| View Poll Results: In newer construction outlets shall be _______ in habitable spaces? | |||
| 6 feet apart |
|
12 | 30.77% |
| 8 feet apart |
|
1 | 2.56% |
| 10 feet apart |
|
2 | 5.13% |
| 12 feet apart |
|
24 | 61.54% |
| Voters: 39. You may not vote on this poll | |||
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
||||
|
||||
|
Hi to all
here is todays question Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#2
|
||||
|
||||
|
210.52 (A)(1) Spacing...
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#3
|
||||
|
||||
|
Quote:
I do not have a book. ha. ha. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#4
|
||||
|
||||
|
(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than XXXXXXXX from a receptacle outlet. Teehehhe.....I XXX'ed out the answer....SUFFER FOLKS ! Now I LOVE how the NEC makes that anser CRYPTIC in nature rather than just giving the answer it makes you THINK for a second to get the answer....Freakin NEC Code Panel........called Job Security.. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#5
|
||||
|
||||
|
Quote:
2002 NEC 210.52 "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#6
|
||||
|
||||
|
OH and don't forget...any wallspace 2' or larger gets a receptacle as well...
(2) Wall Space. As used in this section, a wall space shall include the following: (1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#7
|
||||
|
||||
|
OK...Poll is closed so here is your G. Beaumont answer..
(A) General Provisions. In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dwelling units, receptacle outlets shall be installed in accordance with the general provisions specified in 210.52(A)(1) through (A)(3). (1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet. And since we know cords are 6' long as a standard, placing something in the center of a 12' span will leave you 6' to the receptacle of your choice. Also we all know the famous verbage to commit to memory is 6 and 12 which means 6' from any opening more or less and then every 12' along the wall...I wont get to detailed as I think you get the point. This message has be bought to you by the makers of VOLVO.... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical | 5 | 9/14/08 4:58 PM |
| Handbook for Electrical Safety | pabernathy | Electrical | 1 | 1/1/07 2:14 PM |
| Some good questions that always need answers | jtedesco1 | Electrical | 5 | 6/16/06 10:10 PM |
| Electrical Safety Information | jtedesco1 | Electrical | 0 | 2/19/06 2:48 AM |