus these terms are written in the IRC text that covers this question as well....don't blame the messenger...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 12/26/06, 9:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Quote:
Originally Posted by tdietrich1
upper, lower? Can this joist be confused for a stud? Paul, I'm glad you're an electrician, I'd hate to see the houses you build.

<once again, ducking and running>

tom
FYI....nope......a JOIST is not a stud.....could not support the weight that a ceiling " JOIST" or BEAM would allow....thehehe.....confused yourself didn't you...put that coffee away Thomas.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 12/26/06, 9:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Actually, my floor framing and beams usually look pretty good up until the Electrians and Plumblers show up. ha ha. That is when I have to pay attention to holes and notches.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #8  
Old 12/26/06, 9:15 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Quote:
Originally Posted by mcyr
Actually, my floor framing and beams usually look pretty good up until the Electrians and Plumblers show up. ha ha. That is when I have to pay attention to holes and notches.

Marcel
Woooooooo! I drill tiny 3/8" to 1" holes. The real evil people are the HVAC guys. I've seen them cut 3-4 sections of top plates before they found the right way they wanted to run their ducts. Damn top plate butchers!

tom
Reply With Quote
  #9  
Old 12/26/06, 9:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Quote:
Originally Posted by mcyr
Actually, my floor framing and beams usually look pretty good up until the Electrians and Plumblers show up. ha ha. That is when I have to pay attention to holes and notches.

Marcel
Hey....MY holes are allowed..........we are talking about NOTCHING...think about it...if I NOTCHED the middle 1/3rd......the freakin THING would fall...oh wait...I just gave away the answer.....shucks...oh well!



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 12/27/06, 7:16 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,139
Default Re: QOD- 12/26/2006 - Framing ( IRC-2003)

Quote:
Originally Posted by pabernathy
Hey....MY holes are allowed..........we are talking about NOTCHING...think about it...if I NOTCHED the middle 1/3rd......the freakin THING would fall...oh wait...I just gave away the answer.....shucks...oh well!
Thanks for helping Paul. ha. ha.

Yea, I know, there are still a few that care, right? ha. ha.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Framing Inspection once the walls are up (posted by Lisa Leach) AskNACHI.org AskNACHI.org Forum 3 7/18/07 3:13 AM
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM
Roof framing jcampbell Structural 18 3/15/06 8:10 PM


All times are GMT -4. The time now is 4:14 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts